The lights are 4 x 80w These can't be changed unfortunately, They are controlled by sensors in banks of 6 giving each bank a load of around 8.4A. With the shortest circuit being around 34meters, Within high level lighting trunking. After running the details through our magic software We are getting a cable size of 6mm!Are you saying that, even at a circuit length of 34m, you need to use 6mm²? If so, is it cable grouping that's forcing this size of cable? It can't be volt drop at this length unless you're using a very low volt drop figure?