Discuss Whilst we're on the subject of bonding... in the Industrial Electricians' Talk area at ElectriciansForums.net

Absolutely not.. Diferent ph levels and salts in water can make it more or less conductive according to levels.. What is stopping the water board putting conductive pipe joint underground and then this becoming extraneous conductive.. Small copper pipe after stop tap earth to MET no PD between earths in installation, tick jobs a good one!

You are effectively making whatever it is that you have bonded a part of the electrical installation. For example, a metal sink - this cannot introduce a potential (even earth potential), and so is not extraneous and should not be bonded. You would not be making things safer by bonding it.
What would you be giving it a PD too, as everything that introduces a earth path must be bonded!!
 
If conditions are as described in reg 528.3.4, then '(ii) fault protection shall be afforded in accordance with the requirements of Section 411.'

Then bonding of metal pipes with plastic service supply, may be required.

Sorry tried to do that multi quote thing, this was in response to #44
 
You are effectively making whatever it is that you have bonded a part of the electrical installation. For example, a metal sink - this cannot introduce a potential (even earth potential), and so is not extraneous and should not be bonded. You would not be making things safer by bonding it.
What would you be giving it a PD too, as everything that introduces a earth path must be bonded!!

what if the metal sink has a metal waste, going into the ground?
 
I have but nothing seems to happen when I click it. Got other problems like not all keys strokes showing on screen. Been told to use Chrome.
 

Reply to Whilst we're on the subject of bonding... in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
922
Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Replies
3
Views
1K
Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
666
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock