Late at night....tearing my hair out....need help with working out resistor calcs.

230V supply....R1=70...R2=90

What is the value of a resistor which when connected in parallel with 70 ohm resistor will cause a total current of 2.4 amps to flow in the circuit?


any guidence to push me in the right direction greatly appreciated
 
Let the unknown parallel resistor = Rx
The total circuit resistance (Rt) that would cause 2.4A to flow:
Rt = V / I
The equivalent resistance of the parallel resistors (R1 & Rx):
Req = Rt - R2
The unknown parallel resistor Rx:
1/Rx= 1/Req - 1/R1

Rx= 6.36Ω (to 2DP)
 
Last edited by a moderator:
If you PM me I’ll send an Excel spread sheet. It originally set off as transformer and motor calculations, but it’s got a bit like Toppsy it just keeps growing. Parallel resistance calculations, unbalanced neutral currents and all kinds of things have found there way in there.
 
hi mark
struggling a bit with the calculation as im getting a defferent answer to you.
my working out is as follows....
230/2.4=95.83ohms
95.83-90(R2)=5.83
(1/5.83)-(1/70)=0.17-0.014
1/0.156=6.41
Rx=6.41

anyone able to tell me where i've cocked up? cheers
 
Last edited:
hi mark
struggling a bit with the calculation as im getting a defferent answer to you.
my working out is as follows....
230/2.4=95.83ohms
95.83-90(R2)=5.83
(1/5.83)-(1/70)=0.17-0.014 = 0.171526586 - 0.014285714
You have rounded up the result of each reciprocal above, if your final answer is to be accurate you need to use all the decimal places, as i have shown above, and once you have the accurate final answer then you can round up and simplify to give a real world answer. Where even a precision wound resistor is unlikely to be accurate to more than 2 decimal places.
1/0.156=6.41 1/0.157240072 = 6.359669628
Rx=6.41 therefore Rx = 6.36 (to 2DP) Always show all of your workings before rounding, so that the examiner can award you maximum marks for each step you get right.
anyone able to tell me where i've cocked up? cheers

See the corrections above, hope this helps, Mark.
 
Last edited by a moderator:

Reply to Working out resistor calculations... in the Australia area at ElectriciansForums.net

Similar Threads

My brain has been exercised a bit by this. Am I on the right lines with this extremely simplified example: If we take: -TNCS installation with a...
Replies
11
Views
4K
Page 337 cites UL testing, where arc resistance was found to be only 30 milliohms...
Replies
0
Views
747
Hi I am a current student studying to become an electrician and a question has thrown me. I'm wondering if someone could help, there is a...
Replies
10
Views
8K
Hey, I'm an electrical engineer in training and i was wondering how you could calculate the total resistance in a series-parallel circuit? I...
Replies
10
Views
2K
T
Hi guys, Just wondering if you can help me on this one, I have a RLC series circuit the values are as below; R = unknown L = 800mH C = 300uF...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock