Been asked to carry out some bathroom work including new spots, underfloor heating etc. The existing DB is an old Square D board with no rcd protection at all. Customer wont pay for a new DB, and ive priced a drop in rcbo....... £177 each. Passed this info on to the home owner, and hes...
Hi all,
Looking some electrical advise. I've been told by an electrician that I need to install 5 Nr RCBO's to this consumer unit. Is this correct or is the current set up ok? He has provided me with a condition report stating a 'C2' on the cables concealed in walls. If an upgrade is required...
From the code breakers book,which is a good buy,no mention of the 1667 ohm readings,my thinking if it don’t comply to the Zs measurements,then it don’t comply.
No more sticking a Rcd on that circuit,that’s if anybody does,to protect it .
I have a replacement consumer unit coming upon which is currently off a TT system with a nice low reading on the earth. There is no chance of the DNO converting to TNCS. No SPD or AFDD as per client.
I intend fitting a new Dual RCD consumer unit.
I have researched this site and there was talk...
I'm stuck here fellas.
I have a radial with only one double socket outlet in 2.5mm T&E on a 20A RCBO running five meters in surface mounted trunking. TN-S, R1 and R2 good, 243V measured, Ze 0.12, Zdb 0.29, Zs 0.36, IR all +200MOhms.
RCD trip tests all ok at 0 and 180 and ramp 24mA.
Now these...
Hi everybody.
In the not too distant future I would like to get my current consumer unit replaced. I want to select the brand for my electrician as I’m a pain and like to research things. I was looking to see whether my thought process seems reasonable so would welcome and appreciate any help...
Hi,
I know the basic differences between MCB, RCD and RCBO.
I was wandering what happens to a RCD if the current reaches the RCD's limit?
Why do RCDs have got ampere rating if they don't protect against over current?
In case of RCBO, how do I know at how much ampere they shut down?
Is it the...
I'm fitting two replacement sub-mains panels as part of a long-term upgrade from split-phase to three phase on a part-domestic part-commercial site (my own gaff). I'm using all RCBOs because I like them, but am less keen on the cost of the commercial variants ...
Fellow spark says one MUST use...
I'm looking for a 32A RCBO to fit an old Seimens Stratum200 DB.
I'm going to be doing some work in the kitchen first, then replacing the DB later in the year before other works.
If its another make, it wont matter for the short time its going to be used.
Same reason for not installing a...
Hi guys.
A quick question.
- When people do periodic inspection, is it considerad a defect on the intalation if the Protective diveces are no from the same brand?
- In a TP instalation using fuses should the 3 fuses be from the same brand?
I´m almost sure that I've herad that during my...
At the risk of asking a silly question could someone advise me on the following:
Client has a TT system with only half the circuits covered by an RCD, they want a light adding on a light circuit thats currently not covered by the rcd.
Now with half circuits not going to meet the disconnection...
Hi all
I work on site as a contractor and my colleague was talking to one of the in house electricians on site. He does some work of site for somebody else and the conversation turned to RCBO installation briefly. My colleague stated he was installation last week and this in house electrician...
I'd find a list of manufacturers who are currently producing single module class A RCBOs (and perhaps class A RCDs) quite useful. To my knowledge so far there are:
Hager
Doepke
Schneider
Does anyone know of any others?
Okay may be a thick question but I have an RCD tripping on 5 x test 180 at 40ms. Pass or fail?
GN3 says must not exceed 40ms
BBB says within 40ms
My tester says computer says no.
To be honest I am recommending it be changed anyway but it will be a call back on a new build for another spark so...
My garage has a small consumer unit fitted with elcb and mcbs for the socket and lights. After cutting through a circular saw cable it did not take out the garage elcb but the elcb in the house consumer unit. If I get an electrician to changed the mcbs for Rcbos would this prevent the house elcb...
Well this is a new one on me, new build, very expensive large house, 1 x rfc and radial crammed into in one 20amp rcbo x 2 and multiple circuits in the three 6 amp rcbo's?
Testing an RCD on one rfc upstairs tripped the upstairs and downstairs circuis, which was the RCBO next door to it. Turned off the power to all circuits tested downstairs RCBO on its own RCD failed 1x and 5x tests. Disconnected conductors from this RCBO tested RCD at the board worked ok. Put...
Hi, I just have a few questions in regards to testing an RCBO circuit
Is there a requirement to test at either the furthest point or the DB or is it down to the testers discretion.
Do the test results differ?
What tests on a circuit will trip the RCBO when you are away from the DB. Is it...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.