Why assume it has passed the other tests?Nonsense, if it works it works. The outgoing wiring will not make it trip slower or be less sensitive if it has passed the other tests, what it can do is make it trip faster.
What would be nice would be a consensus of reasons as to why the RCD should be tested with the circuits dissed.
Would it be considered Satisfactory if an RCD operated when tested at the terminals, but failed to operate when tested at a socket-outlet?
What evidence do you have for that?what it can do is make it trip faster.
OK. consensus of opinion is to rest with circuits dissed. seen a few RCDs test fine. then connect the circuits, 1 of which has a N-E fault. in certain cases, the RCD will not trip. so, a perfectly functional RCD will not operate in the real world and maybe death or injury results.