Good points....I wonder how compliance with that regulation could be verified on an EICR? It would be very difficult to gauge the depth of an electrode without digging it up!

Simple, it's exactly the same as checking any other test results on an eicr. Measure the value and compare it to the previous test results, then you can assess any change which may have occurred.
After all one of the fundamentals purposes of carrying out tests and recording the results is to identify changes and trends in changes of the results in order to predict and prevent failures and identify maintainence requirements.
 
If the value of the Ze is above the 200 ohms set by the guidelines but below the maximum permitted value of 1667,ensuring additional protection is correctly installed and operational (RCD) and thus compliant, the installation is perfectly safe to use.

I think a C3 would be reasonable code to note on the EICR. As a value greater than 200 would in theory require further investigation to ascertain stability.

One way to achieve this would be to test the Ze over a period of time under different environmental conditions and then compare the results. I doubt any of us would be in a position to do such monitoring, let alone the cost of such.
So one simple less costly solution would be to install additional rods... to try and achieve a value much less than 200 ohms.
 

Reply to TT High Zs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
531
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock