Doesn't that Wylex switch fuse have double terminals on the main switch that you can loop from?
The older ones did, but I think that one looks like the more recent version with the single terminal.
Discuss Splitting meter tails at 3m in the UK Electrical Forum area at ElectriciansForums.net
Doesn't that Wylex switch fuse have double terminals on the main switch that you can loop from?
Don't think the switch is right for the later version. Looks like a 160CM to me, which should have the loop terminals. A look behind the grey terminal cover will confirm.The older ones did, but I think that one looks like the more recent version with the single terminal.
The 3m limit is mentioned under 433.2.2(ii) and under 434.2.1(i) in the context of where OCPD is located (at source or CSA reduction of cable run, or further along it).There isn't a 3m tails limit in BS7671, to the best of my knowledge, it's a rule that DNOs have and I don't imagine you'd be wildly exceeding it.
Agreed, I was aware of these regs, but I think this easily causes confusion. These are our 3m rules about moving the OCPD along a circuit. I think of these regs when I think of bus-bar chambers and a short run in a smaller conductor in mechanically protected containment to a switched fuse.The 3m limit is mentioned under 433.2.2(ii) and under 434.2.1(i) in the context of where OCPD is located (at source or CSA reduction of cable run, or further along it).
Ah yes, I should read the complete post before starting to reply to it! This is the bit I'd emphasise!However, the specific aspect of relying on the DNO fuse for that OCPD is under 434.3(iv) where it is permitted provided the DNO ("distributor" in the text) agrees to its use.