I’m currently doing some testing on some site temps I have a three phase trip system the tails from the head go into a 100 amp RCD which feeds a board I’m trying to do a pfc on the db but it comes up with 2 lead high which trips the RCD I tried on 2 lead low however came up with 20 amps which didn’t seem right what’s the best way to get round this
 
Last edited:
Can't you get to the RCD input terminals with your probe?

The low current / non-trip results are often not that accurate, but 20A is very suspiciously low even for that.
 
If you can access the RCD input terminals then you can conduct a high current loop test. Some RCD's can cause uplift which skews the results of your test.
That does seem low is this a TT supply by any chance?
If so what are your Ra / Ze readings? Quite high I would guess!

If you can get an accurate measurement at the RCD then you could take an R2 or R1+R2 from the next unit along and calculate the PFC/ Zdb from that.
 
I could try and get to the RCD Input terminals just wanted to check it in the atchual DB aswell would it make to much difference taking the reading at the RCD ?
In the ideal world the RCD would make no difference as it should be only milliohm contact resistance at most, so your result should be dominated by the supply characteristics.

However, RCD have a sense coil designed to pick up the Earth fault current and that can lead to "RCD uplift" where the measurement of PFC is fooled by the differential sense transformer leading to an unrealistically low PFC / high Ze/Zs result. I thought most modern MFT or similar had tricks to reduce this effect but a check on the RCD input should show you a realistic value.
 
My Megger 1741 is supposed to have that ability, but recently whilst testing some old BG type AC RCDs found that it doesn't always work as it should!
 
When I set it to L - PE on the settings it comes up with 2 Lead High but this would trip the RCD it did have a 2 lead low but the reading didn’t seem right when I tried this setting only just got this tester so trying to figure it out

2 lead low current test should be a last resort as they are notoriously bad for uplift. Use a 3 wire low current test for a better chance of getting the right result.

You should be using the tester to carry out the tests you want, not letting the tester dictate what you are doing.
 

Reply to Testing PFC on a three phase board with 100 amp From the meters tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
875
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
379
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Where do people record the Ze & PFC of a 3 phase installation, if there is say 10m of 25mm tails between the 4 pole isolator (next to the meter)...
Replies
7
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
309

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock