Hi there
Been stuck on this for a while. What is the maximum r1+r2 reading possible on a lighting circuit in a domestic property. With a type b 6amp breaker.
Also if you guys could tell me about r1+r2 and rn Maximum readings for ring final.
Thanks
On a job today and when testing got a Ze of 0.03 ohms on a tncs. Using a Kewtech 64DL.
Installation has main fuse in hallway outside the 2 bedflat then a switched fuse feeding a submain cable to the actual CU. I did Ze at both immediately before switched fuse and in CU with earth disconnected...
Hello,
I have recently relocated to Slough. Currently looking for Electrical Engineering related job anywhere in Berkshire & London. I am trying hard to get a job but not yet successful. I am wondering if anyone could suggest or recommend me any engineering job. Even I am happy to work as a...
Hi,
Please can anyone advise me as to who would be able to read the internal memory via the IEC 1107 port of an Ampy 5235A meter. I had one installed as a check meter years ago which was left in place & I believe it holds the data I need to claim back from my supplier all unused exported energy...
Afternoon Ladies & Gents,
I'm a new member to the forum so thought I'd introduce myself.
Been qualified for around 10 years and have finally set up on my own. I am new to the test and inspection side of things so I am seeking advise on the following question. Any help would be greatly...
Hi there
Testing at origin of a domestic property, I have found:
L-N: 0.44 Ohms
L-E: 9.89 Ohms
I had the DNO attend clients address, there response was that it was quite high and confirmed readings of 0.44 for ZE. (Pleasee attached document with their response)
My concern is they don't seem...
Electrical Installation Engineers needed to carry out testing and minor remedial works in domestic properties. Vacancies in London, Hertfordshire, Reading and Cambridgeshire on a permanent basis with immediate start available. Engineers must hold their 17th Edition qualification, ECS and...
Sophie Reuben
Thread
courses
degrees
electrical
electricians london
engineer
engineering
engineers
essex
hiring
london
reading
salary
students
testing
Hi guys.
I have just tested a ring main. The readings end yo end on the 3 conductors were all fine. When I cross connected the live to neutral and tested around the sockets all of the readings were correct ie R1 + rn÷4. But when I tested with live earth cross conceded the readings got higher...
Been testing a modified circuit today.
Ze = o.20
R1 + R2 = 0.77
Zs = 1.77
So the reading is about 0.80 higher than I was expecting... Nothing on this (lighting) circuit switched on..... I was testing at the end of a smoke alarm addition.
I've read elsewhere, that its a good idea to do a Zs on...
Did an EICR in a domestic property, earthing arrangement was a TN-S with a Ze of 0.51 ohms.
There are 2 ring final circuits protected by 32amp 60898 type B mcbs. Both circuits have additional protection from a 30mA RCD.
My Zs readings for the circuits are 1.63 ohms and 1.89 ohms.
My question...
Evening. Did a Zs test today on a TT lighting circuit and got a reading of 335ohms. I haven't checked Ze yet but I'm presuming that's also in the same ball park. I'm aware of the upper limit Zs of 1667 and the advice contained within the good book that states Zs should be below 200, so I'm in...
I am going to quote for a job (new circuit). Problem is the 10mm water bond is under the living room carpet/furniture as there is no stopcock in the house. I know it's within 600mm of the incoming water pIpe because I connected it there many years ago. I did a quick wander lead test from the...
i've recently installed a new Consumer unit at home and will be using it as my first niceic assessment. I'm getting an insulation resistance reading of 1.7 on a lighting circuit in the osg it says minimum reading of 1 is this going to be ok?
I've discovered what section of the circuit is giving...
hi did a IR on a shed board L-N was 0.11Mohms so took out the radial circiut and light circuit did them separately and was fine 299Mohms so why low when they are connected to the shed board????? dont do much testing so help be nice cheers
I bought a light changing LED floodlight on the web and it arrived today - as I'm slobbing around I thought I better take a look at it and read the instructions before I install it...
So this is the unit out of the box:
These are the "instructions" for the unit:
And these are the...
Octopus
Thread
attach
changing
flood
instructions
led
light
longer
media
reading
these
I have just purchased a transformer for some under cupboard strip LED's. The unit is CE marked. The ELV side of the transformer has 2 short flexes coming out of it with a CSA of 0.75mm². I was going to just extend these out to the 2 strips of LED lighting I am installing but after reading...
I've just got the Alphatek Tek837 clamp meter as it seemed a good price compared to others with the same features, does anyone have any experience with this meter, since i ordered it i've learnt it's been sold under different brand names, Metrel tek837, Alphatek tek837, Di log DL6404 and...