Discuss 10.5kW Shower Cable Size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

N

Noob2013

Hi all,

Would a 10.5kW Shower require 10mm or 16mm twin and earth?

I've been doing cable calculations at college and im not 100%.

Cable Length = 20m
Protective Device = 50A
Wiring method = Above plasterboard ceiling not exceeding 100mm insulation

I belive 10mm is sufficient but my calcs are indicating 16mm which I've never heard of for a shower circuit.

Much appreciated
 
Can you include your cable calculations, it would be more helpful if you could.
 
As Pete says, please offer up how you come to your answer, then the guys will help you out.
 
I did 10500 ÷ 230 = 45.6 A

Then I used;

In
Ca Cg Ci Cf

50
1.0 x 1.0 x 0.78 x 1

= 50 ÷ 0.78 = 64.1 A

Table 4D5 shows 10mm can carry 45A with this wiring method.

I've now confused myself because that table shows 2.5mm can only carry 21 A

:S
 
Last edited by a moderator:
Its due to the factors.

By dividing IN by 0.78 you are effectively sizing a cable that will handle a load 20% bigger due to the insulation FACTOR. Ci
 
move the insulation away from the cable.
 
Its due to the factors.

By dividing IN by 0.78 you are effectively sizing a cable that will handle a load 20% bigger due to the insulation FACTOR. Ci

In other words, ...DON'T run the cables surrounded by insulation material, either clip them on top of the loft joists or at the top of the sides of joists. It's not rocket science when all said and done!!
 
it's getting bogged down by technicalities while ignoring common sense.
 
Hi all,

Would a 10.5kW Shower require 10mm or 16mm twin and earth?

I've been doing cable calculations at college and im not 100%.

Cable Length = 20m
Protective Device = 50A
Wiring method = Above plasterboard ceiling not exceeding 100mm insulation

I belive 10mm is sufficient but my calcs are indicating 16mm which I've never heard of for a shower circuit.

Much appreciated

Just to throw a spanner in the works, a 6mm cable will be fine for a 10.5kW shower if no derating factors apply, such as insulation or ambient temperature.

Just goes to show you how running cables in insulation is a bad idea!
 
If you need to run a new cable I would give the customer the price for 6mm and the "upgrade" to 10mm and let them decide. The upgrade isn't much!
 
Hi all,

Would a 10.5kW Shower require 10mm or 16mm twin and earth?

I've been doing cable calculations at college and im not 100%.

Cable Length = 20m
Protective Device = 50A
Wiring method = Above plasterboard ceiling not exceeding 100mm insulation

I belive 10mm is sufficient but my calcs are indicating 16mm which I've never heard of for a shower circuit.

Much appreciated

Seeing as you are an apprentice, i advise gaining access to the trainee section mate.

I am sure you will find it very useful for future questions. :)
 
apprentice?right. then the answer is to use 1.5mm cable so you can observe and study overload effects on cable .
 
And if you plan to install an isolation switch just ake sure you suggest a pull cord and allow for the Crabtree 50A unit.

Pull cords are awful and are a struggle for maintenance . Most customers prefer neon indicated switches as these are more aesthetically pleasing.
 
i prefer a wall switch outside the bathroom. if i have to fit a pull switch , it's got to be crabtree or BG.
 

Reply to 10.5kW Shower Cable Size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
444
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi My 4 bed 2 storey house was extended 2 years ago and completely re-wired, but I am having to upgrade the insulation and board out the loft...
Replies
0
Views
1K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock