Discuss ***Useful Information For The Working Sparky*** in the Australia area at ElectriciansForums.net

FOR DESIGN, CONSTRUCTION, INSPECTION & TESTING : ;)

I being the person responsible for the Design, Construction, Inspection & Testing of the electrical
installation (as indicated by my signature below), particulars of which are described above, having
exercised reasonable skill and care when carrying out the Design, Construction, Inspection & Testing,
hereby CERTIFY that the said work for which I have been responsible is to the best of my knowledge
and belief in accordance with BS-7671:2008 , amended to .............(date) except for the departures, if any, detailed as follows ,

(vi) A Minor Works Certificate will indicate the responsibility for design, construction, inspection and testing of
the work described on the certificate.
(vii) A Periodic Inspection Report will indicate the responsibility for the inspection and testing of an installation
within the extent and limitations specified on the report.
(viii) A Schedule of Inspections and a Schedule of Test Results as required by part 6 should be issued with the
associated Electrical Installation Certificate or Periodic Inspection Report.
(ix) When making out and signing a form on behalf of a company or other business entity, individuals should
state for whom they are acting.
(x) Additional forms may be required as clarification, if needed by ordinary persons, or in expansion, for large
or more complex installations.
(xi) The IEE Guidance Note 3 provides further information on inspection and testing on completion and for periodic inspections ,

ELECTRICAL INSTALLATION CERTIFICATES NOTES FOR FORMS 1 AND 2 :
1. The Electrical Installation Certificate is to be used only for the initial certification of a new installation or
for an addition or alteration to an existing installation where new circuits have been introduced.
It is not to be used for a Periodic Inspection, for which a Periodic Inspection Report form should be used.
For an addition or alteration which does not extend to the introduction of new circuits, a Minor Electrical
Installation Works Certificate may be used.
The "original" Certificate is to be given to the person ordering the work (Regulation 632.1 . A duplicate
should be retained by the contractor.
2. This Certificate is only valid if accompanied by the Schedule of Inspections and the Schedule(s) of Test
Results.
3. The signatures appended are those of the persons authorized by the companies executing the work of
design, construction, inspection and testing respectively. A signatory authorized to certify more than
one category of work should sign in each of the appropriate places.
4. The time interval recommended before the first periodic inspection must be inserted (see IEE
Note 3 for guidance).
5. The page numbers for each of the Schedules of Test Results should be indicated, together with the total
number of sheets involved.
6. The maximum prospective fault current recorded should be the greater of either the short-circuit current or
the earth fault current.
7. The proposed date for the next inspection should take into consideration the frequency and quality of
maintenance that the installation can reasonably be expected to receive during its intended life, and the
period should be agreed between the designer, installer and other relevant parties

SCHEDULES (note 2)
The attached Schedules are part of this document and this Certificate is valid only when they are attached to it.
............ Schedules of Inspections and ............ Schedules of Test Results are attached
(Enter quantities of schedules attached)

GUIDANCE FOR RECIPIENTS
This safety Certificate has been issued to confirm that the electrical installation work to which it relates has been designed, constructed, inspected and tested in accordance with
British Standard 7671 (the IEE Wiring Regulations).
You should have received an "original" Certificate and the contractor should have retained a duplicate. If you were the person ordering the work, but not the owner of the
installation, you should pass this Certificate, or a full copy of it including the schedules, immediately to the owner.
The Certificate should be retained in a safe place and be shown to any person inspecting or undertaking further work on the electrical installation in the future. If you later vacate
the property, this Certificate will demonstrate to the new owner that the electrical installation complied with the requirements of British Standard 7671 at the time the Certificate
was issued. The Construction (Design and Management) Regulations require that for a project covered by those Regulations, a copy of this Certificate, together with schedules is
included in the project health and safety documentation.
For safety reasons, the electrical installation will need to be inspected at appropriate intervals by a competent person. The maximum time interval recommended before the next
inspection is stated on Page 1 under "Next Inspection".
This Certificate is intended to be issued only for a new electrical installation or for new work associated with an addition or alteration or to an existing installation. It should not
have been issued for the inspection of an existing electrical installation. A "Periodic Inspection Report" should be issued for such an inspection ,
The Certificate is only valid if a Schedule of Inspections and Schedule of Test Results are appended ,

Excess earth leakage ;)
The RCDs operating principle is to measure the current imbalance between that flowing into and out of a circuit down live and neutral wires. In an ideal world the current difference would be zero, however in the real world there are a various different types of equipment that will legitimately have a small amount of leakage to earth, even operating normally. If the RCD is protecting too many such devices then it is possible that the cumulative result of all these small leakages will be enough to either
• trip the RCD
• or by passing most of the RCD's trip threshold current, make the RCD excessively sensitive to any additional leakage currents
Appliances that typically exhibit high leakage currents
Dampness : Any device that handles water and electricity will be vulnerable to dampness getting into electrical connections or wiring harnesses. This can result in short term high levels of leakage that mysteriously vanish later (as the affected item dries out). Even condensation forming in equipment can cause this problem.

Split water heater elements. These cause gross earth leakage, and conduct it directly through the water being heated. Contrary to what we were taught about electricity and water in primary school, this does not cause electrocution in practice. Split elements can however cause overcurrent leading to overheating of electrical accessories.

DC Resistance tests : :rolleyes:
First ensure that power is switched off at the main switch. Ensure all appliances are disconnected from the circuit. These tests require that you disconnect the circuit under test from the consumer unit. In the case of a Ring circuit remember to disconnect both legs of the ring. All tests are initially performed on the disconnected ends of the circuit.
There are a number of basic tests that you can do that will identify a great many of the fixed wiring faults that can cause nuisance tripping.
Test :
Live / Neutral Resistance

Purpose :
The first test is a simple resistance test between live and neutral. This test should be done using the highest resistance range on your multimeter. Normally with all the appliances disconnected you would expect to see an open circuit between live and neutral. If this is not the case then you either have something still connected, or you have a serious insulation resistance problem.

Live Earth Resistance :
This test should also indicate an open circuit with the multimeter on its highest resistance measuring range. Any non infinite reading here could be a direct indication of your problem. If you get a non infinite resistance reading, you may be able to track down the location of the fault by breaking the circuit up at strategic points ( typically by disconnecting part of it at an accessory position ).
Again this test ought to indicate infinite resistance. However it is possible that a very low resistance measurement could exist and yet the circuit still work some of the time (especially on systems with TN-C-S Earthing ). Unlike a low resistance reading on a Live to Earth test, this fault would not immediately trip a MCB or blow a fuse .
Neutral Earth Resistance :
Tracing the location of the short or bridge can again be done using the segmenting procedure described above, and also by careful low resistance measurements made in conjunction with expected cable resistances (or see the table in the IEE Wiring Regulations On Site Guide ).
A typical cause of this type of fault, is where a concealed cable has been damaged by a fastening being driven through it. (so if any shelves or pictures have been hung recently, there is a good place to start looking).
 
Last edited by a moderator:
What is a TT Earth and why would I want one ? ;)
If you refer to the Earthing Types article you will see there are a number of ways that an earth can be provided for an electrical installation Of the available types TN-S and TN-C-S, where your electricity supplier also provide an earth, are by far the most common. The next most common category is the TT type. You will encounter this situation where the electricity supplier does not provide any connection to allow the installation to be earthed, or you are working on an electrical installation in an outbuilding where it was not appropriate to export the main earth . In either of these cases you are responsible for providing your own earth connection.
Since a TT earthing system will safeguard both lives and equipment it is important that a correctly designed system is installed. It should have:
* Low enough electrical resistance to earth to ensure correct operation of the circuit earth fault protection device ( typically a RCD ).
* Good repeatability (i.e. it should be able to carry fault currents repeatedly, and its performance should remain in spec all year round, irrespective of varying soil conditions)
* High resistance to corrosion ,
* Long life expectancy ,
Types of earth electrode :
The usual way to provide an earth is to place an electrode into the soil. There are a number of ways of doing this, and how well each of them will work will depend to a large extent on the local soil conditions.
Earth Rods or Spikes :
Earth rods are commonly used since they are easy to retrofit to properties and also work well for a relatively small overall rod area. A typical earth rod is 1.2m long and something like 9 to 14mm in diameter, and usually made from copper clad steel, solid copper, or sometimes stainless steel. This is driven into the ground and an electrical connection made to the top of it via an earth clamp. If the resistance achieved with one rod is too high, then most rods have a threaded section that will allow an additional one to be connected to it, and then that too driven into the ground. (Note that the overall length of the electrode has far more effect on the resistance than the diameter).
The connection to the earth rod should be protected with a suitable enclosure, and this must feature a warning label stating that "this is a safety electrical connection and should not be removed."
Driving an earth rod
The usual solution to this is to hit it with a hammer, and keep doing so until it is nearly all gone. However a modern and much simpler equivalent is to use a SDS drill set to hammer only (i.e. rotation stop) mode, fitted with a square drive adaptor and a socket. The socket will keep the drill centered on the spike and should allow you to "power drive" it into the soil.
For many rod sizes you may also obtain a "driving head". This is a cover that will protect the top end of the rod from damage while driving, which will be important if you need to attach and drive further rods to the first one.
You should choose a section of ground that is away from other service pipes and drains, and preferably is comprised of ordinary soil rather than builders rubble. This will not only make driving the spike easier, but will get a lower resistance electrode as a result.
If the spike hits something immovable and will not drive any further you may be able to pull it out and try elsewhere, or if you managed to drive mostly home before it stopping then it may be worth testing as is and cutting off the excess if the result is good enough. If one rod position on its own is not good enough then additional rods can be driven in other locations and "paralleled up" to lower the overall resistance.
It is wise to try an keep a few meters away from other rods so as not to overlap their resistance area (how far, will depend on how good a conductor the local soil is. The poorer it is the closer they can be together).

Earth Plates :
These are typically either solid copper plates, or lattice like plates made from copper rods. These need to be buried in suitable ground. They can not be "driven" later, and require excavation of soil to fit.
Alternative earth types :
Alternative systems are sometimes used such as earth tapes or wires that are run through long channels dug in the ground. Again difficult to retrofit, and not suitable for soils that require deep penetration to reach permanently damp and frost free conditions. There is also an earthing system constructed using the foundation slab of some building types called an Ufer Earthing
Quality of earth :
The quality of the earth obtained will depend to a large extent on the soil moisture content. Soils that stay damp all year round (like heavy clay) will often perform well in this context. You may need more than one rods length to reach the permanently damp soil.
Different soil types will affect the performance. Marshy ground will perform best, with loam, clay, peat and often chalk also working well when damp. Dry sand and rocky ground however can be much harder to get good results with.
Pay attention to temperature range as well. Frozen ground can be ten times less effective than warmer soil.
Soils with high mineral salt content in their moisture will usually perform noticeably better than "ordinary" damp soil.
Testing the electrode resistance :

The aim of the exercise is to achieve a reasonably low resistance path to earth. Usually with this type of earth it is unrealistic to expect to achieve a resistance as low as that you would get from a supplier provided earth (i.e. under 1 ohm), however it is usually easy to achieve a resistance well under 100 ohms, which when combined with a RCD will offer adequate protection.
When testing the resistance of an earth electrode it is important that any parallel connections to earth (such as main equipotential bonds to water or gas mains) are disconnected when the reading is taken. Note that this in itself raises a danger since some of the buildings equipotential zone will be disconnected, and any other occupants of the premises should be warned.
Without specialist test gear :
Anyone with a bit of electrical common sense, knowledge of Ohm's law, and a decent multimeter can measure earth electrode resistance quite easily. You need to isolate the electrode in question and then find a way of getting some current to flow into it. A safe way to do this is to use a double-wound mains transformer with a secondary voltage of around 24V (exact value not critical).
Exactly how you wire this up will depend on the circumstances. If you have a TN system installation where you are adding an earth electrode for an outbuilding etc, then you can make use of your existing supplier provided earthing point as a return path: Connect one end of the secondary via a suitable length of wire to the main earth terminal in the house and connect the other end to your earth electrode via an ammeter.
Energise the primary of the transformer, and the secondary current which flows will immediately give you a rough idea of the total resistance in the circuit, most of which will be attributable to your electrode. For a more accurate result, drive a second temporary earth electrode (a 2ft offcut of 15mm water pipe will do) into the ground at a distance of 10m or more from the one you're measuring. Then use the meter on volts to measure the voltage drop between the two electrodes. Dividing this figure by the electrode current measured earlier gives you the earth resistance. (Reactance in the circuit will be negligible.) Move the temporary reference electrode to a second position and repeat. Average the two values obtained, but if they are significantly different, try further positions for the reference electrode.
If your whole installation is TT system to start with, and you need to measure the impedance of the main or a secondary electrode, then you will need to use another temporary earth connection as a return path. bash a bit of copper water pipe (or similar) into the ground as far away from the electrode under test as you can manage, and use that to complete the circuit. With this technique you must use the separate sensing electrode (a 2nd temporary rod) to establish a voltage reference. Put this one roughly half-way between the other two, and take measurements with it in two or three different places to check that the resistance areas aren't overlapping too much.
 
Last edited by a moderator:
This could mean the difference between life and death. Apprentice : ;)
We need to remember the following :-

1. When properly connected an electric current flows through the live wire on its way to the appliance and returns to ground via the neutral wire.
2. If for some reason the current “leaks” ( through dampness, frayed wiring, faulty connections etc ) the current will take the most direct path to earth – often through a person’s body. In this situation if the power is not disconnected instantly then there is a strong possibility that the person will die.
3. The path taken by the current also contributes to the severity of the electric shock. An electric shock which flows from the hand through the arms and to the chest will affect the breathing and heartbeat.
4. The greatest contributing factor to the severity of an electric shock is the exposure time to the current. An RCD cuts off the power in less than the time of a single heartbeat.
An RCD can be tested in two ways :-
1. A push button test – this requires no test instrument.
2. By the use of an RCD Tester – an RCD Tester is designed to check the trip current and trip time. Most RCD Testers can measure from 1 millisecond to 2000 milliseconds .
Many RCD Testers will be capable of conducting both an AC and DC test, Note :
The Standard BS-7671requires that RCDs are tested for trip times at specified intervals i.e. not just a push button test. An RCD Tester is required for this tripping time test.
Earth Testing :
Legally it is a requirement – but is it really necessary ?
Potentially the most dangerous appliances are Class I appliances (earthed appliances) e.g. floor polishers and the like, but also in this category are extension leads.

Class I appliances are designed to have an earth – this means that in the example of the floor polisher the body of the polisher is connected to earth - literally to the ground via an earth conductor which goes right back to the building switchboard and then into the ground the building is sitting on.

If this conductor is damaged anywhere then the consequences can be fatal – I will explain this point in greater detail shortly. It is obvious therefore that the conductor needs to be tested.

Insulation Resistance & Leakage Testing
Insulation resistance tests MUST NOT be carried out using ohmmeters or multimeters because these meters only produce a small battery voltage in the region of 1.5 to 9 volts. This small voltage is insufficient to pressure test the insulation to expose any weakness in it and therefore is totally inappropriate for insulation resistance tests.

Insulation resistance testers and PATs on the other hand are specifically designed to produce 500 volts (or even greater voltage values for some applications) which places the insulation under stress. This test will indicate any weakness that may break down under normal use on the 230 volt supply.

It is a requirement that the resistance measured by the insulation tester in this way should be not less than 1 megohm (1,000,000 ohms) for an electrical appliance to pass this test.

A practical example showing how a multimeter or ohmmeter is inappropriate to test the insulation resistance of an electrical appliance is detailed by the following example:

A 230-volt floor polisher has a partial insulation breakdown between the motor windings and the earthed metal case. The polisher when in use and at its normal operating temperature, causes the sub-circuit protective fuse to blow as a result of the insulation breaking down to the earthed metal frame.
The polisher, when tested with an ohmmeter or multimeter, does not indicate the presence of a fault, as the meter voltages are so low that they do not stress the insulation and therefore do not reproduce the breakdown that occurs when the appliance is in use.
However, testing the same polisher with an insulation resistance tester producing an output of 500 volts causes the insulation to break down under test, thereby indicating a low insulation resistance value and the presence of a fault path.
NOTE The importance of a sound low resistance earth continuity conductor is paramount to the safety of any electrical appliance that requires an Earth. A test as described above would not achieve anything if the integrity of the Earth were not first proven to be in good condition. Should the appliance have an open circuit Earth continuity conductor, it would produce a high resistance test result, but in fact when the appliance was plugged in it would enliven the case and expose a potential shock hazard.

APRENTICE : ;) ELECTRICAL RING MAIN OR RADIAL CIRCUIT :
A ring main is exactly what it says on the tin. It is a ring of wires, circling your home, carrying the mains electricity to sockets on the way. It gets the power from the Consumer Unit and delivers it to the sockets. As both ends of the ring are connected to the same terminals at the consumer unit, the current runs in both directions imposing less of a load on the cables. Electricity loses power over long lengths of cable and trying to put too much power through a cable which is not designed for it, is dangerous, so a ring main delivers power from both ends to keep the load as light as possible.
A radial circuit is a mains power circuit found in some homes to feed sockets and lighting points. It is simply a length of appropriately rated cable feeding one power point then going on to the next. The circuit terminates with the last point on it. It does not return to the Consumer Unit or fuse box as does the more popular circuit, the Ring Mains. To see the wiring at the back of the socket please go to the ring main project.
There is no limit to the number of sockets used on a radial circuit providing the circuit is contained within an area not exceeding 50 square m, and, just like a ring main, spurs, or extra sockets, can be added. The number of spurs must not exceed the number of existing sockets. Regs , p-363
A separate ring main is usually installed on every floor of the house to make sure things are kept safe and it is only when, for example, a spur (additional socket) is added on an upstairs ring main, to feed a socket or light on a downstairs circuit, that things can get tricky. Please read Part P Building Regulations / Regs , 314.4
A ring main uses 2.5mm cable comprising of a live, neutral and earth. This is called two core & earth cable. The 2.5mm is the measurement of the cross sectional area of the cables.
The floor area a ring main serves is also governed. This is because the regulation people have some idea of how much power and lighting we can expect to use in such an area. The maximum area for a ring main is 100 square meters. An average house has a footprint of about 64-70 square meters so this allows for the continuation of the ring into a porch or garage etc. The ring main must be protected by a 32amp MCB.
The cable itself can be up to 60 meters long if it is protected by a cartridge fuse and 50 meters long if protected by an MCB.
There is no limit to the number of sockets you can have on a ring main but there is a limit to the number of spurs you can have from those sockets or from the wiring between them. on adding an extra socket. You can also extend the ring main if you need to.
Units or appliances which use a lot of power, like cookers and showers must be installed on their own circuits so please check the appliances you are considering using on your ring main. It is also a regulation that any socket which is capable of being used to supply power outside of the house is protected by an RCD.,

Apprentice : ;) An MCB is a form of fuse (protective device) which overcomes the traditional problem associated with fuses in so much as when one blows it does not need to be replaced as a fuse does. MCB's operate when they sense an overload, or over current, and become an automatic switch, turning off, or tripping, the MCB when it detects such an overload.
An RCD is a similar protective device which is different in two ways. Firstly it is connected to both the live and neutral wires in the consumer unit making it a double pole switch, whereas the MCB is only connected to the live side of the circuit. Secondly, rather than just detecting an overload of current, it detects the fault which causes the overload.
Many consumer units these days are produced to be split load consumer units. See our project on consumer units. Those circuits which need more protection than others, i.e. showers, sockets serving outdoor appliances, external 230V lighting, must be protected by an RCD. Other circuits such as lighting and cookers, are protected by MCB's.
Each individual circuit, of whatever kind, is protected by an MCB. The circuits needing most protection are also served by 1 RCD. Each circuit does not need its own RCD in a split load board.
If you wanted to protect every circuit against overload and faults, you can install an RCBO which is a residual circuit breaker with over current protection. This is a combined MCB and RCD.
Other forms of fuse are either re-wireable fuses and cartridge fuses. Cartridge fuses are simply fuse wire contained in an enclosed glass or ceramic tube (such as the fuse in a plug) and re-wireable fuses (slowly becoming obsolete as wiring regulations are upgraded) which are simply two terminals connected by a length of accessible fuse wire of differing amperage rating.
 
Last edited by a moderator:
The Rules and Regulations Explained : :rolleyes:
Regulation 411.3.3.
States that additional protection by means of a 30mA RCD
is to be provided for all socket outlets with a rated current
not exceeding 20A for use by ordinary persons. The only
exceptions allowed are for socket outlets for use under the
supervision of “skilled” or “instructed persons” e.g. some
commercial / industrial locations, or a specific labelled
socket provided for connection of a particular item of equipment, e.g. a freezer circuit.

Regulation 701.411.3.3
In specific locations such as those containing a bath or
shower there is a requirement now to provide RCD
protection on all circuits, including the lighting and shower circuits.

Regulation 314.1 & 2
Requires that every installation shall be divided into
circuits as necessary to avoid danger and minimise
inconvenience, in the event of a fault. Also reducing the
possibility of unwanted RCD tripping, due to excessive
protective conductor currents but not due to an Earth fault.
Separate circuits may be required for parts of the
installation, which need to be separately controlled in such
a way that they are not affected by the failure of other
circuits. The appropriate subdivision should take account
of any danger arising from the failure of a single circuit eg.
an RCD trip on a socket outlet causing the unwanted failure
of a lighting circuit and its associated hazards.

Regulation 522.6.7
Now requires a much greater use of RCD’s to
protect the wiring concealed in walls or partitions even
where installed in previously defined “Safe Zones”.
These regulations effectively mean that all concealed
wiring at a depth of less than 50mm from the surface now
requires protection by a 30mA RCD unless
provided with earthed mechanical protection

The 17th Edition of the IEE wiring regulations ( BS7671 ), ;)
detail a number of regulations relating to protection against electric shock, including the need for additional protection :

The use of RCD's (Residual Current Devices) with a residual operating current not exceeding 30mA is the
recognised means of providing this additional protection in the event of failure of the provision for basic protection
and or the provision for fault protection or carelessness by users :

Such RCD's should not be used to provide the sole means of protection and do not obviate the need to apply one or
more of the recognised protective measure as detailed in the regulations :

Under the new regulations an installation is required to incorporate one or more RCD's, depending upon the
circumstances. Such instances include:-
• All socket outlets not exceeding 20A, but with certain exceptions. One such exception would be permitted for
a specific labelled or otherwise suitably identified socket outlet for connection of a particular piece of equipment.

• Mobile equipment with a current rating not exceeding 32A for use outdoors

• Electrical circuits installed under “Special installations and locations” as defined in Part 7 of the regulations
e.g. Swimming Pools / Saunas.

• All electrical circuits, including shower and lighting circuits etc. in rooms with a fixed bath or shower e.g.
bathrooms and en-suite bedrooms :

In addition to the protection requirements of the outgoing circuits / loads, the requirements of the installed cabling
also must be taken into account :

Where a cable is concealed in a wall or partition at a depth of less than 50mm from the surface, even if installed in the
“safe zone”, if not provided with earthed mechanical protection e.g. Metal trunking or conduit, it must be
provided with additional protection by means of a 30mA RCD :

Whilst it may be desirable to have one or two circuits fed via an unprotected circuit e.g. an identified / dedicated
freezer circuit, the installation of the wiring may still dictate that the circuit must be RCD protected :

The protection of a circuit by means of a 30mA RCD is also required where cables are concealed in walls constructed
with metal stud partitions which are common in modern buildings, irrespective of the depth from the surface,
unless provided with protection in the form of earthed metallic covering, trunking, conduit or other mechanical
protection so as to avoid damage to the cable during installation or construction of the wall :

In Summary :
Regulations : 411.3.3
Relating to : All socket outlets up to 20A rating for general use by ordinary persons :
Example : - Upstairs sockets - Downstairs sockets - Kitchen sockets - Cooker outlet with integral 13A socket outlet
- Plus any other sockets rated up to 20A including garage sockets
Additional Protection : 30mA RCD ,
Regulations : 701.411.3.3
Relating to : All electrical circuits in a room with a fixed bath or shower
Example : - Shower circuit - Lighting circuit - Heating circuit - Ventilation circuit - Shaver socket - Socket outlets ,
Additional Protection : 30mA RCD ,
Regulations : 522.6.6 / 522.6.7 / 522.6.8 /
All electrical circuits buried in a wall or partition at less than 50mm and without mechanical protection
Example : All concealed wiring - Socket outlets - Lighting circuits - Smoke alarm - Burglar alarm
Additional Protection : 30mA RCD ,

Part P Building Regulations : ( 2392-10 Domestic : ) for Customer , ;)
Please remember when attempting any electrical installations at home that you are obliged to get the completed job tested by a fully qualified electrician and obtain a minor works certificate. Failure to do this may render your house insurance invalid and you may have difficulty selling your home.
 
Last edited by a moderator:
Terms & Conditions : ( this may help self-employed Electricians ) Change some Wording : ;)

:- All material is fully owned by ourselves until invoice is paid off in full, even after installed.

:- Estimates are not fixed quotes and can vary, estimates are approximate minimum-maximum but never a final price.

:- If we do work (including fault finding or cable location etc) then there is a charge and this is not included in free advice.

:- Free advice is general electrical safety recommendations individually to your needs helping to improve the safety of your property/premises.

:- Inspection and testing is included in every invoice as standard (unless specified before work starts) as this is to ensure every circuit worked on complies with current regulations and is safe and fit for use. Sometimes followed with free advice to improve your electrical safety.

:- Inspection and testing is normally including (unless otherwise stated) in all jobs and fully certification given. Certificates are only issued when payment if received in full and all funds have cleared.

:- Duplicate certificates are charged at minimum £ - - per A4 sheet.

:- First invoice is issued and if payment is not received within 10 days (including weekends and bank holidays) a 5% fee is added as late payment and the invoice is resent on day 11 for the extra added amount. Strict 10 days to receive FULL payment, excluding down payments/deposits.

:- Failure to settle account within one calendar month of invoice date will automatically start legal claims proceedings at the FULL rate of invoice. Any discounts / special offers / promotions will be forfeited and reinstated back onto the invoice. All legal costs, late payments fees, additional labour fees can be added to the invoice as decision of Power Plus Electrical. There may be a daily interest applied to any long term outstanding debts until payment cleared in full. Only one reminder is posted as a overdue reminder, this has the 5% added and further to receive payment debt recovery costs started without further warnings.

:- Any equipment requiring hired, i.e. access equipment, other tradesmen (subcontractors, i.e. plumber/builder/carpet fitter/ decorator etc) or any other large cost out with my control will be paid for in advance by yourself the customer (or bill payer) in full before the 1st day of work direct or via ourselves to the subcontractor(s).


:- 1 full years (12 month) guarantee on all parts, labour and any material is included. This does not include access equipment or other trades in guarantee. Lamps, transformers, wear and tear and customer damage/misuse are not included under this clause and chargeable. Any guarantee jobs are only done by ourselves and other contractors services are not refunded.

:- As time, date(s) slot is only agreed when a deposit is paid. A contact is only formed after deposit is received and that time date is arranged, no deposit means no guaranteed start date for work to commence. If work is cancelled without 5 days working notice the deposit is non refundable. More than 5 days prior notice and deposit is fully refundable as long as no material has been ordered. Small jobs normally have no deposit required and can be cancelled at no cost to either party, unless again material is ordered or work has already started. Return materials can have a wholesaler restocking charge.

:- Emergency call out void from a no call out fee, details of call out charge and hourly rate will be explained over the phone. This will vary from job to job , and invoice settled in cash when leaving the property regardless if repaired or return visit required. Return visit is invoiced separately and normally day rates/ costs.

:- Normal working hours at single time are 8am-4:30pm or 9am-5:30pm,, Monday - Friday, including bank holidays, excluding Christmas / New Year. Out with these hours is charged at a higher labour charge.

:- Emergency call out available thought year, 24hour, 365 days a year. (see above).

:- ------- ------- Electrical.co.uk can change its terms and conditions at any time, only in writing if a current contract is already started. No future notice needed to be given to change terms and conditions.

:- Please note that telephone calls are recorded

Fire alarms :rolleyes:

Installing a fire alarm is a legal requirement in most commercial and industrial premises Thus alerting of a fire or a smoldering Problem and getting persons and alarm raised quickly. Fire alarms are extremely reliable and with regular testing can be a life- Saving.
Landlords and mains power smoke alarms with battery backup.

Under the common law, Landlords have the duty to ensure the safety of rented property and its contents to Tenants, occupants, neighbors’ or the public do not suffer injury or damage.

The 1991 Smoke Detectors Act, requires that all new houses that have been built since 1992 must, by law, have a smoke detector installed. The minimum requirement being one smoke alarm on each level of the building.

This is not a piece of legislation aimed specifically at residential letting property, but aimed at all new buildings. If an agent installs smoke alarms into properties that he manages or they already exist, care must be taken in ensuring that it is clear

from the letting agreement who is responsible for the maintenance of the detectors including testing and battery replacement.
To neglect this matter could mean that the landlord or agent is responsible, and in the case of a fire could be held liable for being negligent in their duties. There are different rules covering Houses in Multiple Occupation with regard to the installation of smoke detectors and other fire prevention measures.
Installed smoke alarms must be accompanied with a certificate and be tested regularly by pressing the test button. Most landlord insurance requires this certificate and wont payout in the event of a claim. Only qualified electrical contractors can issue this certificate in accordance to BS5839-6.
 
Last edited by a moderator:
Guidance Note 3 , 2392-10 ;) Initial verification , in the context of Regulation 610.1 , is intended to confirm that the installation complies with design and has been
Designed and constructed in accordance with BS-7671 . ( 610.1 – 611.2 – 612.1 ) :
This Section makes recommendations for the initial inspection and testing of electrical installations .
Chapter 61 of BS-7671 states the requirements for “ INITIAL VERIFICATION “ as far as reasonably practicable , ( 611.2 )
An inspection shall be carried out to verify :
(1) All installed electrical equipment and material is of the correct type and complies ( 611.2 ) with applicable British Standards or acceptable equivalents :
(2) All parts of the fixed installation are correctly selected and erected :
(3) No part of the fixed installation is visibly damaged or otherwise defective :

Guidance Note 3 , 2392-10 ;)
( 132.14.1 ) Verification of polarity – single-pole device in a ( TN- or TT system )
( 530.3.2 ) it must be verified that single-pole devices for protection or switching are installed in line conductors Only .
Accessories and equipment :
Correct connection ( suitability , polarity , e.t.c ) must be checked . 555 :
Table 55.1 of BS7671 is a schedule of types of plug and socket-outlets available , the ratings , and the associated British Standards :
Particular attention should be paid to the requirements for cable couplers , 553.2
Bayonet lampholders B15 and B22 should comply with BS-EN 61184 and be of ( 559.6.1.7 ) temperature rating ( T2 )

Correct connection ( suitability , polarity , e.t.c ) must be checked . 553 : ← ← ***

The client : ;)
Certificates and reports :
( 631.1 ) Following the initial verification of a new installation or changes to an existing installation ,
( 632.1 ) an Electrical installation Certificate , together with a schedule of inspections and a schedule of test results , is
Required to be given to the person ordering the work , in this context , “ work “ means the installation work , Not the work of carrying out the inspection ( 631.2 ) and Test , Likewise , following the periodic inspection and testing of an existing installation ,
( 634.1 ) a periodic inspection Report , together with a schedule of inspections and a schedule of test results , is required to be given to the person Ordering the inspection :
Sometimes the person Ordering the work is Not the User , in such cases it is Necessary for the User ( e.g. employer or householder ) to have a copy of the inspection and test documentation , it is recommended that those providing documentation to the person Ordering the work recommend that the forms be passed to the User including any purchaser of a Domestic property :

2392-10 :rolleyes:
Rented Domestic and Residential Accommodation :
In England and Wales , The Landlord and Tenant Act 1985 , Section (11 ) Repairing Obligations in short leases sub-section (1) (b)
Requires a landlord “ to keep in repair and proper working Order the installations in the dwelling-house for the supply of water, gas and Electricity :
A similar requirement can be found in the House ( Scotland ) Act 2006 , Section 13 The repairing standard sub-section (1)(c)
And Section 14 Landlords duty to repair and maintain :
Although neither of the above Acts makes specific mention of a need to carry out Periodic inspection and testing of the electrical installation , they Do place an Obligation on the landlord to maintain the installation in a condition suitable for the use intended :
Where an installation is Not subject to an effective and ongoing planned and proactive maintenance programme , Periodic inspection and testing carried out at appropriate intervals is a practical way of identifying where maintenance work is most required in order to keep the accommodation in a condition that is Safe for use :
Any repairs must be carried out by a competent person , the Landlord is responsible for confirming the competency of any contractors carrying out such work :

2392-10 : :rolleyes:
( 2.7.4 ) The sequence of tests : GN-3 ,
Initial tests should be carried out in the following sequence where relevant :
(a) Continuity of protective conductors, including main and supplementary bonding ( 2.7.5 ) Regs , ( 612.2.1 )
(b) Continuity of ring final circuit conductors ( 2.7.6 ) Regs , ( 612.2.2 )
(c) Insulation résistance ( 2.7.7 ) Regs , ( 613.3 )
(d) Protection by SELV,PELV or by electrical separation ( 2.7.9 ) Regs , ( 612.4.1 ) ( 612.4.2 )
(e) Protection by barriers or enclosures provided during erection ( 2.7.9 ) Regs , ( 612.4.5 )
(f) Insulation résistance of Non-conducting floors and walls ( 2.7.10 ) Regs , ( 612.5 )
(g) Polarity ( 2.7.11 ) Regs , ( 612.6 )
(h) Earth electrode résistance ( 2.7.12 ) Regs , ( 612.7 )
(i) Protection by automatic disconnection of the supply ( 2.7.13 ) Regs , ( 612.8 )
(j) Earth fault loop impedance ( 2.7.17 ) Regs , ( 612.9 )
(k) Additional protection ( 2.7.15 ) Regs , ( 612.10 )
(I) Prospective fault current ( 2.7.16 ) Regs , ( 612.11 )
(m) Phase sequence ( 2.7.17 ) Regs , ( 612.12 )
(n) Functional testing ( 2.7.18) Regs , ( 612.13 )
(o) Voltage drop ( 2.7.19 ) Regs , ( 612.612.14

Alterations and Additions : :rolleyes:
Every alteration or addition to an existing installation must comply with the Regulations and must Not impair the safety of the existing installation : ( 131.8 – 633.1 – 633.2 )
When inspecting and testing an alteration or addition to an electrical installation , the existing installation must be inspected and tested so far as is necessary to ensure the safety of the alteration or addition . including for example :
* Protective conductor continuity :
* Earth fault loop impedance :
Whilst there is no obligation to inspect and test any part of the existing installation that ( 633.2 ) does not affect and is not affected by the alteration or addition , observed departures are required to be noted in the comments box of electrical installation certificates ( single signature or multiple signature ) and minor works certificates ,

Electrical Installation Certificate : :rolleyes:
Regulation ( 631.1 ) of BS-7671 requires that , upon completion of the verification of a new installation , or changes to an existing installation , an Electrical Installation Certificate based on the model given in appendix 6 of BS-7671 shall be provided Section 632 requires that :
(1) the Electrical Installation Certificate be accompanied by a Schedule of Inspections ( 632.1 ) and a Schedule of Test Results.
These Schedules shall be based upon the models given in appendix 6 of BS-7671 :
(2) the Schedule of Test Results shall identify every circuit , including its related protective ( 632.2 ) device(s) , and shall record
The results of the appropriate tests and measurements ; chapter 61 :
(3) the Electrical Installation Certificate shall be compiled Signed / Authenticated by ( 631.4 ) a Competent person or persons
Stating that to the best of their knowledge and ( 632.3 ) belief the installation has been designed , constructed , inspected and
Tested in accordance with BS-7671, any permissible deviations being listed :
(4) any defects or Omissions revealed by the inspector shall be made good and ( 632.4 ) inspected and tested again before
The Electrical Installation Certificate is issued :
 
Last edited by a moderator:
Initial testing : :rolleyes:
Introduction to test methods :
The test methods described in this section are the preferred test methods to be used , other appropriate test methods are Not Precluded :
Initial testing :
The test results must be recorded on the Schedule(s) of Test Results and compared ( 631.1 ) with relevant criteria for example , relevant criteria for earth fault loop impedance may be provided by the designer , obtained as described in Section 2.7.14 ↔
( Maximum permissible measured earth fault loop impedance ) Appendix 2 On-Site Guide ←

Protective Conductors :
(1) Cables incorporating protective conductors comply with relevant BS- ( Section 511 )
(2) Joints in metal conduit , duct or trunking comply with Regulations ( 543.3 )
(3) Flexible or pliable conduit to be supplemented by a protective conductor ( 543.2.1 )
(4) Minimum cross sectional area of copper conductors ( 543.1 ) (5) Copper conductors , other than strip, of 6mm2 or less protected by insulation ( 543.3.2 )
(6) Circuit protective conductor at termination of sheathed cables installed with sleeving ( 543.3.2 )
(7) Bare circuit protective conductor protected against mechanical damage and corrosion ( 542.3 and 543.3.1 )
(8) Insulation , sleeving and terminations identified by colour combination green and yellow ( 514.3.1 ) and 514.4.2 )
(9) Joints electrically and mechanically sound ( 526.1 )
(10) Separate circuit protective conductors not less than 4mm2 if not protected against mechanical damage ( 543.1.1 )
(11) Main and supplementary bonding conductors of correct size ( section 544 )

Minor Electrical Installation Works Certificate : GN-3 2392-10 :rolleyes:
Notes on Completion ,
Scope :
The minor works Certificate is intended to be used for additions and alterations to an installation that do not extend to the provision of new circuit , Example include the addition of a socket-outlet or lighting point to an existing circuit , the relocation of a light switch etc, this Certificate may also be used for replacement of equipment such as accessories or luminaires , but not for the replacement of distribution boards or similar items , appropriate inspection and testing , however , should always be carried out irrespective of the extent of the work undertaken :
Part 1 : Description of minor works :
* 1.2 the minor works must be so described that the work that is the subject of the certification can be readily indentified :
* 4 , see Regulations ( 120.3 ) & ( 120.4 ) No departures are to be expected except in most unusual circumstances , see also Regulations ( 633.1 )
Part 2 Installation details :
* 2 , the method of fault protection must be clearly identified , e.g. Automatic Disconnection of Supply ( ADS ) :
* 4 , if the existing installation lacks either an effective means of earthing or adequate main Equipotential bonding conductors’ ,
This must be clearly stated , see Regulations ( 633.2 ) Recorded departure from BS-7671 may constitute Non-compliance with the Electricity Safety, Quality and Continuity Regulations 2002 ( as amended ) or the Electricity at work Regulations 1989 ,
It is important that the client is advised immediately in writing :
Part 3 : Essential tests :
The relevant provisions of part 6 ( Inspection & Testing ) of BS-7671 must be applied in full to all minor works , for example , where a socket-outlet is added to an existing circuit it is necessary to :-
* 1 , establish that the earthing contact of the socket-outlet is connected to the main earthing terminal :
* 2 , measure the insulation résistance of the circuit that has been added to , and establish that it complies with table 61 of BS-7671 :-
* 3 , measure the Earth fault loop impedance to establish that the maximum permitted disconnection time is not exceeded :-
* 4 , check that the polarity of the socket-outlet is correct :-
* 5 , ( if the work is protected by an RCD ) ← verify the effectiveness of the RCD :-
Part 4 : Declaration :
* 1,3 : the Certificate shall be made out and signed by a competent person in respect of the design , construction , inspection & testing of the work :-
* 1,3 the competent person will have a sound knowledge and experience relevant to the nature of the work undertaken and to the technical standards set down in BS-7671 , be fully versed in the inspection & testing procedures contained in the Regulations and employ adequate testing equipment :-
* 2 , when making out and signing a form on behalf of a company or other business entity , individuals shall state for whom they are acting :-

Protection by barriers or enclosures provided during erection : 3292-10 :rolleyes:

( 612.4.5 ) this test is not applicable to barriers or enclosures of factory-built equipment , it is
( 416.2.1 ) applicable to those provided on site during the course of assembly or erection and
( 416.2.2 ) therefore is seldom necessary , where , during erection , an enclosure or barrier is
( 416.2.3 ) provided to provide basic protection , a degree of protection not less than IP2X or
( 416.2.4 ) IPXXB is required , Readily accessible horizontal top surfaces must have a degree of protection of at least IP4X or IPXXD :
( 416.2.1 ) the degree of protection afforded by IP2X is defined in BS-EN 60529 as protection against the entry of “fingers or similar objects Not exceeding 80mm in length , solid objects exceeding 12mm in diameter ” the test is made with a metallic standard test finger ( test finger 1 to BS-61032 )
Both joints of the finger may be bent through 90º with respect to the axis of the finger, but in one and the same direction only , the finger is pushed without undue force ( not more than 10 N ) against any openings in the enclosure and , if it enters , it is placed in every possible position ,
A SELV supply, not exceeding 50v , in series with a suitable lamp is connected between the test finger and the live parts inside the enclosure , Conducting parts covered only with varnish or paint , or protected by oxidation or by similar process , must be covered with a metal foil electrically connected to those parts which are normally live in service :
* the protection is satisfactory if the lamp does not light :
The degree of protection afforded by IP4X is defined in BS-EN 60529 as protection ( 416.2.2 ) against the entry of “ wires or strips of thickness grater than 1.0mm , and solid objects exceeding 1.0mm in diameter :
The test is made with a straight rigid steel wire of 1mm + 0.05/0mm diameter applied with a force of 1 N + 10percent ,
The end of the wire must be free from burrs , and at a right angle to its length ,
* the protection is satisfactory if the wire cannot enter the enclosure :
Reference should be made to the appropriate product standard or BS-EN 60529 for a fuller description of the degrees of protection , details of the standard test finger and other aspects of the test ,

Scope : :rolleyes:
It is essential that the inspector and the person ordering the inspection know the extent of the installation to be inspected and any criteria regarding the limit of the inspection , both should be agreed and recorded on the Certificate :

Cable : :rolleyes:
( 132.7 ) where practicable , the cable size should be assessed against the protective arrangement
( 523 ) based upon information provided by the installation designer ( where available )
( 524 ) :- ( 525 ) Reference should be made , as appropriate , to Appendix 4 of BS—7671 :

Fault Protection : :rolleyes:

The methods of fault protection are classified in a number of sub-sections in BS-7671 , and are :
( 411 ) 1 , Automatic disconnection of supply :
( 418.1 ) 2 , Non-conducting location :
( 418.2 ) 3 , Earth-free local Equipotential bonding :
( 413 ) 4 , Electrical separation :

( 411 ) Automatic disconnection of supply ( ADS ) :rolleyes:

The presence , correct sizing , labelling and connection of appropriate protective conductors must be confirmed as follows :
( 542.3 ) * Earthing Conductor :
( 543 ) * Circuit protective Conductors :
( 544 ) * Protective bonding Conductors :
( 544.1 ) – Main bonding Conductors :
( 544.2 ) – Supplementary bonding Conductors :

Sockets-Outlets : 2392-10 ;)
1 , Complies with BS-196 , BS- 546 , BS- 1363 , BS- EN 60309-2 ) and shuttered for household and similar installations ( 553.1.4 )
2 , Mounting height above the floor or working surface suitable ( 553.1.6 )
3 , Correct Polarity ( 612.6 )
4 , if installed in a location containing a bath or shower , installed beyond 3m horizontally of the bath or shower unless shaver supply unit or SELV ( 701.512.3 )
5 , Protected where mounted in a floor ( Section 522 )
6 , Not used to supply a water heater having uninsulated elements ( 554.3.3 )
7 , Circuit protective conductor connected directly to the earthing terminal of the Socket-Outlet , on a sheathed wiring installation ( 543.2.7 )
8 , Earhing tail from the earthed metal box , on a conduit installation to the earthing terminal of the Socket-Outlet ( 543.2.7 )

Joint box :

1 , Joint accessible for inspection ( 526.3 )
2 , Joints protected against mechanical damage ( 526.7 )
3 , All conductors correctly connected ( 526.1 )

Fused Connection Unit :
1 , Correct rating and fuse ( 533.1 )
2 , Complies with BS-1363-4 ( 559.6.1.1 vii )

Cooker Control Unit :
1 , Sited to one side and low enough for accessibility and to prevent flexes trailing across radiant plates ( 522.2.1 )
2 , Cable to cooker fixed to prevent strain on connections ( 522.8.5 )
 
Last edited by a moderator:
Phase Rotation Instruments : ( 612.12 ) :rolleyes:

BS-EN 61557-7 gives the requirements for measuring equipment for testing the Phase Sequence in Three-Phase distribution Systems whether indication is given by mechanical , visual and / or audible means :
BS-EN 61557-7 includes requirements that :
* Indication shall be unambiguous between 85 per cent and 110 per cent of the nominal system voltage or within the range of the nominal voltage and between 95 per cent and 105 per cent of the nominal system frequency :
* the measuring equipment should be suitable for continuous operation :
* the measuring equipment should be so designed that when either one or two measuring leads are connected to earth and the remaining measuring lead(s) remain connected to their corresponding Phase conductors , the resulting total current to earth should not exceed 3.5 mA rms :
* the measuring equipment should not be damaged nor should the user be exposed to danger in situations where the measuring equipment is connected to 120 per cent of the rated system voltage or to 120 per cent of its rated maximum voltage range :
* Portable measuring equipment should be provided with permanently attached leads or with a plug device with live parts not accessible , whether plugged or unplugged :

RCD Testers : :rolleyes:
The test instrument should be capable of applying the full range of test current to an in-service accuracy as given in BS-EN 61557-6 , this in-service reading accuracy will include the effects of voltage variations around the nominal voltage of the tester ,
To check RCD operation and to minimise danger during the test , the test current should be applied for no longer than ( 2sec )
* instruments conforming to BS-EN 61557-6 will fulfil the above requirements : ( 612.1 )

Operation of overcurrent circuit-breakers : :rolleyes:

( 612.13.2 ) where protection against overcurrent is provided by circuit-breakers , the manual operating mechanism of each
circuit-breaker should be operated to verify that the device opens and closes satisfactorily :
( 611.3 ( viii ) it is not normally necessary or practicable to test the operation of the automatic tripping mechanism of circuit-breakers
.any such test would need to be made at a current substantially exceeding the minimum tripping current ii order to achieve operation within a reasonable time , for circuit-breakers to BS-EN 60898 a test current of not less than two and a half times the nominal rated tripping current of the device is needed for operation within 1 minute , and much larger test currents are necessary to verify operation of the mechanism for instantaneous tripping :

For circuit-breakers of the sealed type , designed not to be maintained , if there is doubt above the integrity of the automatic mechanism it will normally be more convenient to replace the device than to make further tests , such doubt may arise from visual inspection , if the device appears to have suffered damage or undue deterioration , or where there is evidence that the device may have failed to operate satisfactorily in service :

circuit-breakers with the facility for injection testing should be so tested and , if appropriate , relay settings confirmed :

GN-3 :rolleyes:

The Requirements of the Electricity at Work Regulations 1989 must be taken into account when considering the use of thermographic surveying Equipment as its use may necessitate the temporary removal or bypassing of measures that provide basic protection ( as defined in BS-7671 ) such as opening doors to electrical panels and the removal of barriers and covers ,
The Requirements of Regulation 14 ( Work on or near live conductors ) which is reproduced below , are particularly pertinent :

No person shall be engaged in any work activity on or so near any live conductor ( other than one suitably covered with insulating material so as to prevent danger ) that danger may arise unless :-

(a) it is unreasonable in all the circumstances for it to be dead ; and
(b) it is reasonable in all the circumstances for him to be at work on or near it while it is live ; and
(c) suitable precautions ( including where necessary the provision of suitable protective equipment ) are taken to prevent injury ,

Thermographic Surveying : :rolleyes:

Important Note : it is recommended that persons refer to the Requirements of the Electricity at Work Regulations 1989
And the guidance given in the Memorandum of Guidance on the Electricity at Work Regulations 1989 ( HSR25 )
Prior to undertaking any work activity which places themselves or those under their control in close proximity to live parts :

External Influences : 2391 - :rolleyes:
( 611.2 ) any known changes in external influences , building structure , and alterations or additions which may have affected the suitability of the wiring for its present load and method of installation should be Noted .

Note should also be made of any alterations or additions of an irregular nature to the installation ,
If unsuitable material has been used , the report should indicate this together with reference to any evident faulty workmanship or design ,

Required Competence : :rolleyes:

( 610.1 ) the inspector carrying out the inspection and testing of any electrical installation must ,
( 610.5 ) as appropriate to his or her function , have a sound knowledge and experience relevant to
( 611 ) the nature of the installation being inspected and tested , and to the technical standards ,
The inspector must also be fully versed in the inspection and testing procedures and employ suitable testing equipment
During the inspection and testing process ,

It is the Responsibility of the inspector to :

( 610.1 ) (1) ensure no danger occurs to any person or livestock and property in not damaged :
( 612.1 ) (2) compare the inspection and testing results with the design criteria :
(3) take a view on the condition of the installation and advise on remedial works :

( 634.2 ) in the event of a dangerous situation being found , the inspector should recommend the immediate isolation of the defective part , the person ordering the work should be informed of this recommendation without delay :
 
Last edited by a moderator:
Enclosures and mechanical protection : :rolleyes:
( 612.4.5 ) the Enclosures and mechanical protection of all electrical equipment should be
( 132.5 ) inspected to ensure that they remain adequate for the type of protection intended , all
( 611.3 ( xiii ) secondary barriers ( to IP2X or IPXXB ) should be in place ,
( 416.2.4 )

Polarity : ( 612.6 ) GN-3 2.7.11 :rolleyes:

Tests should be made to verify that :
(1) the polarity is correct at the meter and distribution board :
(2) every fuse and single-pole control and protective devices are connected in line ( 612.6 ) conductors’ only :
(3) conductors’ are correctly connected to socket-outlets and other accessories / equipment
(4) except for E14 and E27 lampholders to BS-EN 60238 , centre-contact bayonet and Edison screw lampholders
Have their outer or screw contacts connected to the Neutral conductor :
(5) all multi-pole devices are correctly installed :

It should be established whether there have been any alterations or additions to the installation since its last inspection
And test , if there have been no alterations or additions then sample tests should be made of at least 10 per cent of all single-pole and multi-pole control devices and of any centre-contact lampholders , together with 100 per cent of socket-outlets ,
If any incorrect polarity is found then a full test should be made in that part of the installation supplied by the particular distribution board concerned , and the sample testing increased to 25 per cent for the remainder of the installation , if additional cases of incorrect polarity are found in the 25 per cent sample ,
A full test of the complete installation should be made :

Earth Electrode Résistance Testers : :rolleyes:

This may be a four-terminal instrument ( or a three- terminal one where a combined lead to the earth electrode would not
Have a significant résistance compared with the electrode résistance ) so that the résistance of the test leads and temporary spike
Résistance can be eliminated from the test result ,

Aspect affecting in-service reading accuracy include the effects of temporary spike résistance ,
Interference currents and the layout of the test electrodes , the instrument should carry some facility to check that the résistance
To earth of the temporary potential and current spikes are within the operating limits of the instrument ,
It may be helpful to note that instruments complying with BS-EN 61557-5 incorporate this facility , care should be exercised to ensure that temporary spikes are positioned with reasonable accuracy :

2392-10 :rolleyes:

Initial Verification :

Purpose of initial verification :
initial verification , in the context of Regulation ( 610.1 ) is intended to confirm that the ( 610.1 )
installation complies with the design and has been designed and constructed in ( 611.2 )
accordance with BS-7671 ( 612.1 )

this section makes recommendations for the initial inspection and testing of electrical installations :

Chapter 61 of BS-7671 : states the requirements for “ Initial Verification “ as far as ( 611.2 )
Reasonably practicable , an inspection shall be carried out to verify :

(1) all installed electrical equipment and material is of the correct type and complies ( 611.2 )
With applicable British Standards or acceptable equivalents :
(2) all parts of the fixed installation are correctly selected and erected :
(3) no part of the fixed installation is visibly damaged or otherwise defective :

Inspections : ( 611. )
Inspection is an important element of inspection and testing ,
Initial Inspection :
General procedure :
Inspection and , where appropriate , testing should be carried out and recorded on suitable schedules progressively throughout the different stages of erection and before the installation is certified and put into service , Comments on Individual items to be Inspected :
The inspection should include at least the checking of those items listed in Section ( 611.3 ) of BS-7671 :
Tests : ( 612. )
Initial testing : introduction to test methods : the test methods described in this section are the preferred test methods to be used ;
Other appropriate test methods are not precluded ,
Initial testing :
The test results must be recorded on the Schedule(s) of Test Results and compared ( 612.1 ) with relevant criteria .
For example , relevant criteria for earth fault loop impedance may be provided by the designer , obtained as described in section 2.7.14 GN-3 :
Earth fault loop impedance :
Determining the earth fault loop impedance , ( Ze )
The earth fault current loop comprises the following elements , starting at the point of fault on the ↔ ( Line-Earth loop ) :
* the circuit protective conductor :
* the main earthing terminal and earthing conductor :
* for TN-Systems the metallic return part or , in the case of TT and IT systems , the earth return path :
* the part through the earthed neutral point of the transformer :
* the source line winding : and
* the line conductor from the source to the point of fault :

Earth fault loop impedance ( Zs ) may be determined by : ( 612.9 ) ↔ ( 612.8 )
(1) measurement of ( R1 + R2 ) during continuity testing and adding to ( Ze ) i.e. Table 41.2 : Table 41.3 : Table 41.4 :
( Zs = Ze + ( R1 + R2 )
( Ze ) is determined by :
* measurement ( see below ) , or
* enquiry of the electricity supplier , or
* calculation , or

(2) direct measurement using an earth fault loop impedance tester ( see below )

Determining ( Ze )
Measurement :

The reasons that ( Ze ) is required to be measured are twofold :

(1) to verify that there is an earth connection :
(2) to verify that the ( Ze ) value is equal to or less than the value determined by the designer and used in the design calculations :

( Ze ) is measured using an earth fault loop impedance tester at the origin of the installation :

( 542.4.2 ) the impedance measurement is made between the ( Line of the supply ) and the means of earthing with the mains switch open or
With all the circuits isolated , the means of earthing must be disconnected from the installation earthed equipotential bonding for ( 610.1 )
The duration of the test to remove Parallel paths , care should be taken to avoid any shock hazard to the testing personnel and other persons on the site both whilst establishing contact , and performing the test : ENSURE THAT THE EARTH CONNECTION HAS BEEN REPLACED BEFORE RECLOSING THE MAIN SWITCH :

Main switch ( Open ) :
Test of ( Ze ) at the Origin of the Installation :

Measurement of ( R1 +R2 ) to add to ( Ze )
Whilst testing the continuity of the protective conductors of Radial Circuits , or whilst testing the Continuity of ring final circuits , the value of
( R1 +R2 ) test ; is measured ( at the test ambient temperature )

The measured value of ( R1 +R2 ) test ; for the final circuit should be added to the value of ( R1 +R2 ) test ; for any distribution circuit supplying the final circuit , to give the total ( R1 +R2 ) test ; from the origin of the installation :

Direct measurement of ( Zs ) :rolleyes:
Direct measurement of ( Zs ) can only be made on a LIVE INSTALLATION ,
Neither the connection with earth nor bonding conductors are disconnected Readings given by the loop impedance tester may be less than Ze + ( R1 +R2 ) because of PARALLEL EARTH RETURNPATHS provided by any bonding extraneous-conductive-parts ,
This must be taken into account when comparing the results with design data :

Care should be taken during the tests to avoid any shock hazard to the testing personnel , other persons or livestock on site :

Enquiry :
Where ( Ze ) is determined by enquiry of the electricity supplier , ( Zs ) is then determined by adding ( R1 +R2 ) to this value of ( Ze )
However , a test must be made to ensure that the electricity suppliers earth terminal is actually connected with earth , using an earth fault loop impedance tester or a test lamp :

Verification of test results : :rolleyes:
Values of ( Zs ) should be compared with one of the following ( 612.1 ) :
(1) for standard thermoplastic ( PVC ) circuits :
(2) earth fault loop impedance figures provided by the designer : table 41.2 )
(3) tabulated values in BS-7671 , corrected for temperature : table 41.3 )
(4) rule-of-thumb figures : table 41.4 )
Appx 14 :
 
Last edited by a moderator:
Earth fault Loop impedance test voltage : :rolleyes:

The normal method of test employed by a line-earth loop tester is to compare the unloaded loop circuit voltage with the circuit voltage when loaded with a low résistance , typically 10Ω this method of test can create an electric shock hazard if the line-earth loop impedance is high and the test duration is not limited , in these circumstances the potential of the protective conductor could approach line voltage for the duration of the test :

Earth fault Loop impedance testers :
These instruments operate by circulating a current from line conductor into the protective earth ,
This will raise the potential of the protective earth systems :
To minimise electric shock hazard from the potential of the protective conductor ,
The test duration should be within safe limits , this means that the instrument should cut of the test current after 40 ms or a time determined by the safety limits derived from the information contained within DD IEC/TS 60479-1 ,
If the voltage rise of the protective conductor exceeds 50v during the test :

Instrument accuracy decreases as scale reading reduces , aspects affecting in-service reading accuracy include transient variations of mains voltage during the test period , mains interference , test lead résistance and errors in impedance measurement as a result of the test method , to allow for the effect of transient voltages the test should be repeated at least once , the other effects cannot be eliminated by test procedures :

For circuits rated up to 50A , a line-earth loop tester with a resolution of 0.01Ω should be adequate , in general , such instruments can be relied upon to be accurate down to values of around 0.2Ω :

Instruments conforming to BS-EN 61557-3 . will fulfil the above requirements :

These instruments may also offer additional facilities for deriving prospective short-circuit current , the basic measuring principle ids generally the same as for earth fault loop impedance testers . the current is calculated by dividing the earth fault loop impedance value into the mains voltage . instrument accuracy is determined by the same factors as for loop testers . in this case , instrument accuracy decreases as scale reading increases , because the loop value id divided into the mains voltage , it is important to note these aspects , and the manufacturers documentation should be referred to :

Test Instruments : GN-3 :rolleyes:

Instruments standard :
BS-EN 61010 Safety Requirements for Electrical Equipment for Measurement Control and Laboratory use is basic safety standard for electrical test instruments ,

The basic instrument standard is BS-EN 61557 Electrical Safety in Low Voltage Distribution Systems up to 1000V a.c and 1500V d.c
Equipment for testing , measuring or monitoring of protective measures , this standard includes performance requirements and requires compliance with BS-EN 61010 :

Reference was made to the use of test leads which conform to HSE Guidance Note GS-38 , the safety measures and procedures set out in HSE Guidance Note GN-38 SHOULD BE OBSERVED FOR ALL INSTRUMENTS , LEADS , PROBES AND ACCESSORIES , IT SHOULD BE NOTED THAT SOME TEST INSTRUMENT MANUFACTURERS advise that their instruments be used in conjunction with fused test leads and probes . Other manufacturers advise the use of non-fused leads and probes when the instrument has in-built electrical protection , but it should be noted that such electrical protection does not extend to the probes and leads :

Routine checks : :rolleyes:

Electrical Installations should not be left without any attention for the periods of years that are normally allowed between formal inspections ,
In domestic premises it is presumed that the occupier will soon notice any breakages or excessive wear and arrange for precautions to be
Taken and repairs to be carried out . in other situations , there must be arrangements made for initiating reports of wear and tear from users of the premises , this should be supplemented by routine checks , the frequency of these checks will depend entirely upon the nature of the premises , routine checks would typically include :

Activity : ………………………………………… Checks :
Defects reports : …………………………………. All reported defects have been rectified
Inspection : ………………………………………. Look for : ↔ ( breakages ) ( wear/deterioration ) ( signs of overheating )
( missing parts ( covers , screws ) ( loose fixings )

* confirm :
Switchgear accessible ( not obstructed )
Doors of enclosures secure : adequate labelling in place :

Operation …………………………………………. Operate :
…………………………………………………….. switchgear ( where reasonable )
…………………………………………………….. equipment – switch on and off
…………………………………………………….. including RCDs ( using test button )

These routine checks need not be carried out by an Electrically Skilled Person but should be done be somebody who is able to safely use the installation and recognise defects :

Periodic Inspection Report : :rolleyes:

BS-7671 requires that the result and extent of periodic inspection and testing shall ( 631.2 ) be recorded on a periodic inspection
Report and provided to the person ordering the ( 634.1 ) inspection :

The report must include : ( 631.1 )
(1) a description of the extent of the work , including the parts of the installation inspected and details of what the inspection
And covered :
(2) any limitations which may have been imposed during the inspection and testing of the installation :
(3) details of any damage , deterioration , defects and dangerous conditions and any ( 634.2 ) non-compliance with BS-7671
Which may give rise to danger :
(4) Schedule of inspections :
(5) Schedule of test results :

Any immediately dangerous condition should preferably be rectified , if Not , the defect should be reported in writing without delay to the employer or responsible employee ( see Regulation 3 of the Electricity at Work Regulations 1989 )

( 621.2 ) installations including those constructed in accordance with earlier editions of BS-7671 should be inspected and tested
For compliance with the current Edition of BS-7671 and departures recorded , however , reference should be made to the note by the Health and Safety Executive following the preface to BS-7671 , that installations conforming to earlier editions and not
Complying with the current Edition do not necessarily fail to achieve conformity with the Electricity at Work Regulations 1989 ,

Guidance on the action to be taken is to be given in the Observations and Recommendations section of the Periodic Inspection Report by Numbering each observation ( non-compliance ) ( 1 ) to ( 4 )

If the number ( 1 ) is allocated to an Observation , indicating that it requires urgent attention ,
Then the overall assessment must be that it is unsatisfactory ,
An example of this is an installation which has no earth , if numbers ( 2 ) or (3 ) are allocated , the person carrying out the test
Will have to use judgement to determine whether or not the installation can be classed as Satisfactory :

Where an “ ( X ) “ ( unsatisfactory ) observation has been recorded against any item in the Schedule of inspections ,
A corresponding comment should be included in the “ Observations and Recommendations Section :

Insulation testing: A guide to getting it right : Apprentices’ : ;)

The insulation test performs a measurement of the resistance of a product's insulation protection by applying a DC voltage between phase and neutral to the earth conductor for Class I equipment; and between phase and neutral to the outer case for Class II equipment. The test results in a reading of resistance measured in M ohms.

So why is it necessary to carry out the test? The test is designed to ensure that protective insulation is sufficient good enough to form a barrier to make sure that electricity does not come into contact with a user causing harm or to ensure that other manufacturing systems and machinery are not adversely affected.

So why is it necessary to carry out the test ? The test is designed to ensure that protective insulation is sufficient good enough to form a barrier to make sure that electricity does not come into contact with a user causing harm or to ensure that other manufacturing systems and machinery are not adversely affected.

In the manufacturing environment, the advent of legalisation such as the Low Voltage Directive (LVD) requires evidence of due diligence and the results of this and other tests can be used in this respect. The same can be said of in-service testing too.

Testing conditions : Regs : table 61
The test can be applied to both Class I and Class II equipment. The test should be carried out using probes or insulted clips, and without the equipment being connected to a power supply. Test voltages vary between standards - although 500V DC is the most common application - and the voltage is applied for a maximum of three seconds.

“ Dead Test “
Insulation Résistance Test Instrument , ( MΩ )
Capable of Supplying the Test Voltage D.C. Indicated in ( Table 61 )
Single-Phase Installation ( Line ↔( Live ) to Neutral ) L1 / N1 :

Red Lead / Line ↔( Live ) – Neutral : Black Lead / Earth : ( 2 – Leads Only )

( Line 1 – Brown :
( Line 2 – Black :
( Line 3 – Gray :
( N1 – Blue :

Three-Phase installation : ( 3-leads or 4-leads )
Phase ( L1 and L3 ) ← Brown / Gray
Phase ( L1 and L2 ) ← Brown / Black
Phase ( L2 and L3 ) ← Black / Gray

Test each Line in Turn to the Neutral

Three-Phase installation : ( NICEIC )
Line ( L1 to Line 2 ) Brown / Black
Line ( L2 to Line 3 ) Black / Gray
Line ( L3 to Line 1 ) Gray / Brown

Then Test each Line in turn to the Neutral :

* Insulation Résistance is Measured Between Live Conductors ( Line & Neutral ) CPC :
Single-Phase Installation :
 
Last edited by a moderator:
New posts

Reply to ***Useful Information For The Working Sparky*** in the Australia area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
735
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
662

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock