First guess is lots of earth leakage on a certain part of the cycle, e.g. when pump starts, or heater starts, etc. Try it on another circuit (plug into socket on a different circuit & RCD, assuming you have more than one socket circuit). If it now trips the other circuit, then either have someone look/repair the machine, or just buy a new one (often cheaper nowadays).
 
If it always stops at the same part of the wash cycle, then, as above. If it's more random, then it could be a minor internal water leak, dripping water into the electrics.
Another possibility is that there's nothing wrong with the washing machine at all, and the problem is a neutral to earth fault on a completely different circuit, served by the same RCD. Washing machine just provides the current surge to shunt enough current through the actual fault, to trip the RCD.
 
Another thing you can try yourself is to try and trigger the RCD with the washing machine unplugged / isolated.
If you plug in a fan heater or hair dryer to a circuit protected by the same RCD, and the RCD trips then it proves the issue is elsewhere and the washing machine just happens to be the thing sending current through the fault to cause a trip. If the RCD doesn't trip then it's pointing to the appliance.
If you call a decent sparks in, then within hour 1 they should be able to discover whether the problem is with fixed wiring (and if so, which circuit) or the appliance.
 
Another thing you can try yourself is to try and trigger the RCD with the washing machine unplugged / isolated.
If you plug in a fan heater or hair dryer to a circuit protected by the same RCD, and the RCD trips then it proves the issue is elsewhere and the washing machine just happens to be the thing sending current through the fault to cause a trip. If the RCD doesn't trip then it's pointing to the appliance.
If you call a decent sparks in, then within hour 1 they should be able to discover whether the problem is with fixed wiring (and if so, which circuit) or the appliance.
Good idea, if possible try the socket the washing machine is plugged into
 

Reply to Washing machine is tripping the house RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
576
Hj our washing machine tripped out electrics the other day. Everytime we switched it in the electrics cut out. We noticed a larger bend in the...
Replies
0
Views
435
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
842
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock