It's particularly important to ensure that ADS (automatic disconnection of supply) will occur under fault conditions. The only way to be sure is to know that the CPC path has a sufficiently low impedance to allow enough current to flow to trip the protective device.Of course I know it's done, but I'd almost consider thay a slightly greater risk than omitting an R1+R2 - especially if there's evidence of recent periodic testing.
Worst case - no IR testing so you don't know you have a N-E fault in your new section, no R1+R2 testing so you don't know you have no earth path back, and you could end up with metalwork that's gives someone a shock if touched.
If I had an EICR showing a circuit was recently in fine health, and a board that was particularly problematic to work on for any of a number of reasons, at an absolute minimum I might do a live Zs before I start on the unmodified circuit, IR the new section, and do a live Zs when I finish. This at least tells me that there is earthing and no cable faults in my addition/alteration.
I'm not encouraging this sloppy practise but it's better than no testing at all.