- Reaction score
- 5,848
That sounds like a 32A Hager MCB which is most definitely not suitable for a 10.5kW shower, even if it really is 9.6W. It may not trip during the length of any normal shower session, but will routinely overheat, and suffer internal damage.Posted it above. Current fuse thingy-ma-jig says - "32amp MTN 110 6000 Hager fuse" - that OK for a 10.5kw shower?
It's not even suitable for the existing 8.5kW shower.