Discuss Solar earthing re: isolation transformer in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

D

Dbreeze

Hi Guys

Do you know whether I could fit an external isolation transformer up to a transfomer less inverter, to save me earthing the array. Is this ok and possible. Just don't want to earth array as customer doesnt want the driveway to come up etc. Or is the only way to install a TL Inverter.

Cheers
Dan
 
why do you have to dig up the drive to earth the array?. If you are on TN-S earth to the MET, or if TNC-S an earth rod and 15 metres of 10mm green must be cheaper than sourcing and fitting a Tranny, or just use an inverter with a transformer in.
 
It is a TNCS therefore having to install earth rod, just need to know as they already have TL inverter whether a isolation transformer can be used between inverter and AC isolator (to be advised)
 
look at page 202 in Regs it shows a separate isolation transformer. So easy answer to your question is yes fit an external isolation transformer if this is the most cost effective solution. The tranny is to isolate the array from the earthed public distribution system Read section 413 page 56 in the Regs. The Inverter should be considered one item of current using equipment. 413.1.1
 
Ive read through several posts and I am still not sure why you need to earth / bond the array, can anyone tell me why I should be doing this please?:dozey:
 
I'm fairly certain that fitting a separate isolation transformer is not an option
this is how it was explained to me by one of SMA's engineers
one aspect of the isolation transformer is that it provides separation within the inverter in order to prevent the AC transfer on to the DC cables (electrical separation) , a transformerless inverter obviously cannot do this hence the need to earth the array ,as the above mentioned AC is carried up to the array frame via the DC cables. This is called capacitive discharge and can be over 30mA this is why some inverters require the use of an B type 100mA Rcd, this charge,(I've measured this and seen 120v) is sitting there waiting for somewhere to go, all it needs is a path to earth ,ie the customer cleans the array or is doing work on the roof off an aluminium ladder makes contact with the array and receives a shock ,which may not be enough to kill but could cause them to fall
fitting a transformer upstream of the inverter will not prevent this from happening.
 
@edexlab,

The reason for the Type B RCD is DC injection into the AC, hence shifting the voltage of the AC, it's not there to protect the DC side, it's to protect the AC side from being fed with DC. In a TL inverter the built in RCD doesn't provide RCD protection for the cable, if that is needed (buried etc) you still need to provide an RCD.

Interesting comment about the AC feed into the DC, however and AC current won't create a capacitve effect - because it is an 'Alternating Current', it'll charge / discharge at 50hz, it's DC that builds the capacitve effect.

However without galvanic isolation, the DC creates a potential to earth.

Galvanically isolate it and there still could be a potential difference when measured to one of the DC Cables, howver because the units are Class II, there is no earth route.

(A bit like on a PME system, even when the systems live, ther's no PD between Neutral and earth)
 
Isn't installing a seperate isolation transformer defeating the object? Surely you'll be adding another device which will lower the efficiency of the system.

Just fit a transformered inverter and you're away.
 
Just to get htis straight. Are you saying that any transformerless invertor must have the mounting sytem bonded by use of an earthing rod, and it should have a type b rcd fitted to the circuit?

Also slightly off tangent, dou you conceal/protest your dc cabling on large installation? 9Runs over 50 Meters) . I am quoting for a large 5oKw system, and this will be an issue for the quote.
 
9 runs over 50m? Just make sure you do your volt drop calculations.

As it is, arrays with a transformerless inverter must have the array bonded to earth - on an earth rod if the the supply is a TN-C-S set up.
 
See my post above and my post on the Segen tech conference in Brum, why has been well covered elswehere.

50m runs shouldn't be a problem with correctly sized cable, I regularly have some which have just under 200m round trip (roof 64 long, then 30m to inverter = 94 then back again = 188m +14 panels (12m) = 200m). When you run big strings (close to 1000V, 6 Amps) and size the cable properly the voltage drops can be nominal.
 
Hi Worcester

I just don't get the requirements, even the guide gets the definitions wrong, should I be earthing or bonding the array frame

Also what are the risks particular to PV arrays that needs them to be earthed or bonded?

sorry to be a pain
 
Thanks Worcester , I've definitely got a bit mixed up with my facts here ,case of shoot first check later after a long week
thats one of the best things about this forum there is always someone who can steer things the right way!

I checked my notes and the SMA guy as you would expect did explain things correctly ,
however he did say that in TL models some AC is transferred to the Dc side contributing to capacitive discharge,
Also when I've tested the voltage between the array and the electrode it's been an AC voltage present
I reread the SMA pdf concerned below,

"2 How does a capacitive discharge current occur? During operation,the Pv module is connected to the alternating current grid via the inverter.Thus depending on the device type, a portion of the alternating voltage amplitude arrives at the Pv module.
At this point two cases must be distinguished
1.Transformerless inverter In almost all transformerless models ,half the grid amplitude is operationally passed on to the module. the set up oscillates with 115v/50Hz this applies to SunnyBoy/Sunny Mini Central devices in the product names

2.Inverter with transformer
In Devices with a transformer,the voltage within the Pv module fluctuates with a so called ripple of just a few volts"
as i read this, I'm thinking its the AC causing this effect​



 
Last edited:
Consider this All exposed conductive parts must earthed unless otherwise protected.
An aluminium array is an exposed conductive part.
Otherwise protected -
Double insulated system
Electrically isolated using an Isolation transformer
Non conductive location not feasible
Earth free equipotential bonding not feasible
So An inverter with an isolation transformer or
a separate isolation transformer What has efficiency got to do with where the tranny is inside or outside the Inverter.
No isolation transformer then the Array needs earthing IF it has exposed conductive parts
 

Reply to Solar earthing re: isolation transformer in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
Hi all. We have had 7x 400w solar panels for a number of years now on our roof which is se/nw facing end terrace. 4 on se side 3 on nw side...
Replies
0
Views
831
Hi. I have a UK customer that has an agricultural building that will have a Diesel TPN generator supplying a corn dryer electrical installation...
Replies
1
Views
1K
I have a doorbell I want to install. The issue is the 16v transformer is designed to sit on a DIN rail. I have a 10 way 17th edition BG Nexus...
Replies
4
Views
901
Guys in a solar PV plant room I have a single phase LV board for power and lighting. This is fed via 2 phases off a solar inverter through a 415 >...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock