Gavin John Hyde

-
Esteemed
Arms
Patron
Reaction score
5,173
I tend to run a mile from underfloor heating as its a pain in the backside to put right if it goes wrong.
Got a regular customer whose old manual thermostat has died, power goes to it, but nothing else, its dead. Tested resistance of the heat mat and the values pretty much same as paperwork when installed.
Being a basic manual one, from my limited UFH experience then any other manual one should work? after all it only has Live and Neutral from supply, CPC terminates on back. then live out to mat, neutral out to mat, with 2 wires for the sensor down through conduit.
Anybody got any thoughts?
pic shows current one. I shall be hoping to replace with another one of same ilk. albeit newer.

stst.PNG
 
I can't say for certain as I don't have much experience with UFH, but I suspect the temperature sensing element and the thermostat itself may need to be matched.

There are a few methods of sensing temperature electronically, some purely resistive (like thermistors - which have different temperature curves and values) and some semiconductor based which operate in an entirely different way.
 
I can't say for certain as I don't have much experience with UFH, but I suspect the temperature sensing element and the thermostat itself may need to be matched.

There are a few methods of sensing temperature electronically, some purely resistive (like thermistors - which have different temperature curves and values) and some semiconductor based which operate in an entirely different way.
I think that is why a lot of the thermostats available come with the probe/thermal sensor aswell, to ensure compatibility. It relies on the original install to have installed a conduit or pipe run to be able to slide it down or into the floor..
Electrically speaking it is straight forward, just a nightmare to fix as it can mean ripping the floor up!
 
or buy a stat that is capable of sensing room temp. this would normally be set lower than you'd expect as ufh is generally to keep your tootsies warm, not heat a room.
 

Reply to Underfloor heating thermostats in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Got to look at a job where the builder has cut through the underfloor heating mat and it’s gone right through the heated cable. Not...
Replies
3
Views
746
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
665
m having a bit of an issue that is proving difficult to resolve. For 2 years I have been having no problems with my setup. I have a 3 zone house...
Replies
1
Views
1K
I'm after some advice please, I have carbon mat underfloor heating throughout my bungalow, each room has its own thermostat and are fed via a...
Replies
1
Views
792
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
997

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock