max Zs= U0/Ia (x0.8) only works for B C D mcbs 60898 rcbos 61009. (table 41.3) makes life easier to work out max zs without looking it up... fuses i look up. ;-)
Jud - you are strictly correct but post #75 was in reply to another post and I, at least, think it quite obvious that he is referring to his discovery/realisation that the 5, 10, 20 only works with 60898s.

Also, as you can see he does refer to 'without looking it up' or as I put it 'needing the graphs'.

I just got the impression that you were 'raining on his parade' when he wasn't really wrong if read in conjunction with his previous post.


Edit -substituted I for you
 
Last edited by a moderator:
Jud - you are strictly correct but post #75 was in reply to another post and I, at least, think it quite obvious that he is referring to his discovery/realisation that the 5, 10, 20 only works with 60898s.

Also, as you can see he does refer to 'without looking it up' or as I put it 'needing the graphs'.

I just got the impression that you were 'raining on his parade' when he wasn't really wrong if read in conjunction with his previous post.


Edit -substituted I for you

I didn't intend to rain on his parade. His previous post regarding 60898 and 61009 breakers was bang on the money.

I was replying soley to post #75, which is why I quoted it. SimpleSimon asked if the formula also applied to BS 88 fuses, to which Smiffy replied...

max Zs= U0/Ia (x0.8) only works for B C D mcbs 60898 rcbos 61009. (table 41.3) makes life easier to work out max zs without looking it up... fuses i look up. ;-)
 

Reply to Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
787
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
764
Hi All, Can anyone help with calculating a Zs value for the fuse described in the title. The fuse sizes in Fig 3A3(c) of the 18th edition wiring...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock