require

  1. driverman

    Rotary switches.

    Hi, As daft as it seems I have never installed a rotary isolation switch in my life. I've wired for an AHSP whereby 2 x 1 circuits are required, one of which was wired in 10.0mm. AHSP installers require 2 x isolator switches indoors by control equipment. They insist on isolator switches indoors...
  2. B

    HNC Building Services - Maths Skills Require Brushing Up!

    Hi everyone, First time poster but long time member who could use some friendly and helpful advice please. Basically I'm at that point in my career were I'd like to move higher up the ladder and after speaking to work colleagues I've been advised that a HNC/HND in Building Services Engineering...
  3. Energetic

    Does a TT Earth 0.13Ohms require a 100mA incomer?

    Had an interesting one this week, customer assures me he's on TT, DNO days the same but i'm getting 0.13Ohms on the Ze, never seen it that low befor. There's no 100mA RCD on the supply and it doesn't look as if there's ever been one, so with that reading i'd assumed it was a TN system... so my...
  4. C

    Do hand dryers require RCD protection

    Guys i'm doing an EICR at the minute. Do hand dryers for public use require RCD protection? Wired in singles in earthed steel pipe, no bath or shower in the room........
  5. M

    16A socket on a radial require 20A Overcurrent device, where's the reg?

    Hi all, I hope this is the right place to post this question. I'm revising for my 17th edition exam tonight, I qualified on the 15th edition too long ago to mention, and my on site guide says in section H3 that radial final circuits using 16A sockets complying with BS EN 60309-2 should be...
  6. R

    Do I require a fuseboard ?

    Hello there, can anyone tell me to which regulation I should have a fuseboard ? I have looked at Reg 533.1 but it does not say I cannot have one to a different regulation number. The scenario is thus: A council run block of flats. It is an outside scenario in a mains cupboard. It is supplying...
  7. H

    Require Training

    Hi all I am new to this forum and looking for some advice..I am currently doing the 2357 city&guild and I am close to completing the 17th edition but the trouble is I need a bit of hands on training.. I am willing to work for free jus to get a bit of training can anyone advice me what to do.. It...
  8. K

    how to use mulimeter analog. i require to check charger volt and ampere.

    how to use mulimeter analog. i require to check charger volt and ampere. Please help me...I want to say thank you for all your kind help.
  9. L

    22Kw Motor, 415v Cable Installation

    Hi all, Just a quick check to make sure I've got the right size cable really. I have been asked to wire up a conveyor system which has a 22Kw, 415v motor. With the following information I have determined that I require a 50mm 4 core SWA cable for the installation and would just like to clarify...
  10. i=p/u

    pir that doesnt require a neutral.

    im looking for a pir that doesnt require a neutral . im looking to replace a pull cord in a bathroom ... when i search for this i seem to get directed too the ones you would put at switch height.... these seem exspensive would their be any problems or have you any expierience in using them...
  11. D

    RCD protection in garage

    If I have a distribution circuit (to a garage with accommodation upstairs) does the CU in the garage have to have RCD protection or is it sufficient for the main CU in the house that feeds the garage to have RCD protection? Just wondering about regulation 411.3.3 additional protection as there...
  12. M

    Does Single Phase Or Three Phase Require a Neutral?

    Also, how does the neutral work on a phase system?
  13. M

    in-line fuses in fan isolator

    hi all, bit of an issue... i have a property which is has finished decor and wired in 3 plate. not ideal time to be accessing floors etc for cables and its a flat roof extension with the bathroom and utility etc not being last rooms in circuit. i would like to keep the fans we have and they have...
  14. C

    Boiler room sockets - do they require an RCD?

    Hi all A customer has had a recent PIR at a commercial premises and some boiler room sockets have been flagged as a D1 for not having RCD protection. All are in the locked room which is only accessible to the caretaker. I don't see a problem with this and don't see why they need an RCD adding...
  15. K

    SMA 400TL tripping RCD

    Just switched on and inverter goes through the motions. Just at the generating stage and it trips out the RCD. Replaced RCD, checked ALL connections 10 times each, run as 2 strings as many times before, all connections are correct. Any ideas? I don't really want to take this out now and send...
  16. S

    Testing block of flats

    Hello, Couple of questions, firstly does each flat require it's own dedicated earth to the main incoming on the ground floor of the property, zs readings are fine with the 10mm 3 core SWA that has been used. (never certed a block of flats before, jus wanted to be 100%) And, there is a...
  17. S

    solar pv and automatic disconection of supply ADS

    forget type B rcd's at minute do we have to use a .30ma rcd to meet 17th edition requirments of .4 seconds disconection times for domestic solar pv system (16amp) even if cable is surface mounted outside in conduit ? regardless of Zs as its normally low anyways to gain 1% volt drop. but...
  18. D

    Does a CPC require mechanical Protection

    We have been asked to carry out some linking up eart bars on 5 blocks of flats, they want the CPC running in metal conduit, where I think that a CPC can be clipped direct, anyone know the answer and possible reg number.
  19. S

    SJIB (Scottish) Certification Scheme Sjib

    I have been trying to get a SJIB grading card but have come up against the following obsticles. I completed an Electrical Engineering apprenticeship which had all aspects of Installations, maitenance, fault finding,inspection and testing of electrical systems. I also have 17th Edition IEE...
  20. P

    what requirements do you require to install PV.

    Evening all, have ben aproached by a few customers enquiring about pv. what do you need to start installing please, I know the new c&g 2351 does go into pv,but wasn't sure is 2330 allows you to do installs! thankyou for any help and guidance anyone can give I really apreciate it! Paul

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock