Discuss Three-phase circuit breaker size calculation help in the Australia area at ElectriciansForums.net

I know this is an old thread but i had a similar problem at work and i cant work out how the motor vendor did his calculation .is there any good online calculators , the motor was a 55kw 400v 3 phase pf .81 squirrel cage motor DOL and the vendor said 60amp????
 
Then is the C type 50 amp Breaker suitable for Zs of the circuit ? As it seems if a C wont work then change it for D type is so common without any regard for the supply cable size or starter/ overload ect. As long as it works !
i had to listen to this kind of thing a while back of ov someone in the wholesalers

it was a walk in fridge that kept tripping the MCB at a resteraunt...

so this fella comes in asking for a 16A d curve MCB.....eh i thought....to feed a chuffin fridge...
so i asks him what the Zs was....he didn`t know....hadnt measured it....
good start methinks..

anyway...
his argument was that the chef was going nuts over this fridge tripping out....so he was going to install this d curve..to `eliminate the problem`..and to `cover his back`...
christ...

i explained to him that he would be better `covering his back`..by ensuring he met disconnection times

didn`t listen...off he tootled to fit it

saw him again about a week later....same topic...same wholesalers..

turned out that someone had swapped the 16A MCB for a 6A...and that was the reason it was tripping...

he hadn`t even bothered to look at the rating of the existing MCB before this `upgrade`...

well. it take allsorts......i suppose
 
Last edited:
i had to listen to this kind of thing a while back of ov someone in the wholesalers

it was a walk in fridge that kept tripping the MCB at a resteraunt...

so this fella comes in asking for a 16A d curve MCB.....eh i thought....to feed a chuffin fridge...
so i asks him what the Zs was....he didn`t know....hadnt measured it....
good start methinks..

anyway...
his argument was that the chef was going nuts over this fridge tripping out....so he was going to install this d curve..to `eliminate the problem`..and to `cover his back`...
christ...

i explained to him that he would be better `covering his back`..by ensuring he met disconnection times

didn`t listen...if he tootled to fit it

saw him again about a week later....same topic...same wholesalers..

turned out that someone had swapped the 16A MCB for a 6A...and that was the reason it was tripping...

he hadn`t even bothered to look at the rating of the existing MCB before this `upgrade`...

well. it take allsorts......i suppose

are you one of these people who argues in the wholesales?
 
Well, at the moment your waiting for some poor unsuspecting soul to come on the forum so you can ambush them, as you have put in your other post, and you know your stuff. I'm not taking the pee or anything I love watching arguments in the suppliers.
 
I'm sure its only ever constructive criticism right Glen?
oh aye...

just thought it a bit disconcerting that this fella thought it was cosha to start altering the characteristics of a circuit...

without consulting BS7671, looking at the existing to verify or getting some values first to confirm what he was going to do was acceptable...

very strange...
 
......
night-of-the-living-thread.jpg
 
Kilowatts to amps (A) conversion calculator plenty calculators here Strange how he got to 60 amp when closer to 100 amp would be the answer.
Welcome to the Forum John, if you wish to divulge your Electrical level (DIY, Trainee, fully qualified etc) we can give you access to the relevent areas of the forum to suit, if not then enjoy anyway you'll be made more than welcome.
 
Good day Guys

Read all the comments. Similar issue, I have a 32A MCB Hager NF332A for battery charger to charge Airplane Luggage Tuggers. Recently been tripping out a lot, measured and found 25A on each phase. Nothing has changed but the vendor purchased new units. so my calculation as per root3 method comes to18,475A max, which would explain the tripping. to fix this i would need a 43,3A minimum which i would need a 50A breaker. this really seems like too much and i am thinking we going to burn the cabling or connection points as they are all rated at 32A.

As per your guys comment the 32A should be sufficient to keep the 25A load, as is. Might be something else causing the trip?
 
So, your saying a three-phase circuit breaker say 32 amp is actually 3x32amp MCBs fitted together?
i am highly thinking this is the case. As per the OEM (Technical Properties NF332A - https://www.africa.hager.com/nf/products/energy-distribution/protection-devices/miniature-circuit-breakers/mcbs-ne-nf/nf332a/20543.htm) its rated at 32A not specifying whether its per phase or not. i do not think they will design a unit that first needs calculation to install. opens up for too many ways for error. so i am with you on this one. would of been great to hear from someone working at breaker OEMs
 
Good day Guys

Read all the comments. Similar issue, I have a 32A MCB Hager NF332A for battery charger to charge Airplane Luggage Tuggers. Recently been tripping out a lot, measured and found 25A on each phase. Nothing has changed but the vendor purchased new units. so my calculation as per root3 method comes to18,475A max, which would explain the tripping. to fix this i would need a 43,3A minimum which i would need a 50A breaker. this really seems like too much and i am thinking we going to burn the cabling or connection points as they are all rated at 32A.

As per your guys comment the 32A should be sufficient to keep the 25A load, as is. Might be something else causing the trip?
32A should be correct for a 25A load .. might need a C type, dependent on Zs and disconnection times being met. also check that cable size is sufficient for 25A. installation ref. methods may lead to derating of the cable.
 

Reply to Three-phase circuit breaker size calculation help in the Australia area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
844
I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...
Replies
5
Views
923
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
608
Hi , Currently doing a design project in college and I need to pick a circuit breaker ( In device rating and type) for a food holding equipment...
Replies
17
Views
3K
Hi, I'm a first year apprentice... just trying to get an edge on theory. Calculating breaker size: W ÷ V = A So say appliance needs 4000 watts...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock