Discuss Solar PV supply taken from a 32 amp ring circuit. Is this acceptable? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
0
One of my domestic electrical customers has recently had a 4Kw solar PV system installed.
The area in the garage next to where the array was located does not have easy access to the main Consumer Unit so the installers have installed a 2-way garage consumer unit to connect the inverter. This 2 way garage unit obtains its supply by breaking into the original local 32 amp ring circuit to use as the main supply conductors. This original ring circuit is protected by an rcd at the main consumer unit and since the PV system has been installed the rcd at the main consumer unit trips on a very regular basis.
I have tested the rcd on the main consumer unit and it operates as it should.
I would like to know if this type of connection is acceptable as I believe that the inverter should be on its own dedicated circuit that is preferably non rcd protected.
Can anyone give me advise please.
 
Hi,

The PV system should be on it's own circuit with it's own breaker. For example it may be a B20 for a 4KW solar PV system.
If the sparky who installed it had no space on your consumer unit it may be why he doubled it up, although it is not acceptable.
A spare way should be used on the board where applicable or a secondary consumer unit should be added (with tails).
A RCD should be avoided where applicable as a 30mA RCD may nuisance trip.
 

Reply to Solar PV supply taken from a 32 amp ring circuit. Is this acceptable? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
839
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
3
Views
151
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K
hi thank you for help in advance have a potential pv installation for a garage roof that is some 60m from the main house (main incomer in the...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock