So this would be as if both cpc and line conductors are the same Size but sometimes its not the case
CPC, line conductor, neutral conductor, it doesn't matter what they're called in the table. They're all copper, and they all have the same resistance per meter for a given cross sectional area. 1 meter of 2.5mm² twin and earth is 2 meters of live conductor: 1 meter of 2.5mm² line and 1 meter of 2.5mm² neutral.

Read back over my post carefully, it should explain things
 
To the OP: Focus on understanding the principle.. NOT a formula. The OSG & BS7671 & all the IET books that I've looked at... try to make things easier by giving you the same thing in a different way. But IMHO this just makes things far more confusing...

I think all the standard publications could be made half the size they are if they removed all the variations. Oh, and added page numbers to the index !!
 
To the OP: Focus on understanding the principle.. NOT a formula. The OSG & BS7671 & all the IET books that I've looked at... try to make things easier by giving you the same thing in a different way. But IMHO this just makes things far more confusing...
Completely agree with this. It's messy, and a nightmare when trying to learn. Eg the table on p196 should have just 3 columns: conductor CSA, resistance/m copper, resistance/m Aluminium. No need to mention line conductor, protective conductor, R1 or R2.
 
VD itself is as we know mV/A/m * Ib * L

Max VD is either 6.9v (3%) or 11.5v (5%) for lighting & power respectively

We can rearrange the formula (using Max & Actual VD) to find Max circuit length for the calculated VD



Let's say we have a 6 mm² T&E with pvc insulated and sheathed cable feeding a a lighting circuit which has a mV/A/m value of 7.3. The actual circuit current is 12.5 A, and the length of run is 14 m.
Volt drop = 7.3 x 12.5 x 14 / 1000
= 1.28 V


If a 14 m run gives a volt drop of 1.28 V,
the length of run for a 11.5 V drop will be:
11.5 x 14m = 105m
Completely agree with this. It's messy, and a nightmare when trying to learn. Eg the table on p196 should have just 3 columns: conductor CSA, resistance/m copper, resistance/m Aluminium. No need to mention line conductor, protective conductor, R1 or R2.
I'd drop the individual rows for line and CPC, as you say you just want a value for 2.5 and 1.5, doesn't matter if it's line neutral or CPC.

I disagree on dropping R1+R2, I find that useful for determining the length of a circuit (or an implausibly low/high reading), dividing my R1+R2 value by the listed value
 
I'd drop the individual rows for line and CPC, as you say you just want a value for 2.5 and 1.5, doesn't matter if it's line neutral or CPC.

I disagree on dropping R1+R2, I find that useful for determining the length of a circuit (or an implausibly low/high reading), dividing my R1+R2 value by the listed value
Problem is, you need both line and CPC columns present in order to have an R1+R2 column. Can't drop one without dropping the other!

Personally I think it clutters the mind when learning. And it's not difficult to calculate (R1+R2)/m if you have the resistance/m of each of the conductors: just add them together.

I would have the resistances in ohms/m as well. It would remove the annoying step of dividing by 1000 to convert from milli ohms to ohms.
 
The other basic method of working out the voltdrop they tend to use on the 2391 is using ohms law, I believe they use this to test the candidates basic knowledge

You would need to use your R1+RN mutipled by the design current and then mutilpying by 1.2 to allow for the circuit to be running at 70°c

A basic question would be
"Whats the volt drop on a 13 amp immersion circuit with an R1+RN of 0.30 ?"

A=4.68v
B=3.59v
C=4.45v
D=5.68v

Answer
13x0.3x(1.2) = 4.68v
 

Reply to Voltage drop/2391 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
Replies
7
Views
2K
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
746
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi chaps, Been working though the electrical design guide and I'm stumped on reactive power. volt drop and the equations are easy enough but I...
Replies
1
Views
883
hello. i need to run power to a cabin that is 350 feet from the service pole in our driveway. the problem is voltage drop. the service pole is 150...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock