Discuss What electrical tests to do when someone has a flood? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
I am never quite sure if I am doing too little or too much when someone has a flood and I am called in.

The most recent example is a chap has had fairly major flood damage to ceilings, carpets etc and it has poured through certain ceiling pendants and downlights.

Advice on the net states that a full EICR should be carried out. I feel this 'may' be too much and also not enough.

The chap has had some of his floorboards up, he can see where the flood water has gone and we can identify which lights are within the flood zone. Today I have pulled down every ceiling rose and downlight within the flood zone (which you wouldn't do with an EICR) to have a physical check and also carried out an IR test of the entire property to make sure nothing is sitting in water. Would you guys have done more than this? If so, what?

I haven't checked the loft, oven, garage (random examples of places/items definitely not affected by the flood) which you would do with an EICR but would be silly in this case.

PS.. I'm typing this on my new laptop... which I love! It has 8 core don't you know.
 
I would check that all exposed conductive parts on the affected circuits had R2 to them with the wander lead (and ideally every point in the flood zone, even where no ECPs present). Without confirming R2, you might get inaccurate IR results (for example, you had an unearthed class I light that had water sitting in it, it might not show up under an IR test if there was no earth continuity).

Also, would IR test between L+N combined, to the casing of any class II metal lights etc, again using the wander lead.

Other than that, I'd follow your approach.
 
I would check that all exposed conductive parts on the affected circuits had R2 to them with the wander lead (and ideally every point in the flood zone, even where no ECPs present). Without confirming R2, you might get inaccurate IR results (for example, you had an unearthed class I light that had water sitting in it, it might not show up under an IR test if there was no earth continuity).

Also, would IR test between L+N combined, to the casing of any class II metal lights etc, again using the wander lead.

Other than that, I'd follow your approach.
Really good point about the unearthed class 1. Luckily, I had only carried out an EICR on this same property a few months before, but that's besides the point and your point is a good one.
 
Whether things are directly in the flood area or not, the moisture in the air can corrode back boxes, electronics, switch contacts etc.

When my neighbours had a flood, everything was replaced except for lengths of cable…. Unless it was damaged itself by collapsing wet timber structures.

You don’t want to miss something out just because it wasn’t near the actual flood, just for it to become faulty a few months down the line.

Don’t start replacing anything until the dehumidifiers have done their work.
 
I would be a bit concerned about water tracking along cables and ending up somewhere totally different so i would check a few switches on both levels. One flood i dealt with the water had travelled along the cables and made its way all the way back to the DB and into the breaker.
 

Reply to What electrical tests to do when someone has a flood? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
792
So I just started out recently and I’m struggling with what to price myself at. It’s worth noting I live in the east London area and I’m looking...
Replies
12
Views
601
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K
I was asked to see why a set of sockets weren’t working in the house (which appear to be a ring circuit based on breakers) There was no power on...
Replies
27
Views
1K
Hi All I am a seeking help and advice from you lovely sparkis, I have removed a old flood light which was fitted 25 years ago by a friend of a...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock