Discuss Tumble Dryer Tripping Rcd in the Electrical Appliances Forum area at ElectriciansForums.net

M

Marc13

I have a 3 month old condensing tumble dryer, which has recently started tripping out the RCD (63A, 30mA) within 30 secs of being on. I've tested the RCD, which was going out at 18mA, and the tumble has an earth leakage of 1.17mA. I have now changed the RCD, but still continues to trip, within about 5 mins of running this time though. Any advice? Should I contact the manufacturer?
 
was going to edit my post, but as you beat me too it haha, considering the age I would return the product as faulty if the RCD is tested as okay, thanks Dillb
 
I have a 3 month old condensing tumble dryer, which has recently started tripping out the RCD (63A, 30mA) within 30 secs of being on. I've tested the RCD, which was going out at 18mA, and the tumble has an earth leakage of 1.17mA. I have now changed the RCD, but still continues to trip, within about 5 mins of running this time though. Any advice? Should I contact the manufacturer?

Mine stared doing that, then a couple of weeks ago it caught fire.

I've cleaned it up now & given it to Tidy Boiler .............
 
Probably an element issue but dosn't show until its heated up... its within warranty so as already stated return the goods as faulty, you could confirm by bypassing rcd and clamping leakkage as it runs, you'll probably find it suddenly rises enough to cause a trip.
 
I had a similar problem with an Indiset conenser drier. When the condenser had filled with fluff etc, water would leak in to a resivoir in the bottom of the drier. Over time the resivoir would overflow. The drier fan would then flick the excess water into the heater element, causing a short and tripping the rcd. All I did was clean the condenser, removed the panel from the back of the drier, and dried out the element with a hair drier. Following this, I put an rcd plug on the drier and clean the condenser out monthly. The problem has not occured again.
 
If there's nothing wrong with the appliances you may have to run it off its own dedicated circuit...that's if its not on one?

I could be leaving myself open to some abuse here(ref:am1)....could you not surface run (trunking) a new feed without RCD protection aslong as you label the circuit not RCD protected?
 
wonder whether i should return my condenser dryer under warranty. got it from the council tip 3 years ago for £2 in the lads' tea kitty. filter's a bit iffy now.
 
If there's nothing wrong with the appliances you may have to run it off its own dedicated circuit...that's if its not on one?

I could be leaving myself open to some abuse here(ref:am1)....could you not surface run (trunking) a new feed without RCD protection aslong as you label the circuit not RCD protected?

but it's more than likely faulty and only 3 months old, best to send it back.
 
Why not pat test it, this the only procedure for light at end of tunnel and resolution to what you do next.
Pat engineers 1 electricians 0
 
Stop shooting me down when im trying to be intelligent :laugh:

to be fair, i forgot/misread about it being 3months old lol - what MDJ said, send the bloody thing back :biggrin:
Do you usually have an habit of loading the enemies gun.... i would hope you are intelligent rather than trying to be ;)
 
Last edited:

Reply to Tumble Dryer Tripping Rcd in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
577
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
793
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock