You've a TN-C-S (aka PME) system and need to replace that 16mm T&E before worrying about anything else!
 
oh ok, is there a problem with that wire?
You'll need to consult with a reputable electrician to you, but in the U.K. that would not meet our regulations.
 
oh ok, is there a problem with that wire?
Years ago it would be OK, now it either needs to be replaced by armoured, or surface/contained, depending on how far it goes it may need local protection (such as fuses etc), it also looks a little small - depends on your fuse size but it will be a maximum of 80A
 
Years ago it would be OK, now it either needs to be replaced by armoured, or surface/contained, depending on how far it goes it may need local protection (such as fuses etc), it also looks a little small - depends on your fuse size but it will be a maximum of 80A
fuse is 63amp, so you mean that it would have to be on a metal earthed conduit? being concealed in the ESB box?
 
the last page of this Hager Tech datasheet mentions that RCCB is not permitted in PEN.
It is just as I suggested in #2. It's talking about PEN conductors - you don't have those in your system.

Your installation is not TN-C, it's TN-C-S. N & E become separate at the service head.

Aso this thread on the IET forum states that an RCD will not work on a PEN system: Electrical Blog - Electrical Advice | Free Electricians Advice Forum - https://electriciansforums.co.uk/discussions/viewtopic/1037/25035

regarding the comment you made about the type, being F perhaps more suitable for some circuits, I'd say that given all the modern equipment we have, (water pump, modern washing machines, dishwashers, and all the IT equipment) maybe even a type B may be more appropriated?
Unlikely - Type F will be OK for the sorts of loads you find in domestic installations, apart from EV charging points, but they're better off separated from the main house installation anyway.
 
fuse is 63amp, so you mean that it would have to be on a metal earthed conduit? being concealed in the ESB box?
There are multiple options, much depends on how long the run is from the isolator to the cu, and where it is, if it is surface, that is different from concealed; but yes, if it is concealed one option is a metalic conduit.

This work is controlled in Ireland, so you need a fully qualified person to do the work, and they will cover this aspect as much as the actual cu replacement.
 
There are multiple options, much depends on how long the run is from the isolator to the cu, and where it is, if it is surface, that is different from concealed; but yes, if it is concealed one option is a metalic conduit.

This work is controlled in Ireland, so you need a fully qualified person to do the work, and they will cover this aspect as much as the actual cu replacement.
I can see your point, the box was actually smashed to get the meter tails and the service cable, this is 1997... these houses were thrown together in a weekend, way overdue for an upgrade and an in-depth inspection, I will stop here, there are so many other aspects that would not be compliant with the latest regulations... I'm just afraid I'm going to have to rewire the whole house and it will cost me an eye and a leg ;-)

Thanks for your comments
 

Reply to TN-C-S (PEN) RCBOs Discussion in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
We have a customer in a large office block with all power in the building fed from an Electrak plug in busbar system. Lots of desks, lots of...
Replies
7
Views
603
I've tried to understand one way or another but this seems to be connected to the DNO fuse/cutout, and then loops down (out of sight) and comes...
Replies
2
Views
802
Hi All, I understand the requirement for PEN fault detection on EV chargers for TN-C-S installs (or to place an earth rod). However, when I was...
Replies
3
Views
1K
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top