Hi Guys,

I have been testing for about a year and have come across my first tt system yesterday.


I disconnected the earth and tested for Ze and got 8.67 ohms which I believe to be a great reading as osg allows up to 200 ohms. I couldn't do a Ra reading as the rod is under the house and impossible to get to.

But when I'm doing all the earth loop tests on all the circuits I'm getting similar readings between 7ohms to 9ohms. As I havent tested this before and not really sure on it I dont know what im doing wrong, what the problem is and how to fix it? So any help would be great if possible.

Many thanks.
 
Probs getting better connection with parralel paths from water and gas assuming main bonding is present. That's if readings are lower. As monkey said there usually very close anyhow. What were you expecting?
 
There's nothing to fix tho. You have confirmed your reading complies and there is external earth. Note figures on cert and move on. Simples.
 
All circuits on a TT must be protected by an RCD so that earth faults will cause disconnection, a L-N fault will disconnect the MCB but a L-E fault will only disconnect the RCD. The RCD only needs 30mA and you would have about 29A with that Zs.
 
Hi Guys,

I have been testing for about a year and have come across my first tt system yesterday.


I disconnected the earth and tested for Ze and got 8.67 ohms which I believe to be a great reading as osg allows up to 200 ohms. I couldn't do a Ra reading as the rod is under the house and impossible to get to.

But when I'm doing all the earth loop tests on all the circuits I'm getting similar readings between 7ohms to 9ohms. As I havent tested this before and not really sure on it I dont know what im doing wrong, what the problem is and how to fix it? So any help would be great if possible.

Many thanks.

That's an impressive Ze on TT - did you disconnect the water and gas bonding?
 
I mean no disrespect to Adamdee because you only experience whats in front of you,this is a general forum moan

The amount of threads that contain very confused folk in this subject is very surprising.
It would seem to be essential to obtain this understanding
,I am sorry to say a TT system is well documented type,its in all the books and should be understood even if it has not been experienced
 
I mean no disrespect to Adamdee because you only experience whats in front of you,this is a general forum moan

The amount of threads that contain very confused folk in this subject is very surprising.
It would seem to be essential to obtain this understanding
,I am sorry to say a TT system is well documented type,its in all the books and should be understood even if it has not been experienced

But rarely taught
 

Reply to TT System testing and results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
974
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Hi How do i access the earth rod to service it, where abouts will it be located and does a tt system have upfront rcds which will be probably in...
Replies
3
Views
983

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock