In the BYB:

421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:

  • (i) have their enclosure manufactured from non-combustible material, or
  • (ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12.
NOTE 1: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.
NOTE 2: The implementation date for this regulation is the 1st January 2016, but does not preclude compliance with the regulation prior to that date.

BTW, direct copy from the electronic version of the BYB a few seconds ago.
You know the scope of 61439-3
I realise that there are other 61439-* standards, and you could argue that some of them apply.
Also some similar switchgear will be made to alternative -* numbers, there in lies another failing of the reg.

So when has this changed? Where is the mention of 960° glow wire tested plastic not meeting this regulation?
 
So when has this changed? Where is the mention of 960° glow wire tested plastic not meeting this regulation?


You have been looking at the DPC.
This is from the released version.
The reference was removed between the DPC & the final draft for signing off, which I was lucky to see a page of @ Elex Sandown.
The above quote is the actual reg that has been published.

There are also further changes that have gone in under the radar as it were.
 
You have been looking at the DPC.
This is from the released version.
The reference was removed between the DPC & the final draft for signing off, which I was lucky to see a page of @ Elex Sandown.
The above quote is the actual reg that has been published.

There are also further changes that have gone in under the radar as it were.

So bollo*ks to it then. 960° glow wire tested plastic is non-combustible as defined in the product standard. The version of the BYB I was shown had this reference in it. It seems this has now disappeared.

Why are we now having this conversation??

We can give up talking altogether about metal boards in domestic finally!
 

Reply to Tails - metal board - TT system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
351
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I have added a consumer unit and an earth stake to this so called temporary supply. This is a full rcbo board apart from the mcb to the spd...
Replies
11
Views
3K
Hi, I was hoping someone with a little more insight might be able to shed some light on a potential issue I have, as I can't seem to find another...
Replies
75
Views
7K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock