so, one advantage of the 17th is, with everything now on RCD ( well almost), we don't have to remember all those max. Zsvalues for different MCBs. every cloud has a silver spoon!
 
RCD/RCBO circuits will have the Zs part of the form filled in as 1667 as that is the "Zs" as such for the circuit.

On domestic the chances are that as the board that is fitted will be a dual board then you also have overload protection by MCB and that circuit will have your Zs, and you will enter the Zs results. A lot of argument is now happening that even on dual boards you can fill the Zs for each circuit as 1667 as all circuits are RCD protected. IMO in a few years once we are all use to this we will all fill the schedule of resutls with RCD protection as 1667. I have to admit until recently I use to fill the Zs part in for each circuit as measured but I will start doing it the 1667 method.

Obviously on PIR's for older installtions, and installtions not needing RCD protection you will still do Zs as normal.
 
even so, still put in the measured Zs in it's column, but max. as 1667.
 
Well that's your answer Malcolm, the Lord hath spoken!

And on the seventh day, the NICEIC wrote the regulations!
 
1667 is for TT systems.
On a TNS system the mcb or rcbo is your method of complying with 411.3.2.2 & you use table 41.3
The rcd is for additional protection so 1667 does not come into it.

Table 41.5 is for TT systems.
 
1667 is for TT systems.
On a TNS system the mcb or rcbo is your method of complying with 411.3.2.2 & you use table 41.3
The rcd is for additional protection so 1667 does not come into it.

Table 41.5 is for TT systems.

If the maximum Zs value for a circuit in a TN system cannot be met, the circuit may be protected by a 30ma RCD. 531.3.1
 
Last edited:

Reply to Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
787
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
765
Hi All, Can anyone help with calculating a Zs value for the fuse described in the title. The fuse sizes in Fig 3A3(c) of the 18th edition wiring...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock