1) fuses are better than mcbs
2) we don't, there are mccbs and so on that provide similar protection to mcbs in larger sizes.
3) switch fuses are cheaper than mccbs
 
It wouldn't be a switchfuse if it didn't have fuses in it.
Do you mean why would someone choose to use a switchfuse instead of an MCB or MCCB?
Fuses generally are better for protecting distribution circuits, they generally can clear higher fault currents and may discriminate better.
Fuses also, generally, allow a higher Zs.
 
While it seems a simple question, the answers are very complicated.

Fuses have several advantaged over MCB/MCCB:
  • Much lower maximum let-through energy
  • Easier to achieve selectivity
  • Lower one-off cost
  • Generally higher maximum break capacity (e.g. BS88 fuses are often around 50kA or more, most MCB around 6-15kA, and few MCCB at/above 50kA)
But of course MCB/MCCB have other advantages:
  • Lower let-through energy at medium fault currents (in the ~1kA PFC range where you have just entered the "instantaneous" trip region)
  • Can be reset by non-skilled people
  • Can be used safely to break/make under load
  • No risk of accidental replacement with wrong value
Cascading MCB leads to poor selectivity: basically the upstream breaker's magnetic trip is often already well underway before the downstream MCB's contacts have opened enough. MCCB, at least the fancy expensive electronic types, can have a bit of a delay to achieve good selectivity with downstream MCBs trip characteristics.

Fuses, due to their smooth trip current/time curves, etc, find it easier to achieve selective with around a 2:1 rating difference (e.g. a 16A fuse down from a 32A fuse will always blow first) and even with the let-through behaviour of MCBs, still achieve acceptable selectivity for most combinations of MCB & PFC value.

So the TL;DR answer is: Fuses are far better, for a given cost, as an upstream OCPD choice.

If you have a spare half hour you might want to watch this semi-sales video:
View: https://www.youtube.com/watch?v=3dckmSgp1nw

[automerge]1596581555[/automerge]
Fuses also, generally, allow a higher Zs.
I forgot to mention that, please don't take my "Fuse appreciation society" badge away"!

Basically as you get to fault currents that blow a fuse in under tens of seconds the fusing time decreases very rapidly with increasing PFC. So for a given disconnection time requirement (whether 5s or 0.4s) you will generally find a fuse can meet it at a higher Zs (i.e. lower PFC) than a MCB, even though the MCB will trip quicker than the fuse when looking at lower overload levels that take minutes to clear.
 
Last edited:
Part of the reason we use HRC type fuses in industrial / large loads is
because HRC fuses ere designed to contain the sometimes learge arc that can occur when a large and / oir reactive load is suddenly isolated.
Something a standard type mcb would not handle.
They do make some industrial size circuit breakers with biult in ceramic lined arc shutes.
these types of breakers will handle it, not cheap mind !
 

Reply to Why do we use cartridge fuses and not MCBs? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

when installing circuits protected my mcb's , i have always used the 80% rule. eg a lighting circuits where the load won't exceed 80% of the mcb...
Replies
2
Views
848
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
653
8.5K shower unit is wired to plastic box consumer unit to 30 amp cartridge fuse with no RCD It’s the original shower installed when the house was...
Replies
19
Views
4K
Hi I have a customer who has a kiosk with 100 amp cut out fuse supplied from UK power, he needs to bring the power 178 meters to his house, He...
Replies
8
Views
942
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock