CDB

-
Reaction score
10
Hi all,

I have a 32A Final Ring Circuit that I have swapped a single socket to a FSU for an outside light. I'm now testing it and finding it has a discontinuous earth - I'm also kicking myself for not checking from the off but we learn. Anyway from the attached image you should be able to see my results arranged in a rough layout of the property. If you were looking for a DE where would you start?

ringMain.PNG


I didn't do anything on the day I was there because I didn't have a long lead kit. I'm now kicking myself because I feel I should have been able to suss it on the day.

Thanks in anticipation of your help.
 
Not quite sure of your explanation (of the fault), but from your end to ends looks like there is a bad connection on r2 (>500mOmhs)?

Is the dodgy socket s2 in the dining room?
 
disconnect the cpc's from the CU, then with a wander lead, go from one leg end round the sockets. when you run out of readings, then do same for other leg. the fault will be between the 2 sockets that have o/c readings.
 
Assuming the values given on the plan are Zs readings then having 1.7Ω in the dining room that close to the CU would indicate to me that you are measuring the resistance of the cpc over the length of the ring so the expected disconnection would be from CU to S1 (possibly S2) in the dining room.

Theoretically from the readings at a glance the ring would be laid out like the below diagram.
However just a guess.
ring missing cpc.jpg
 
At the board connect live and cpc of one of the legs. Measure R1+R2 at each socket. At some point you will get 'open circuit'. Repeat for the other leg. It may help to to draw a diagram, as you go and note readings. You should now be able to narrow the fault down to a couple of sockets.

I had to read this twice but what you are suggesting is like the fig8 tests which I've done but on 1 half of the ring only! Good call. Wish I had known that when at the property - I didn't think I could do anything because I didn't have a long lead with me.
 
Assuming the values given on the plan are Zs readings then having 1.7Ω in the dining room that close to the CU would indicate to me that you are measuring the resistance of the cpc over the length of the ring so the expected disconnection would be from CU to S1 (possibly S2) in the dining room.

Theoretically from the readings at a glance the ring would be laid out like the below diagram.
However just a guess.
View attachment 36157

Hi Richard,

That's really helpful. Thank you. They are r1+r2 fig8 results. So, if I understand correctly, the low values I see in the Kitchen are because they only have one short leg from the CU and the 'return' journey via the dining room is open circuit. The LIM at s2 is because its behind a large dresser.
 
disconnect the cpc's from the CU, then with a wander lead, go from one leg end round the sockets. when you run out of readings, then do same for other leg. the fault will be between the 2 sockets that have o/c readings.

Thanks. This is the method I knew but didn't have a long lead for.
 
Thank you guys (and gals) for all the replies. First post on the forum and super impressed with the helpful and supportive responses. Its hard being a lone worker as I'm sure many of us are when you cannot just knock on your colleagues office door for a second opinion. Its nice to know that help is only a post away.

Thanks again!
 
Hi Richard,

That's really helpful. Thank you. They are r1+r2 fig8 results. So, if I understand correctly, the low values I see in the Kitchen are because they only have one short leg from the CU and the 'return' journey via the dining room is open circuit. The LIM at s2 is because its behind a large dresser.
R1+R2
 
No. That's fine. My OCD just wishes I could edit it so it was correct. I'm getting use to a new keyboard which is a bit rubbery and smaller than my standard desk one. I'm all fingers and thumbs!
 
Hi Richard,

That's really helpful. Thank you. They are r1+r2 fig8 results. So, if I understand correctly, the low values I see in the Kitchen are because they only have one short leg from the CU and the 'return' journey via the dining room is open circuit. The LIM at s2 is because its behind a large dresser.


I'd tell her to hurry up getting dressed and shift out the way so you can also check that socket. :D
 
Reminds me of a job a couple of months ago on a house refurb. I narrowed it down to one room and it turned out they had built a stud wall directly in front of an existing wall and boarded straight over the socket where the fault was. Only managed to find it as I started lifting floor boards to trace back the wiring.
 

Reply to Starting point for discontinuous earth fault on final ring. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
566
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
I recently sold my Renault Trafic as it had done 214,000 miles and I also wanted something more economical. I bought the Citroen Berlingo LWB. A...
Replies
34
Views
2K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock