Discuss Wall sockets in utility room not working but there is power to them Nothing has tripped fuses ok in the UK Electrical Forum area at ElectriciansForums.net

Sockets in utility room not working but power reading when checked with meter Consumer unit hasn’t tripped Lights ok
Try operating the CB for the socket it may have tripped but the switch indicator has not moved to the off position
 
Tested live to neutral? If there’s power at the terminals, but not going to appliance, then check the fuse in the plug, otherwise faulty socket.

(try a known good appliance like a table lamp)
 

Reply to Wall sockets in utility room not working but there is power to them Nothing has tripped fuses ok in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
629
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Have a single plug socket which has been working fine for years. It is behind a unit so nothing has hit it. I looked at the socket and can seen no...
Replies
13
Views
1K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
735

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock