Discuss The Ring is dead, long live the Radial!⚡ in the UK Electrical Forum area at ElectriciansForums.net

In the US, the ring circuit is a totally different concept to me, everything is wired radial.

As I investigated this, it seems it's used to insure proper voltage & amperage depending on where the home is located in proximity to a power station.
Am, I correct?

Stateside, using a ring circuit, the issue would be to make sure it's connected back to the correct leg @ CU (panel)! If not, that'd be a dead short.
the purpose of a ring is to share the load between both legs. e.g. cable rated at 27A (2.5mm in UK) with a ring circuit it almost doubles the current capacity. at the mid point a 30A load will share current 15A each leg. so cable is not overloaded. at other points on the ring, the sharing is proportional to the respective lengths of each leg. near 1 end, the short leg will carry more current than the longer leg, due to lower resistance.
 
You forgot the black pud but I'll let you off ?
but i don't like black pudding. diane abbott is labour. my political leanings are slightly to the right of maggie thatcher, (God bless).
 
Not sure if you were addressing my point or not but the separate circuit requirements for a fixed load over 2KW can be found in Annex 55A, Final Circuit Arrangements (Normative), 4th Ed., page 306
Thanks
In the interests of equality and diversity what about white pudding:D:D
BPM Black Pudding Matters
 
Or a red pudding?
Or a smoked sausage?
We have to cater to all tastes here!
all tasres maybe, but not the vegans. they originate from the planet Vega and are aliens beyond our comprehension.
 
You must be thinking of the Italians.

As the regulation restrict the amount of MCB's per RCD (eight) and the requirement to have separate radials for most white goods and other items the amount of RCD's soon mount up and lets face it we in the UK where very late in realising we should have two.
 
Last edited:
Wouldn't have made any difference anyway, the Gerries were behind them as well.....so much for the magnificent Maginot line.....we'll just go round it. :(
Maginot Line was a waste of time. they should have built it as a ring, not a radial.
 
Well at least there was a strong Resistance, must have been a circuit of some sort.
you need to speak to Rene about the resistance... listen carefully. I shall only say this once.
 
Are you mistaking multimeters for the Multi Function Testers (MFT's) we use for installation testing, we still use the standard multimeters but these are not capable of carrying out the tests needed to verify an installation

You've got a good point, can't do a megohm test with a multimeter.

To be more specific, as an electrician (installer), we're not required to do these loop tests, megohm tests on houses, last I knew anyway. I have been required to do these in factories for certain circuits as well as for feeders. On some jobs, ie: power plants, chip fab plants; we did have crews "commissioning" EVERY circuit, including feeders.
 
You've got a good point, can't do a megohm test with a multimeter.

To be more specific, as an electrician (installer), we're not required to do these loop tests, megohm tests on houses, last I knew anyway. I have been required to do these in factories for certain circuits as well as for feeders. On some jobs, ie: power plants, chip fab plants; we did have crews "commissioning" EVERY circuit, including feeders.
There is a very strong requirement here for dead testing before the circuit is energized, both for a full installation and for simply adding a new circuit to an existing system. That applies for domestic, commercial and industrial stuff.

Not just IR testing to see if the cable is OK, but also testing R1+R2 (live and earth resistances) both to verify socket & SP switch polarity, and also from the boards Ze (earth loop impedance) to check the circuit's Zs value is going to allow fast enough disconnection by the choice of fuse or MCB, etc.
 
There is a very strong requirement here for dead testing before the circuit is energized, both for a full installation and for simply adding a new circuit to an existing system. That applies for domestic, commercial and industrial stuff.

Not just IR testing to see if the cable is OK, but also testing R1+R2 (live and earth resistances) both to verify socket & SP switch polarity, and also from the boards Ze (earth loop impedance) to check the circuit's Zs value is going to allow fast enough disconnection by the choice of fuse or MCB, etc.
Me thinks they do things slightly differently in the US. Might be wrong.
 
Radials are usually quicker to install and quicker to test - so cheaper on labour, material wise breakers are same price and cable works out about the same or actually cheaper without the return leg.(Eg 30m of 4mm or 60m of 2.5mm) I do mainly commercial and use 25a 4mm radials a lot for runs along store walls etc. Also wiring rings in singles in containment is a massive pain to keep the right “leg” together and also twice as many drums to get tangled up and wrapped round your ladders ? rings have there place still, probably make more sense in houses and offices kitchens etc
 
When we buy a house later this year .I am doing a radial rewire . Might mean a huge consumer .But if possible will make every room radials etc
 
When we buy a house later this year .I am doing a radial rewire . Might mean a huge consumer .But if possible will make every room radials etc
my preference is rings for kitches/utility rooms. 2-3 radials for rest of house. (average house, not a mansion).
 

Reply to The Ring is dead, long live the Radial!⚡ in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
344
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
813
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock