Most likely answer I think is a N-E fault somewhere in the installation.
Unless it's got a different type of RCD installed, either an A or B type instead of AC?
Yes that's the conclusion I came to. Thing is I've completely disconnected all circuits and tested them one by one, started with radials and it trips the rcd no matter which circuit I test.
 
me and max are trying to get my head round this, the possibility he has over sensitive rcd ,he needs to put the tails from where rcd trips to the other side ,and see if that trips. swap rcd's if possible.
 
Yes

I have. It does not give me options of a 3 lead test or two lead test.
I'm confused, which test option do you have? As I said before, my Megger 1730, gives the options of;
3 lead low, 2 lead low & 2 lead high Zs/Ze tests. I can't understand how yours does not? I'm really trying to help.
 
I think you misunderstood my question.

The cu in question has 2 x rcd's, did you actually test the other one, and if so does it test properly,?
I understood what u wrote, the rcds are fine under rcd test. They trip and comply with bs7671. Zs is the issue I'm having.
 
Yes
I'm confused, which test option do you have? As I said before, my Megger 1730, gives the options of;
3 lead low, 2 lead low & 2 lead high Zs/Ze tests. I can't understand how yours does not? I'm really trying to help.
there are two types of 1730. The earlier version does not give you the options. Yours is the new version 1730
 
Yes

there are two types of 1730. The earlier version does not give you the options. Yours is the new version 1730

I see, I didn't realise that. Yours must have a really old firmware version, I purchased mine in 2012. Have you considered getting a firmware update? Megger offer that option with their calibration service £69 + vat.
 
I see, I didn't realise that. Yours must have a really old firmware version, I purchased mine in 2012. Have you considered getting a firmware update? Megger offer that option with their calibration service £69 + vat.
Think I'll have to. Thanks for your patience and feedback
 
Your post has nudged my elderly memory. I seem to remember before I bought mine, of issues with the early 1730 firmware causing problems with certain RCD's, amongst other things. I've googled back a few pages, and there's quite a few references to that around 2012. Might be your issue? What is the make of RCD's?
 
Your post has nudged my elderly memory. I seem to remember before I bought mine, of issues with the early 1730 firmware causing problems with certain RCD's, amongst other things. I've googled back a few pages, and there's quite a few references to that around 2012. Might be your issue? What is the make of RCD's?
contactum
 

Reply to Zs tripping rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
346
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
829
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock