Questions and electrical advice in the Periodic Inspection Reporting & Certification - This Section is STRICTLY for testing PROBLEMS which members have occured, misunderstood readings, Periodic Inspection Reporting / Electrical Installation Condition Reports, Mathematical Equations/Solutions, Part P and other legislation which require you to Inspect and Test..

Some popular forums: Electrical Forum - Electrical Wiring, Theories and Regulations - Periodic Inspection Reporting & Certification - Electrical Jobs

B
http://esc.org.uk/forum/RCDversionFlowchart1.pdf
Replies
1
Views
1K
robswainelect
R
anyone come across this before zs at board 0.28. then when measure zs on rcd side on live and neutral, reading of 0.77. from the same earth...
Replies
14
Views
3K
S
Hii all I am pretty new to this job and was wondering if somebody could just give me some advice on Zs readings? What would be most likely the...
Replies
4
Views
3K
stu35
S
G
Hello I have just changed a fuse board in a domestic property and have had to install an earth rod as Ze was 1.79k ohms due to corroded clamp...
Replies
4
Views
3K
Engineer54
E
T
Hi Iam working on an outdoor public toilet and my zs readings to the circuits are in the range of 62 to 68.5 ,wereas on other simalir units it's...
Replies
1
Views
2K
I have a circuit of only approximately 8-9 metres from a 61009 type B 32A Rcbo to an oven & hob all run in m T&E and have got a Zs result on "No...
Replies
7
Views
1K
The last problem I have to finish the paperwork is that I have a Zs @DB reading from the house CU of 0.31ohms with a Ipf @ DB of 0.74 ka. On the...
Replies
11
Views
2K
Hi guys, I had a job this morning to change a faulty shower unit in a flat with a direct replacment. when I had fitted the replacment...
Replies
41
Views
7K
Blowcat
B
B
Hi all with a heathy ZE ..22 on a TN-s system i had a R1+R2 of .40 oh my suprise to find that the Zs was 1.01at the furthest socketrechecked my...
Replies
5
Views
2K
N
Hi guys, I was measuring the Zs on a small office ring circuit (9 sockets) using a Megger MFT, the results I got on every socket was <0.01ohms &...
Replies
6
Views
2K
E
Can anyone tell me where i can find the maximum ZS readings for fuses like the ones on the back of the NICEIC booklet for minor works. Cant find...
Replies
2
Views
2K
Please accept my apologies if this is in the wrong category, and also my ignorance as I feel I should know this but I think the heat has confused...
Replies
26
Views
4K
S
A bit confused as to what the prefered method of testing and recording Zs should be? I normally do (r1+r2) +Ze and record all the details...
2
Replies
26
Views
7K
K
HI Guys, ze at the board on a tt system must not exceed 200 ohms i have 138 ohms lovely. but when measuring zs at the sockets, lights, etc im...
Replies
13
Views
3K
J
hi all am i right in saying on tt systems the Zs reading will be a lot higher than the max? and is this exeptable?
Replies
18
Views
2K
M
Afternoon all, Just a quick one, When calculating the Zs on a circuit fed from a secondary distribution unit do you add the R1+R2 of both the...
Replies
1
Views
1K
Guest123
G
S
Hi guys had a conversation with the boss in the office after work today about a zs I got on a 32A c type rcbo bs 61009, the earthing system is...
Replies
8
Views
3K
Morning Guys, Ive done a Zs test on an outside light which is on its own circuit and am getting a reading of 35.8 ohms on no trip mode. Im using...
Replies
11
Views
2K
N
Hello, I have a small query I am hoping somebody can answer for me. When completing a MWC following the addition of a socket to a circuit, where...
Replies
6
Views
899
If you are adding something on a circuit, ie another light, fan etc, when doing the r1+r2 do you get that from the part of circuit you have added...
Replies
7
Views
2K
Post a New Thread / Question

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock