Hi.....I think I'm being dumb.....when installing 35mm swa cable and then recording it on the schedule of test results sheet ....what conductor size do I log for live and cpc.....thanks in advance...
 
Hi.....I think I'm being dumb.....when installing 35mm swa cable and then recording it on the schedule of test results sheet ....what conductor size do I log for live and cpc.....thanks in advance...

Using a little bit of common sense would suggest that recording the size of the conductor in the boxes where the size of the conductor is required would be a good idea!
It is common practice to record something like 'swa' in the box for the cpc for such an installation, but you can equally record the actual csa (which you will know from when you looked it up to do the calculation for it) although it will look a bit odd as it won't be a standard size.

Applying a little more common sense you could also see that the flux lead to the banjo would be better off being of an equivalent size to the rest of the cpc (allowing for the difference in materials of course)
 
I generally record SWA, but if you want a size and assuming it is a four core the csa of the armour is approximately 80.0mm. Due to the higher resistance of steel in relation to copper this relates approximately to a csa of 6.0 for use as a cpc. Hence the size of conductor from your earth tag should not be less than 6.0.
 
Last edited:

Reply to Steel wire armour in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K
Hi all, Figured I'd come straight to the experts with this one because I don't have a great deal of electrical experience. I'm a designer at a...
Replies
21
Views
2K
Hi There Just a quick one, I'm wondering what's everyone's thoughts on this are. A subby has clipped a cable to a plaster board ceiling using 3m...
Replies
8
Views
694
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock