Discuss Volt stick gives "false" reading in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
52
I'm not an electrician but have worked as a mate and know my limitations. To fit a new light in a bedroom (loop at ceiling rose), I isolated the supply at the CU and tested supply at ceiling rose with Fluke T150, obviously no voltage detected between L and N or L and CPC (safe isolation - near enough, I was the only person in the house). Out of interest I also tested using a Kewtech Duo volt stick and got a "reading" from the Neutral. I realise that only the live conductor is isolated at the MCB so was this "back feed", if so can someone explain please?
 
If you rub a volt stick on your jumper it lights up.
Follow proper safe isolation procedures using the correct tools.
 
Thanks for your replies. I understand what safe isolation is and voltsticks are only an indication and never to be used to assume circuit is dead. As I said I used a Fluke T150 to test the circuit was actually safe to work on.
 
Duo volt stick and got a "reading" from the Neutral. I realise that only the live conductor is isolated at the MCB so was this "back feed", if so can someone explain please?

If it was a backfeed then it would have shown up when you tested it properly, and the lighting circuit wouldn't have worked properly in the first place.

This will most likely have been due to capacitive coupling, though this normally happens on disconnected cables. Did you check the polarity of the supply at any point?
 
If it was a backfeed then it would have shown up when you tested it properly, and the lighting circuit wouldn't have worked properly in the first place.

This will most likely have been due to capacitive coupling, though this normally happens on disconnected cables. Did you check the polarity of the supply at any point?
Thanks for taking the time to reply. I did test between L/N, L/E and N/CPC and got the expected results. I'll need to think this through.
 
Thanks for taking the time to reply. I did test between L/N, L/E and N/CPC and got the expected results. I'll need to think this through.

Do you mean you tested for polarity and it was ok or that you tested for isolation?
 

Reply to Volt stick gives "false" reading in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi everyone, I really hope someone will be able to help. So last night I tried to change 2 ceiling rose / pendant lights at my mother in laws...
Replies
5
Views
1K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Having a bit of a mare at the moment with a small 2 story HMO (6 single rooms with shared kitchen) which was fitted relatively recently (2016 or...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock