Much though I don't like it, once in a while I use a second hand MCB - for one that has long since gone obsolete and new ones are unavailable. What about testing used MCBs before reusing them, does anyone actually do this?

I just tested a 5A MCB at a couple of values of loading, it seemed to more or less follow the curve in the BGB - for example, at 12.5A, it reliably trips after approx. 25s. I'm thinking this is all I can practically do.

NB: For a much larger rated MCB, even this would get tricky, I don't have readily available loads.
 
Don't go there, it's well out of a sparks remit.

The machine will probably be the same price as a Porsche.
 
Don't go there, it's well out of a sparks remit.

The machine will probably be the same price as a Porsche.

Umm what machine, can you elaborate?
I'm testing using a spare CU on the bench, some loads (e.g. kettles & toasters) and a stopwatch!
 
Just thinking about this out loud, I'm sure someone will correct me if I'm wrong.


Say a D40 60898 requires testing for instantaneous disconnection. That's x20 In? 800A?

Not to be done in ones shed.
 
For smaller MCB's like 1A - 10A you could just apply an appropriate load and test the curve of the thermal operation, for larger values you'd need to invest in a current injection unit. Problem is though you won't be able to test the disconnection times of the mag operation under fault conditions.

I'd say it wouldn't be acceptable to use second hand MCB's at all to be honest.
 
I'm really only interested in domestic MCBs, so mostly type B, but even then I know I don't have the current to test at 5x rating for the higher values like 40A or 32A. The post was more to ask is anyone actually doing any testing at all in these circumstances, and if so, what.
 
For smaller MCB's like 1A - 10A you could just apply an appropriate load and test the curve of the thermal operation, for larger values you'd need to invest in a current injection unit. Problem is though you won't be able to test the disconnection times of the mag operation under fault conditions.

I'd say it wouldn't be acceptable to use second hand MCB's at all to be honest.

I really don't like to use second hand MCBs (it is rare that I do), and I certainly don't like the thought of using one without at least some testing.

You can find a huge number for sale on the likes of eBay. Some sellers describe them as removed from a working board, occasionally a seller will say they are tested but whether that is actually the case or not is difficult to verify. There must be people out there buying and using these, or they wouldn't be the market there is for them.
 
And how would you measure the trip time with any reasonable amount of accuracy?!
1: assume they'll operate as specced
2: don't buy 2nd hand gear that you don't know its history
 
I have used a second hand breaker once to feed a sub board for a shower, the board was too old and had to go down the used route, only option, I'd prefere not to, but sometimes you have to.
 
....... occasionally a seller will say they are tested but whether that is actually the case or not is difficult to verify.
I don't see that helping you if there's ever a comeback because one of them failed to operate when it mattered. If they'd been tested to any relevant standard they'd come with a certificate.
 
You would need a primary injection set or a decent MCCB/Breaker tester to fully test a MCB with any accuracy, and as someone has already pointed out, they DON'T come cheap!!

Have a look in ''Test Meter'' product range, you'll probably find one or two lurking around in there.
We use the Megger PCITS 3000-2 (comes in 2 sections) to test our ACB/GCB's's and current relays etc, and that cost around £10K 6 or so years ago. We made up our own current test leads, or you'll be paying something like £1.5K per lead (£3k for both)!! Expensive business what, but you will get 5% discount from our sponsor!! lol!!

So best policy is, if you suspect a malfunctioning MCB, replace it with a new one for the cost of a few quid, you know it makes sense!!.... lol!!
 
Last edited by a moderator:
You would need a primary injection set or a decent MCCB/Breaker tester to fully test a MCB with any accuracy, and as someone has already pointed out, they DON'T come cheap!!

Have a look in ''Test Meter'' product range, you'll probably find one or two lurking around in there.
We use the Megger PCITS 3000-2 (comes in 2 sections) to test our ACB/GCB's's and current relays etc, and that cost around £10K 6 or so years ago. We made up our own current test leads, or you'll be paying something like £1.5K per lead (£3k for both)!! Expensive business what, but you will get 5% discount from our sponsor!! lol!!

So best policy is, if you suspect a malfunctioning MCB, replace it with a new one for the cost of a few quid, you know it makes sense!!.... lol!!

Every little helps!!
 
You would need a primary injection set or a decent MCCB/Breaker tester to fully test a MCB with any accuracy, and as someone has already pointed out, they DON'T come cheap!!

Have a look in ''Test Meter'' product range, you'll probably find one or two lurking around in there.
We use the Megger PCITS 3000-2 (comes in 2 sections) to test our ACB/GCB's's and current relays etc, and that cost around £10K 6 or so years ago. We made up our own current test leads, or you'll be paying something like £1.5K per lead (£3k for both)!! Expensive business what, but you will get 5% discount from our sponsor!! lol!!

So best policy is, if you suspect a malfunctioning MCB, replace it with a new one for the cost of a few quid, you know it makes sense!!.... lol!!

Clunk clik every trip
 

Reply to Testing MCBs in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Is there a room in professional PAT testing for a business model other than 'per unit'? I ask because I've been giving this some thought. I've...
Replies
40
Views
9K
We’ve had a few power glitches/cuts recently by our supplier. Each time, on power restoration our RCD has tripped. Irritatingly we were on holiday...
Replies
56
Views
19K
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K
Well I'm am out of the training game for a bit.. I've got a couple of work offers but I am basically whoring myself out to whatever is paying for...
Replies
29
Views
5K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock