Discuss Type of earthing system? in the UK Electrical Forum area at ElectriciansForums.net

newfutile

-
Esteemed
Arms
Supporter
Reaction score
388
What type of earthing system is this?
 

Attachments

  • 7B6B5761-96A8-4078-9C0F-E061CF154FDC.jpeg
    317.4 KB · Views: 92
This one causes confusion
SNE = separate neutral and earth
The sticker looks fairly recent and I’d put a fiver on TNS
Last time I had this I measured pscc and pefc and found them sufficiently different to conclude it was certainly TNS.
 
Unlike the old TN-S supply cables we expect to see modern SNE supplies will use split concentric cables.
 
I was about to say splitcon? In which case you may not detect difference.
I guess next thing is to look at reasons it might mattter since you are below tncs threshold anyway.
Is main earth/bond at least 10mm?
Any relevant special locations or car charger about to be installed?
I see no reason not to believe the sign anyway!
 
Is this in a flat as the red fuse holder would suggest it's a solid link and it's fed from a Ryefield or similar distribution set up
Could be like my flat: TN-S at the head (red link) but seems to be TN-C-S at the Ryefield (actually Lucy) board down in the hallway.

Determining TN-S or TN-C-S by measurement is hard to do. If the PEFC is much lower than the PSCC then it is clear, but on split con cable back to some linked point both N & E are often identical conductors so your measurements will be very similar.

If you have a low-ish PFC, so Ze in the 0.3 ohm or more region, then you have a sporting chance of measuring N-E resistance (with care, power off but at input of isolator, MET not bonded to avoid links via service pipes, etc) to see if it is comparable to Ze (so a long length of N linked to E way back and similar to the estimated L distance/impedance). If you get near-zero then it is clearly linked at the cut-out! Here having Ze near 0.1 is surprisingly low hence my original though about where the N-E link really is (as it is always linked somewhere/somehow).

But as I found in my flat being TN-S at the cut-out is no guarantee that are not really on a PME supply. However, they say SNE so TN-S and unless it is ground floor for EV charger, etc, it is simpler just to go with that!
 
They are flats fed from a Lucy board i am conducting an EICR for the communal areas , just wondered what box to tick ? Although i have been told almost everything is PME at some point these days.
 
The notice label to the right of the cut out says PME
 

Reply to Type of earthing system? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, How do you think reference method and type of wiring for flat twin and earth in non-metallic conduit will be : just C and B...
Replies
2
Views
234
Hi All, As mentioned, I’ve got what looks like a TNCS system but CPC is coming via an earth rod???? Not tested TNCS system yet to see if earthing...
Replies
9
Views
661
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
341
See attached photo of my new 3 phase supply at my house. Tails supply a Schneider 3ph board. Sparky is in two minds about the correct earthing...
Replies
11
Views
578
2 questions.. 1. Will the mini Starbreaker RCBO's fit in this board? Below is a picture of the board and also the type of RCBO I want to fit in...
Replies
3
Views
348

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock