Discuss Voltage drop calcs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

C

Cider

Hi

Could someone kindly put me in the right direction for voltage drop in cables.
I have the formula from OSG (mV/A/m) x lbxL divide 1000 but cant get my brain to kick in and piece everything together.
There is very little in 7671 unless im looking in the wrong part.
Do I require tables for the cables.
Many thanks

Cider
 
volt drop for a given csa of cable is given in app.4 brb. and is in millivolts per amp per metre. so you have to multriply the value from brb by the current, then the length. then as it's given in millivolts, divide bt 1000 to get volts.
 
big red book, otherwise known as BS7671, the bible, bed time reading for electro fanatics, cash cow for the IET
 
Assessment of existing is done with the formula..

vd = (R1&RN) x Ib x F

where F=1.20

Just a point, if using Appendix 4, then the assumed temp will be at 70 C/90 C, so no factor required unless adjustments for temp are being made.

Onsite Guide, the Resistances are taken at 20 C, so as Widdler has pointed out correction factor will be required to get from lets say 20 C to 70 C.

Chris
 

Reply to Voltage drop calcs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
788
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
908
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
not to sure on how to find the wats for the power cable calcs could anyone help me its for a ring with 3 Dubble sockets on DB05-3L2 cable size...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock