Discuss Wiring High bay lighting in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
74
Good Morning all,
Just scratching my head a bit, Doing a bit of preliminary design for a large factory and I've come to sizing cables for the lighting, The lights are 4 x 80w These can't be changed unfortunately, They are controlled by sensors in banks of 6 giving each bank a load of around 8.4A. With the shortest circuit being around 34meters, Within high level lighting trunking. After running the details through our magic software We are getting a cable size of 6mm! Which do not connect into the light fittings. I can't change the fittings, or the locations of them etc.

In my experience on the tools I haven't really had a lot to do with wiring such a system so was wondering how they are normally wired. I didn't know whether it would be best to wire the 6mm to a marshalling box/Klik rose type system and then flex out to the light? But then was thinking that Connecting 2 x 6mm's into a such a system may be difficult.
How have you guys done this in the past?
 
Or you could wire a 2.5mm rfc and spur off using click roses.
 
4 x 80w These can't be changed unfortunately, They are controlled by sensors in banks of 6 giving each bank a load of around 8.4A

Assuming power factor of unity. Are you certain that this is the case for the existing fittings, before getting too committed to 8.4A Ib?

I'll put that info Through Our machine

What sort of machine do you need to work out voltage drop? I normally use a smoke packet.
 
Assuming power factor of unity. Are you certain that this is the case for the existing fittings, before getting too committed to 8.4A Ib?



What sort of machine do you need to work out voltage drop? I normally use a smoke packet.


My dear old mother would be most upset if I took up smoking just to work out volt drop, So I just use Hevacomp Connect software.

I'd never even considered power factor to be honest, I'll look into that!
 
I'd never even considered power factor

On corrected electonic ballasts it might be very near unity, on uncorrected wirewounds the current may be 50% higher than you've allowed.

Re outsize cables, I remember designing some circuits for 120V discharge followspots in a theatre built to US wiring code. The spots were plugged into 20A NEMA outlets, but the length of the cable and low permissible drop lumbered us with 4AWG (21mm²) cable, which obviously had to be terminated in a separate box with a 14G link to the outlet.

BTW I don't smoke either.
 
On corrected electonic ballasts it might be very near unity, on uncorrected wirewounds the current may be 50% higher than you've allowed.

Re outsize cables, I remember designing some circuits for 120V discharge followspots in a theatre built to US wiring code. The spots were plugged into 20A NEMA outlets, but the length of the cable and low permissible drop lumbered us with 4AWG (21mm²) cable, which obviously had to be terminated in a separate box with a 14G link to the outlet.

BTW I don't smoke either.

do you want me to send you some of my old smoke packets to do your calcs. on? you can ignore the Polish health warnings. where can you buy smokes named "eithers"?:35:
 
Don't worry Tel, I've got an app for my phone. You can select between Marlboro, B&H and Silk Cut, you can do trig in either degrees or radians, ten memories, optional scientific notation and it has a special function for making little sketches of tricky conduit bends.
 
The lights are 4 x 80w These can't be changed unfortunately, They are controlled by sensors in banks of 6 giving each bank a load of around 8.4A. With the shortest circuit being around 34meters, Within high level lighting trunking. After running the details through our magic software We are getting a cable size of 6mm!
Are you saying that, even at a circuit length of 34m, you need to use 6mm²? If so, is it cable grouping that's forcing this size of cable? It can't be volt drop at this length unless you're using a very low volt drop figure?
 
Re: Wiring High bay lighting
quote_icon.png
Originally Posted by YoungBart
After running the details through our magic software We are getting a cable size of 6mm!



Have you considered the fact that apart from the first section of cable the rest won't be carrying the full current?

Yep, That's all been taken into account, it's the first section I'm referring to.

HandySparks, unfortunately we are already tight on Volt drop due to the length of incoming cable and supply to the DB feeding the lighting.
 
Just looking at your Signature YoungBart, this is a famous Einstein quote but he was unaware at the time that there is actually a fish that does climb tree's as a survival instinct when its natural water habitat drys up - Mangrove Killifish be the strange creature and means Einstein on this occasion slipped up as that so called genius fish exists ;)
 
Last edited:
Just looking at your Signature YoungBart, this is a famous Einstein quote but he was unaware at the time that there is actually a fish that does climb tree's as a survival instinct when its natural water habitat drys up - Mangrove Killifish be the strange creature and means Einstein on this occasion slipped up as that so called genius fish exists ;)
Youll be telling me next E doesn't equal mc2 :49:
 
Yep, That's all been taken into account, it's the first section I'm referring to.

HandySparks, unfortunately we are already tight on Volt drop due to the length of incoming cable and supply to the DB feeding the lighting.

If the volt drop is already tight on the distribution circuit then no amount of messing around with the lighting circuit is going to cure that and you will be stuck with big cables.


But look on the bright side, at least you don't have to worry about grouping factors
 
If the volt drop is already tight on the distribution circuit then no amount of messing around with the lighting circuit is going to cure that and you will be stuck with big cables.


But look on the bright side, at least you don't have to worry about grouping factors

That's what I figured unfortunately, Just wasn't sure if there was a certain way of wiring this type of circuit, Looks like wiring as a 2.5mm Ring has sorted it.
Thanks for all the help guys.
 
Last edited:

Reply to Wiring High bay lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
683
Hi everyone, I really hope someone will be able to help. So last night I tried to change 2 ceiling rose / pendant lights at my mother in laws...
Replies
5
Views
1K
Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
557
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock