Discuss Solar Array swa sizing in the UK Electrical Forum area at ElectriciansForums.net

I may have really over-estimated the average solar power, but equally I have probably underestimated future electricity costs as well but a large amount!
 
There are on line estimating tools which can produce annual and month by month figures for pv generation.
I have seen some tools such as that and they offer you the expected annual power. But the problem here is the I2R losses depend on the current squared, so the shape of the illumination waveform has an impact on the relationship between average solar generation and average cable loss.

E.g. if we get 10% of the panel capacity on average (roughly what I just saw on one site for south England) that could be:

100% generation for 10% of the time, so I2 term is 0.1 * (17.4)^2 = 302.7
50% generation for 20% of the time, so I2 term is 0.2 * (17.4 / 2)^2 = 15.1
25% generation for 40% of the time, so I2 term is 0.4 * (17.4 / 4)^2 = 7.6

Due to Earth's rotation the average daylight per year is 50% so 10% panel capacity averaged per year really means 20% average illumination per day, so probably 30-40% sunny cloud-free time and allowing for sine-shaped illumination arc over the day, etc. (but of course that varies summer/winter, and so on).

Above I had assumed 100% time at 1/4 power = 18.9 for I2 term so loss cost maybe high by 20-50% or something.
 
Last edited:
The trick of course is to connect the panels to achieve the highest off load pv array voltage - to keep current lower for a given power- while being mindful of the inverter input voltage limit and staying under the Uo/U voltage spec of swa cable noting that for example 600/1000V are ac rms figures so higher figures for dc by a factor of sqrt2 Thus 850/1400V dc.

Uo voltage between live conductor and earth.
U voltage between live conductors.


In practice, peak panel power output is normally at a voltage whigh is between 70 and 80 % of the no current open circuit voltage not at 50% I mentioned in my opening post. I tend to do pessimistic calculations so it performs better than expected rather than worse. Real panel voltage/current/irradiation curves tend to allow thinner rather than thicker cables cos the IsquaredR energy loss is lower Than the 50% assumption would calculate.
 
Last edited:
PMP = Maximum power point.
1650378722529.png
 

Reply to Solar Array swa sizing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning, I was just looking for some advice on what other sparks would do for the following scenario:- A detached Garage is going to house a...
Replies
9
Views
2K
Hi I currently on a job where the garage is having an office built above it with solar panels installed on the roof. I have ran a 16mm 3 core...
Replies
3
Views
146
Hello, My current 2.5kW Solar pv array is in a less than favourable position, but there is plenty of space to expand the array. I have an...
Replies
2
Views
1K
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
522
My best mate has been medically retired from the prison service at the young age of 52 and has time on his hands :D He's looking at a 'plug in'...
Replies
7
Views
498

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock