Discuss UPS spec - help required. in the UK Electrical Forum area at ElectriciansForums.net

DPG

-
Esteemed
Arms
Patron
Reaction score
16,681
Morning all, and happy Friday!

I've been asked my advice on what UPS would be suitable to run an ICT machine (ICT=In Circuit Test, it's machine that tests electronic PCB assemblies).

Now it is fed from a standard 3 phase supply, but I am confused a little by the rating plate - I've attached a picture (hopefully!) of the plate. Looks like it will need a standard 3 phase UPS rated at 35A, but the lower part of the spec plate shows 220V 18A, even though the 3 phase box is ticked.

Any thoughts? Apologies if my inexperience on these things is showing!

Cheers,
Daz

View attachment 35599

View attachment 35600
 
Yeah, that's confusing.

Can you get them to run it up and put a clamp on around each line? (Or how many phases you find when you open it up.)
 
Last edited:
....and the last time I had to spec a UPS I just called APC UK. Got them to do the donkey work.

That's some serious cash though, especially if the machine needs to finish its full cycle. Could be a long run time at high load.
 
Last edited:
I'd say the top half of the plate shows possibilities and maximums whilst the bottom half shows 'as configured'.

But I agree with @LeeH clamp it to confirm and get APC doing the donkey work for you. I've found them very helpful in the past when I've had to source server room UPSs.
 
....and the last time I had to spec a UPS I just called APC UK. Got them to do the donkey work.

That's some serious cash though, especially if the machine needs to finish its full cycle. Could be a long run time at high load.

Yeah I imagine it's going to cost some. Will get them to ask APC I think. Cheers.
 
I'd say the top half of the plate shows possibilities and maximums whilst the bottom half shows 'as configured'.

But I agree with @LeeH clamp it to confirm and get APC doing the donkey work for you. I've found them very helpful in the past when I've had to source server room UPSs.

I think you are probably right - didn't expect such a big difference in the 2 figures though. I will get them to see what APC say - should be easy enough for them eh!

Cheers,
Daz
 
At those sort of loads it might be a UPS and backup generator depending on the run time and resilience required

There's a backup genny but the machine drops out and has to go through a re-start process before the genny can start up. Often get short duration drop-outs (a bit out in the sticks!). UPS wouldn't need to run for more than 10 minutes I reckon.
 
Already read it :) It still didn't clarify the spec plate completely though, unless I didn't read it properley!

Daz
 
There's a backup genny but the machine drops out and has to go through a re-start process before the genny can start up. Often get short duration drop-outs (a bit out in the sticks!). UPS wouldn't need to run for more than 10 minutes I reckon.
Changes the OP a bit then, having said that is the generator man enough to run what is connected to it seen a lot of sites expand beyond the generators capability and one of them was a hospital
 
Changes the OP a bit then, having said that is the generator man enough to run what is connected to it seen a lot of sites expand beyond the generators capability and one of them was a hospital

Yes, the genny is up to the job and has a suitavbly large fuel reservoir.
Daz
 
Morning all, and happy Friday!

I've been asked my advice on what UPS would be suitable to run an ICT machine (ICT=In Circuit Test, it's machine that tests electronic PCB assemblies).

Now it is fed from a standard 3 phase supply, but I am confused a little by the rating plate - I've attached a picture (hopefully!) of the plate. Looks like it will need a standard 3 phase UPS rated at 35A, but the lower part of the spec plate shows 220V 18A, even though the 3 phase box is ticked.

Any thoughts? Apologies if my inexperience on these things is showing!

Cheers,
Daz

View attachment 35599

View attachment 35600
Are talking about a "no break" setup?
 
It doesn't tolerate 'unclean' mains failures and has suffered before causing production down time (ÂŁÂŁÂŁ).
I've also suggested maybe some sort of power conditioning/surge arrestor.

Daz
 
It doesn't tolerate 'unclean' mains failures and has suffered before causing production down time (ÂŁÂŁÂŁ).
I've also suggested maybe some sort of power conditioning/surge arrestor.

Daz
You require a "floating" system which means it will be permanently using the ups output so there is no loss on mains failure.
 

Reply to UPS spec - help required. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Hello, I'm seeking some advice on an overheating plug adaptor please. Complete amateur so please forgive any errors in calcs / assumptions /...
Replies
6
Views
973
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
Evening all.. A friend/customer has just asked if I could connect up this commercial washing machine down at his domestic stables. He has had it...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock