Search for tools and product advice,

Discuss Solar inverter problem? in the UK Electrical Forum area at ElectriciansForums.net

Poppymac

DIY
Reaction score
6
I'm hoping someone out there has come across this problem.
Just had -8 days ago- a 6k solar panel system plus 4.8k battery pack installed.
When the electrician left the batteries showed 20%full.
Next few days inverter showed producing 30kwh but batteries did not charge.
We normally use 8.5kwh per day, this was from readings taken off the grid meter over 30 days before installation. I also noticed that overnight, on the meter they installed next to the grid meter, it showed we were exported 0.2kwh to the grid when the solar was not produced.
Contacted the installer but they did not get back to us.
Eventually on the 5th day we had a video call and we noticed that the inverter showed our usage grew and waned in time with the production of solar, more produced more we used.
AHH I know what it is said the installation manager, turn the clamp on the red wire the other way round, it's because you've got an old style fuse box.
I did that and the battery started to fill =success I thought.
However, the battery fills but cannot be used.
If I turn the clamp back to its original position the battery discharges, but the same thing happens. My usage goes sky high and the battery discharges quickly.
I turned the clamp back after it dropped 30%, and that night the grid used 4kwh, the battery wàs full and it sent 3kwh back to the grid.

So now we have a full battery not using it, when the solaris not producing the inverter shows no usage.

We use IKwh from the grid overnight and send 0.2back to the grid overnight

Basically: inverter shows more solar more we use, even when we are only running the fridge and freezer
No solar no power used

Can charge the batteries but they can't he used
Using power from the grid not the batteries and sending to the grid overnight

Only asking here as the company are not getting back to me at all now

Thanks

I have photos but not sure I can upload them
 
put photo/s on desktop. go back into forum, click on attach files, then double click each image.
 
like this:
 

Attachments

  • 003 (2).jpg
    330 KB · Views: 18
First move, get the company back on site…. Second, trading standards…..third, don’t pay them a penny! You can go to your bank and try and cancel payments.
Any fault should be covered by the company’s warranty

region of Scotland? There might be a local member that knows pv that could assist.
 
Last edited by a moderator:
First move, get the company back on site…. Second, trading standards…..third, don’t pay them a penny! You can go to your bank and try and cancel payments.
Any fault should be covered by the company’s warranty

region of Scotland? There might be a local member that knows pv that could assist.
Thank you. We paid a deposit then a part payment after installation. We held back an amount. We are near Perth in Scotland. Thank you
 
Thank you. We paid a deposit then a part payment after installation. We held back an amount. We are near Perth in Scotland. Thank you
Trying to show you what happens when I put on the oven. The display shows that the export to the grid goes up. Problem seems to be that the power usage always corresponds to the solar produced therefore the batteries never kick in
IMG_20210619_091309.jpg
IMG_20210619_104212.jpg

Thank you. We paid a deposit then a part payment after installation. We held back an amount. We are near Perth in Scotland. Thank you
 
Trying to show you what happens when I put on the oven. The display shows that the export to the grid goes up. Problem seems to be that the power usage always corresponds to the solar produced therefore the batteries never kick in
View attachment 86922View attachment 86923
The sun is shining so producing more energy. No appliances being used only fridge freezer same as the first photo. See how our power usage soars in line with the solar produced
IMG_20210619_144555.jpg
 
What make is the invertor and what make is the battery system. There are a number of ways to manage the solar output and battery charge and discharge BUT the arrangement of the clamp meters need to be correct and the battery / invertor system needs to be configured correctly to the arrangement of your clamp meters. I strongly suspect this is not set up correctly.
 
What make is the invertor and what make is the battery system. There are a number of ways to manage the solar output and battery charge and discharge BUT the arrangement of the clamp meters need to be correct and the battery / invertor system needs to be configured correctly to the arrangement of your clamp meters. I strongly suspect this is not set up correctly.
Thank you. The inverter is a Solis and the batteries are Pylontech US2000.
When I did eventually get a phone call, he had me turn the clamp around
 
Just found this on the Solid site, does this sound correct?

F6---4kW single phase Energy Storage Inverter。
Got it off here

 
Yes but the devil is in the detail, so you need to know exactly what Solis product you have. Basically, the output of the solar needs confirming with a clamp meter and the load of the house ditto, against what the display is showing, only then will you know what is wrong. I cannot help until i know what product you have and access to the installation manual for CT locations against what has been installed and what settings have been put in the commissioning parameters of the invertor.
What you should see is:
1. PV output A/C correctly measured
2. House load correctly measured
3. If PV is greater than house, battery charges
4. If PV is less than house battery discharges until exhausted (like at night)

cheers
P&S
 
Yes but the devil is in the detail, so you need to know exactly what Solis product you have. Basically, the output of the solar needs confirming with a clamp meter and the load of the house ditto, against what the display is showing, only then will you know what is wrong. I cannot help until i know what product you have and access to the installation manual for CT locations against what has been installed and what settings have been put in the commissioning parameters of the invertor.
What you should see is:
1. PV output A/C correctly measured
2. House load correctly measured
3. If PV is greater than house, battery charges
4. If PV is less than house battery discharges until exhausted (like at night)

cheers
P&S
Thank you I understand. going to grab a torch to try and take a photo of the panel. I understood as you say, that the battery would kick in once solar produced is less than what is used, but as the usage rises when the solar rises and usage goes to zero when solar is not produced the battery never kicks in. ? Off to try
 
Thank you I understand. going to grab a torch to try and take a photo of the panel. I understood as you say, that the battery would kick in once solar produced is less than what is used, but as the usage rises when the solar rises and usage goes to zero when solar is not produced the battery never kicks in. ? Off to try
Is this enough for your needs?
IMG-20210620-WA0000.jpg
 
Nice system !
Here is the manual RHI-3K-48ES-5G - https://www.ginlong.com/rhi_inverter1/1952.html

Your display indicates that the installer has made two connections to your fusebox, one for house and one for critical loads, hence the picture of a house and light bulb. There is only one CT which is measuring grid incoming/outgoing power.

Look at Fig 4.8 /4.9 and see if this represents how your installation is wired. If you look under the Solis, there are two connections , one for Grid and one for critical loads, be interesting if both have been used. I suspect they will have to come back physically to check over the connections.
A photo of the CT would be useful just to see how it has been connected
 
Oh and this is a relatively new concept as its wants to power the critical loads "off grid" - this would require a bit of re-jigging of the fusebox / a second fusebox - so i am now curious how they did it :)
 
IMG_20210620_110911.jpg
IMG_20210620_111206.jpg
IMG_20210620_111516.jpg
IMG_20210620_111133.jpg
IMG_20210620_111019.jpg
IMG_20210620_110949.jpg

Oh and this is a relatively new concept as its wants to power the critical loads "off grid" - this would require a bit of re-jigging of the fusebox / a second fusebox - so i am now curious how they did it :)
Hi I'm glad it's a good system just a pity it doesn't work ?
We have a very old fuse box and i did ask them if it should be changed, but they said no they were just adding a small one just for the system. See photos. Then when the battery didn't charge, the instal manager said it was due to the old fusebox, had the same problem at his place, he said. Just turn the clamp. As I said, that worked to charge the batteries but did not stop the other problems not did it allow the batteries to be used.
 
View attachment 86948View attachment 86949View attachment 86950View attachment 86951View attachment 86952View attachment 86953

Hi I'm glad it's a good system just a pity it doesn't work ?
We have a very old fuse box and i did ask them if it should be changed, but they said no they were just adding a small one just for the system. See photos. Then when the battery didn't charge, the instal manager said it was due to the old fusebox, had the same problem at his place, he said. Just turn the clamp. As I said, that worked to charge the batteries but did not stop the other problems not did it allow the batteries to be used.
IMG_20210620_111842.jpg

Oh and this is a relatively new concept as its wants to power the critical loads "off grid" - this would require a bit of re-jigging of the fusebox / a second fusebox - so i am now curious how they did it :)
 
I think i can see the critical load connection, it is marked A/C Backup, there is also one labelled A/C Grid, be interesting to see where those cables from Solis actually go. They should go to separate "fuse boxes" and did they ask you what you wanted wrt stuff to keep on if there is a power cut, maybe lights ?
 
I think i can see the critical load connection, it is marked A/C Backup, there is also one labelled A/C Grid, be interesting to see where those cables from Solis actually go. They should go to separate "fuse boxes" and did they ask you what you wanted wrt stuff to keep on if there is a power cut, maybe lights ?
Hi thanks. The wires come down through the ceiling in a conduit (another gripe). No they did not ask. Electrician had loads of problems getting the wires down from the cupboard upstair to the meters in the hall. One new fuse box. I'll try and take a video when I get home, I took one but don't seem to be able to find it ?
 
Ok but i dont have knowledge of that model to help diagnose the problem but i can see its not right. It is either the CT is not giving an accurate account of the grid incoming / outgoing or the parameter settings on the solis are not right. I have had similar problems with batteries not either charging or discharging but it was a much more complicated system involving multi vendor. As this is all Solis, it should work almost out of the box. The installer needs to come to site preferably when he can call tech support for assistance. When he does come back you can ask him what loads are on backup... :)
 
Ok but i dont have knowledge of that model to help diagnose the problem but i can see its not right. It is either the CT is not giving an accurate account of the grid incoming / outgoing or the parameter settings on the solis are not right. I have had similar problems with batteries not either charging or discharging but it was a much more complicated system involving multi vendor. As this is all Solis, it should work almost out of the box. The installer needs to come to site preferably when he can call tech support for assistance. When he does come back you can ask him what loads are on backup... :)
Thank you IF they come back. They are not answering me now?
 
IMG_20210620_183629.jpg
Thank you IF they come back. They are not answering me now?
Ok so I've taken more photos. The wires come down and into the new fusebox can't see wires going into the counter showing import and export, but it's right up against their fuse box.
Two grey wires come out of their fuse box into the two small boxes on top of our fuse box. Earth wire goes to the earth and a clamp with black and white wires clamps onto the red wire that goes into the fuse box.
Whilst I understand you cannot give me a solution, you have helped me know that the system is a new kind of inverter and you said it was 'nice', putting my mind at rest that isn't a bad system. As it is new type, I am assuming this is why they are having a few problems. I know what to say to them, thanks to you. I'll let you know what happens ?
IMG_20210620_183537.jpg
IMG_20210620_183606.jpg
 

Attachments

  • IMG_20210620_183640.jpg
    270.8 KB · Views: 19
Well solis are massive in the inverter market and an integrated single box solution for battery storage (now with off-grid working) is basically what has been needed in the market. FWIW Solar companies can be hit and miss with respect to service. When this system is working you will be impressed how the battery fills in the cloudy moments and extends the solar day. Hope it works out
 
Well solis are massive in the inverter market and an integrated single box solution for battery storage (now with off-grid working) is basically what has been needed in the market. FWIW Solar companies can be hit and miss with respect to service. When this system is working you will be impressed how the battery fills in the cloudy moments and extends the solar day. Hope it works out
Thank you ?
 
Thank you ?
You were completely correct.
After corresponding with you, I contacted Solis in the UK outlining the problem. I received a very quick reply from their engineer, who also happened to be the UK manager and he said straight away it seemed the installer had had problems.
Cut a long story short, the installer came out on Tuesday, reluctantly as they thought nothing was wrong. However after about an hour of trying the clamp in different places and unplugging the fridge freezers, he could see , hooray, there was a problem. So he tried to contact the engineers but was unsuccessful. I emailed the engineer and he spoke to the installer. He went into the system over the internet, got back to the installer, told him what to do and bingo it's working. Still the readout is a little strange at times, but as you say, even today the batteries have been charged quickly even though it is cloudy. Best thing is, we've only used 1kwh from the grid since Tuesday and that will be due to the kettle and oven being used later in the evening
Need to get a slower kettle to maximise the solar . At the moment very pleased with it ?
 
Glad its sorted, batteries must discharge overnight if they do not you may be charging from the grid.
Here is a pic of the one i had issues with
Hi yours looks a similar problem, it just doesn't make sense.
The batteries are discharging overnight now, and in fact they supplement the power a tad in the day if needed and charge back up with the solar.
I can change the time the batteries charge, but for now I'm leaving well alone. Once the new supplier is in place I'll look at the battery charge times.
I'm keeping a close eye on things, but thanks for pointing me in the right direction ?
 
Ok update. After 12 days of the system working (although still had problem with the usage showing zero in the evening) the system reverted back to the original problem. Eventually after much back and forth with the Solaris people and the installer, the installer decided it was the emeter at fault, it was loose. I tightened screws to find something was amiss, it was ok one second next it wasn't. Then after a few days the emeter stopped working. Eventually it was changed, but now the battery does not run the fridges and freezers overnight - the grid does. Installer says the batteries only kick in if we use .30 to .50kwh, so we will use the grid. Why have batteries if they won't kick in? They did when the system worked for 12 days. Used 1kwh every 4/5 days. Now using 2kwh overnight . ?. The inverter readout still does not add up either.
 
My posts 26 and 27 enquired about what is connected to the critical loads circuit, Is this the fridge , freezer you refer to. Without knowing this you will never be able to figure out what is what.

Can you take a pic of the display again
 
My posts 26 and 27 enquired about what is connected to the critical loads circuit, Is this the fridge , freezer you refer to. Without knowing this you will never be able to figure out what is what.

Can you take a pic of the display again
H yes I can.

It has been changed though so that the only one it goes through is the house not the backup light symbol.

This was done previously and it worked well for twelve days

Then when the emeter was changed, the installer changed it to show the house and the backup.

That's when the usage overnight was 2-3 kWh for the fridge and freezer

I asked to change it back to how it was when it worked for 12 days ie house.

I have just changed it back.

See photo.
 

Attachments

  • 1626535078183..jpg
    487.7 KB · Views: 16
Yes that's not the problem. It does do that. It's at night. The batteries aren't used to run the fridge freezers. The grid is used. I'm hoping that putting it all through the house, then the batteries and not the grid will be used.

Up to now, since the emeter was replaced, the grid had been used throughout the night
 
At night i would expect the batteries to run down powering whatever is needed. As long as the batteries are flat before the Sun comes out, i guess it does not matter
Well exactly what I said to the installer.

We have full battery 4.8kw and it's not being used overnight. It discharges to say about 80% as we use the oven and watch TV when the solar is producing less.

At the moment I am using the oven and the solar is powering it along with Some from the battery, with alternating every second or so, using from the grid sending to the grid. Once the oven comes to heat, usage drops and the solar is producing enough .

Once we get only to using only the freezers and fridges it is powered by the grid even though the battery is still 80% full.

That's when the installer vtoldvme the battery wouldn't kick in if the fridge and freezers used less than .30kwh, which I find ludicrous to be honest. Bit sure I believe him.

So tonight I am hoping that as it's all routed to the house, then things will work properly.

See photos with oven on
IMG_20210717_180458.jpg
IMG_20210717_180455.jpg
 
Ok still no further forward. On a cloudy day we saw what happened. At 81% the battery powers the fridges and freezers ok. As soon as it hits 80%, the battery goes into 'sleep mode' and power source switches to the grid. No one knows what the problem is - anyone got any thoughts?
 
I haven't had a chance to read this in depth, but the fact that the battery hits 80% and stops discharging could indicate that the depth of discharge setting is too high. Generally the installer sets the system so that 10-20% of the battery is not used, as even though lithium batteries can be discharged very low you buy quite a bit of extra life for them by allowing this buffer. The installer or Solis tech should be able to see the setting remotely. It could be as simple as they thought they were setting it to stop at 80% DoD and in fact were setting it to stop at 80% capacity.

Sometimes a factory reset and reconfigure can help.

Most likely something that has already been looked at, but thought I would mention it!
 
I haven't had a chance to read this in depth, but the fact that the battery hits 80% and stops discharging could indicate that the depth of discharge setting is too high. Generally the installer sets the system so that 10-20% of the battery is not used, as even though lithium batteries can be discharged very low you buy quite a bit of extra life for them by allowing this buffer. The installer or Solis tech should be able to see the setting remotely. It could be as simple as they thought they were setting it to stop at 80% DoD and in fact were setting it to stop at 80% capacity.

Sometimes a factory reset and reconfigure can help.

Most likely something that has already been looked at, but thought I would mention it!

Thanks both of you. I've got videos but I'm unable to attach them - only photos are showing when I try to attach.
With regards to the settings, it is strange.as before the new emeter was installed (before it gave up the ghost completely) for 12 days it was working perfectly. The system was installed on the 9th June.

I will try and take a photo tomorrow as the battery is at 83% at the moment and is powering the lights and fridges although I have to say that the power is jumping either to or from the grid constantly since we are using just battery power.


Can you take a pic of the display when it is in that state, i.e. your are clearly drawing power but the batteries are not contributing
 
Thanks both of you. I've got videos but I'm unable to attach them - only photos are showing when I try to attach.
With regards to the settings, it is strange.as before the new emeter was installed (before it gave up the ghost completely) for 12 days it was working perfectly. The system was installed on the 9th June.

I will try and take a photo tomorrow as the battery is at 83% at the moment and is powering the lights and fridges although I have to say that the power is jumping either to or from the grid constantly since we are using just battery power.
IMG_20210727_050535.jpg
IMG_20210727_050535.jpg
 
I see that the critical load is back (lightbulb), its got to be in the parameter settings as there is clearly a load for the batteries to contribute to, but it has decided it does not want to.
I would try and contact Solis again and see if they will dial in and go through the parameters.
 

Reply to Solar inverter problem? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
804
Hi I currently on a job where the garage is having an office built above it with solar panels installed on the roof. I have ran a 16mm 3 core...
Replies
3
Views
166
Hi, firstly appologies if my terminology is wrong but I know very little about electrics and have no idea why this is happening - I have 2...
Replies
4
Views
455
For power outages, my solar inverter (+battery) is able to take on the entire house load - as long as I unplug my collection of vintage kettles...
Replies
3
Views
959
Hi all. We have had 7x 400w solar panels for a number of years now on our roof which is se/nw facing end terrace. 4 on se side 3 on nw side...
Replies
0
Views
861

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock