When unable to carry out a Zs test on a lighting circuit (large/heavy chandelier type lighting), then the R1+R2 + Ze measurements are instead used and this is noted, but is it the norm to still write this value in the Zs box on the schedule of test results or just in the notes. I ask because...
Nicebloke
Thread
box
calculation
chandelier
lighting
results
schedule
still
test
Hi for a ring circuit, is there any need to measure and enter R1 + R2 values on a schedule of results ? Because an r2 value is already measured (together with r1 and rn). If I needed a ring R1 + R2 value to calculate ZS (although i would find ZS with a socket tester so really no need; but if I...
Hi
I have just changed both an off-peak CU and a normal CU. I have tested both. Can i put them both on the same cert or do they need to be on two different EIC's ??
Hi, Hoping someone who is familiar with Easycert can tell me how to export a DB schedule to excel/word. Apparently its been added as a feature in a recent update but I cannot for the life of me find how to do it.
Any ideas? Otherwise I will email tysoft tomorrow for the answer.
Hi all
A little clarification please if anyone can help.
I work for a metering company installing modbus and AMR tenant sub metering and data logging equipment.
when installing a new supply (1new circuit) from an existing DB for whatever purpose, we are filling out a full E.I.C cert if an...
I did a DB schedule on MS Excel. It is editable and you can add your own company details and logos etc.
I print several off at once on to A4 sticker paper, and it gives a nice professional finish.
I can email you the files if you PM me. I did try to upload them just now but could not due to...
if you can help me along on the tick sheet cheers..
these are the faults i found today..
1.Cable duct not sealed C3
2. unterminated sy cable laying on floor (not live) C3
3. Rcd for additional protection not tripping in required times C2
4 no discrimination between protective devices...
Hello all,
The Schedule of Inspection forms for an EIC offer you 2 suggestions to enter in the boxes, either a tick to say an inspection has been carried out and the result is satisfactory or N/A to show that an inspection is not applicable to a particular item.
In section 7 (consumer...
Hi guys, been away off this site for ages, glad to be back. No doubt been asked many times before,but is there is a link whereby I can download EICR / EIC forms just to use as a one off.
Also as I'm very rusty filling in these forms, is there an explanation page for the Schedule of Inspection...
Hello everyone I'm hoping somebody can shed some light on a few of the inspections on the Electrical Installation Condition Report.
can somebody explain the following few querys and what it is they are looking to no.
4.4 condition of enclosures in terms of fire rating etc
is this a metal clad...
Hello everyone
I'm doing my 2395 practical assessment this week and I'm looking through my condition report inspection schedule.
in the case I come up against a low ( < than 1 mohm ) value on mega ohms while completing a IR test which box in the inspection schedule should I code this fault...
I know theres a 'tick sheet' explained sticky at the top of the forum, but was wondering how we could put one together for the current inspection schedule ticket sheet. As the sticky at the top doesn't cover everything on the current one?
I have done a personalisable DB schedule that may be of interest to others.
I have it in Excel format and can do it as a PDF. Don't know whether it would keep all the formatting in Excel on other peeps PC's, if it doesn't I can put in your details and send as a PDF when I have a spare moment...
Looking for either a good excel template or a nice piece of software to create a cable schedule, with the usual to from and cable size etc, termination details, anyone have one or knows of any downloads.
im having a blank moment! when completing a cert for changing a consumer untit (Electrical Installation Cert) is the schedule of inspections relating to that? The only reason i ask is for example:
routing of cables within prescribed zones - Well im only changing a consumer unit and adding the...
Sorry this may seem like are really daft question but during initial verification and testing do you issue one schedual of inspections for the whole installation or do you issue one for each circuit ?
Hi All,
can anyone explain the purpose of the document "schedule of inspection" why we need it and also the other document "Generic Schedule of Test Results"
cheers
Pete
I was asked which tests during a Schedule of test on a new building and then on an in use building were mandatory.
Where ever I look in the few regs books I have with me they say where "relevant" or "recommended" not will be or shall be done!
So,..... R2 test mandatory or if you feel like it...