Toneyz
Price the job as per BS7671 using 30mA slightly higher than you usually do (not too high that you would be ripping him off) and make it clear that it is with 30mA only.
Discuss 10mA RCD for bathroom circuits in the UK Electrical Forum area at ElectriciansForums.net
Walk away, customers who think they know better are nothing but troubleBeen to look at a job this morning for a CU change, customer the type who wants to have his say on every tiny detail. He has already bought the CU as well, a Wylex RCBO unit.....
I pointed out that the RCBO ratings he has bought don't align with what I actually need...and that some will need to be swapped. So far, so good.
He then says he wants to include 10mA RCD protection for all circuits in the bathroom. This will be lighting, shower and spa bath pump. I point out that I don't think Wylex do 10mA RCBOs....and if they do why hasn't he bought them instead of 30mA ones...to which he said he why can't I add the 10mA after the RCBOs. I tried to tell him that having two RCDs in series isn't great as they won't discriminate and in this case would actually be pointless. I also said that 30mA protection is the accepted standard for this job. Nevertheless, he still wants it.
I told him I'll be back next week, but he gave me a headache. Just wondered what any of you guys would do in this situation?
tell him to get someone else to do it. Don't take ---- from any wise aholeBeen to look at a job this morning for a CU change, customer the type who wants to have his say on every tiny detail. He has already bought the CU as well, a Wylex RCBO unit.....
I pointed out that the RCBO ratings he has bought don't align with what I actually need...and that some will need to be swapped. So far, so good.
He then says he wants to include 10mA RCD protection for all circuits in the bathroom. This will be lighting, shower and spa bath pump. I point out that I don't think Wylex do 10mA RCBOs....and if they do why hasn't he bought them instead of 30mA ones...to which he said he why can't I add the 10mA after the RCBOs. I tried to tell him that having two RCDs in series isn't great as they won't discriminate and in this case would actually be pointless. I also said that 30mA protection is the accepted standard for this job. Nevertheless, he still wants it.
I told him I'll be back next week, but he gave me a headache. Just wondered what any of you guys would do in this situation?
Forget protection, just don't go there!what RCD rating for his bum?
Reply to 10mA RCD for bathroom circuits in the UK Electrical Forum area at ElectriciansForums.net