There isn't a 3m tails limit in BS7671, to the best of my knowledge, it's a rule that DNOs have and I don't imagine you'd be wildly exceeding it.
The 3m limit is mentioned under 433.2.2(ii) and under 434.2.1(i) in the context of where OCPD is located (at source or CSA reduction of cable run, or further along it).

However, the specific aspect of relying on the DNO fuse for that OCPD is under 434.3(iv) where it is permitted provided the DNO ("distributor" in the text) agrees to its use.

So if the DNO said yes, then the cable is protected at source and no 3m limit, however, if they have not approved that and/or the fuse is not able to protect according to BS7671 (5s disconnection time for sub-main fault) then you would need to put in your own protection that does meet BS7671.

The DNO is not obliged to meet the BS7671 disconnection times as their fuse is intended to protect their network from overload (and as a means of isolation, of course) and it is not for shock protection ADS, hence the reason that Ze can be up to 0.8 ohm TN-S and still seen as OK even for a 100A fuse supply that would need 0.3 ohm or so to be compliant for ADS.
 
Last edited:
The 3m limit is mentioned under 433.2.2(ii) and under 434.2.1(i) in the context of where OCPD is located (at source or CSA reduction of cable run, or further along it).
Agreed, I was aware of these regs, but I think this easily causes confusion. These are our 3m rules about moving the OCPD along a circuit. I think of these regs when I think of bus-bar chambers and a short run in a smaller conductor in mechanically protected containment to a switched fuse.
The thing is, these regs only come into play if the supplier fuse isn't deemed to protect the tails.
However, the specific aspect of relying on the DNO fuse for that OCPD is under 434.3(iv) where it is permitted provided the DNO ("distributor" in the text) agrees to its use.
Ah yes, I should read the complete post before starting to reply to it! This is the bit I'd emphasise!

In the OP's case it seems as though it could be arranged to have minimal extra tails length. Not one I'd lose sleep over, compared to some we see!
 
Agreed, here the tails seem to be well protected in the plastic pipe along with their usual double sheath. Extending/splitting them to another fused-switch along side it would seem a reasonable thing to do.
 

Reply to Splitting meter tails at 3m in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
890
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
723

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock