Of course I know it's done, but I'd almost consider thay a slightly greater risk than omitting an R1+R2 - especially if there's evidence of recent periodic testing.
It's particularly important to ensure that ADS (automatic disconnection of supply) will occur under fault conditions. The only way to be sure is to know that the CPC path has a sufficiently low impedance to allow enough current to flow to trip the protective device.

Worst case - no IR testing so you don't know you have a N-E fault in your new section, no R1+R2 testing so you don't know you have no earth path back, and you could end up with metalwork that's gives someone a shock if touched.

If I had an EICR showing a circuit was recently in fine health, and a board that was particularly problematic to work on for any of a number of reasons, at an absolute minimum I might do a live Zs before I start on the unmodified circuit, IR the new section, and do a live Zs when I finish. This at least tells me that there is earthing and no cable faults in my addition/alteration.
I'm not encouraging this sloppy practise but it's better than no testing at all.
 
Evidence of an EICR means little unless you have access to the Report. The cìrcuit you are working on may have Code 2 issues.
 
It's particularly important to ensure that ADS (automatic disconnection of supply) will occur under fault conditions. The only way to be sure is to know that the CPC path has a sufficiently low impedance to allow enough current to flow to trip the protective device.

Worst case - no IR testing so you don't know you have a N-E fault in your new section, no R1+R2 testing so you don't know you have no earth path back, and you could end up with metalwork that's gives someone a shock if touched.

If I had an EICR showing a circuit was recently in fine health, and a board that was particularly problematic to work on for any of a number of reasons, at an absolute minimum I might do a live Zs before I start on the unmodified circuit, IR the new section, and do a live Zs when I finish. This at least tells me that there is earthing and no cable faults in my addition/alteration.
I'm not encouraging this sloppy practise but it's better than no testing at all.
Genuine question here - and I'm probably missing something obvious. You say no R2+R2 means no proof of earth back - surely a Zs measurement within the specification of the device proves there is?

Again I may be missing something here...
 
Genuine question here - and I'm probably missing something obvious. You say no R2+R2 means no proof of earth back - surely a Zs measurement within the specification of the device proves there is?
A Zs certainly gives a strong indication all is well which is why I suggested doing this if a board truly can't be worked on. That said...

An R1+R2 is proving good connections and path along a specific CPC.
A live Zs test can prove there is a path back, but it could well be via metal trunking, bonding and a copper water pipe.
But as above, it gives some reassurance and is a lot better than nothing.
 
A Zs certainly gives a strong indication all is well which is why I suggested doing this if a board truly can't be worked on. That said...

An R1+R2 is proving good connections and path along a specific CPC.
A live Zs test can prove there is a path back, but it could well be via metal trunking, bonding and a copper water pipe.
But as above, it gives some reassurance and is a lot better than nothing.
Thanks. This really has been useful. Can definitely see the pitfalls to relying on live Zs. I think I'll get cracking on writing up some procedures.

In the meantime there's a few jobs coming up on site - mainly adding some FCUs for door controllers. All fed from small MEM2 boards. Think I'll undertake full testing of these to give me some support in my studies. Thanks for the help as ever guys.
 

Reply to Testing when modifying a circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
919
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
671

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock