Discuss Voltage on high res. extraneous part in the UK Electrical Forum area at ElectriciansForums.net

LastManOnline

Esteemed
Arms
Reaction score
1,230
During an FLI test recently on a high resistance extraneous part (several thousand ohm) I decided to test what voltage appeared on the metal while the test was been carried out.I used a Metrel M1 3000.I measured approx 40 volt. Its well over 20 years since I conducted a similar test and my memory was of a higher voltage.? Is my memory flawed? Do others get similar type measurements with their testers?
 
In think modern MFT / loop testers moderate the test current so they don't produce too big a change in supply (implying too high an exposed part voltage).

Certainly if you looked to design a loop tester with safety in mind you would put in some check / system so the test current was ramped up and limited by either 50V change or the "no trip" limit as the test started.
 
Certainly if you looked to design a loop tester with safety in mind you would put in some check / system so the test current was ramped up and limited by either 50V change or the "no trip" limit as the test started.

In GN3 it states that for 2 wire high current tests, the instrument should cut off the test within 40ms if the voltage rise on the protective conductor exceeds 50v during the test. Are you sure you didn't write it? 😉
 
In think modern MFT / loop testers moderate the test current so they don't produce too big a change in supply (implying too high an exposed part voltage).
This was really what I, m wondering about. The FLI test was traditionally regarded as potentially dangerous. Hence the requirement to carry out earth continuity tests on all exposed/extraneous parts first. But if as you suggest (correctly I believe) that modern testers are designed to reduce the voltage on the exposed part than by definition the potential danger of the FLI test is reduced as well.
 

Reply to Voltage on high res. extraneous part in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My system has had an intermittent problem for the last few months. The inverter has occasionally been reporting PV Voltage Too High, then it would...
Replies
13
Views
6K
I've had my work assessed which has raised a question about Extraneous-conductive-part. I just want to be sure I fully understand this. BS7671...
Replies
12
Views
8K
P
I have been trying to pass the written 2394 for a while now. The course that I am on is sadly lacking. I passed the 2395, but am having terrible...
Replies
8
Views
1K
Plonker 3
P
I think I have a faulty 66kva transformer but have little to no experience with them (delta star I believe) Call out due to reported problems...
Replies
39
Views
4K
Hi all, I am undertaking a partial rewire of a house that a client is needing to do quite a bit of surgery on as tenant just left and what a mess...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock