Discuss 120v 400w Metal Hallide HID Light running on 100v line? in the Lighting Forum area at ElectriciansForums.net

Reaction score
0
So I'm trying to run this 400w HID light in Japan (which has 100v output) but the ballast for the light is rated for 120v-240v.

I want to know if the light will still operate, albeit at lower output, or if there is risk of damaging the light.
 
As the 'ballast' accepts a range of voltages, I assume it is an electronic 'lamp power supply', i.e. an SMPSU rather than a wirewound ballast. This is an important distinction. An LPSU runs at constant power and will normally drive the lamp correctly at full power or not at all. The lamp would not be underrun, as it would be with a 120V wirewound ballast. However, when the supply voltage is too low, the input current will be increased and at some voltage, the unit will shut down to protect itself. Or it should; there is a possibility of blowing its internal fuse in the meantime.

Most 120V equipment will work in Japan so long as the voltage is actually around 100V and not affected too much by drop in the wiring; 85V might be pushing your luck. It will depend on how well designed and built the LPSU is.

Many years ago I remember a new and very expensive piece of kit that kept shutting down due to undervoltage when we were using it in Tokyo on its 120V setting. In a bit of a hurry, I nicked the transformer out of something else less important and reconnected it as an autotransformer, with part of the secondary working as a boost winding to make 120V from 90.
 
As the 'ballast' accepts a range of voltages, I assume it is an electronic 'lamp power supply', i.e. an SMPSU rather than a wirewound ballast. This is an important distinction. An LPSU runs at constant power and will normally drive the lamp correctly at full power or not at all. The lamp would not be underrun, as it would be with a 120V wirewound ballast. However, when the supply voltage is too low, the input current will be increased and at some voltage, the unit will shut down to protect itself. Or it should; there is a possibility of blowing its internal fuse in the meantime.

Most 120V equipment will work in Japan so long as the voltage is actually around 100V and not affected too much by drop in the wiring; 85V might be pushing your luck. It will depend on how well designed and built the LPSU is.

Many years ago I remember a new and very expensive piece of kit that kept shutting down due to undervoltage when we were using it in Tokyo on its 120V setting. In a bit of a hurry, I nicked the transformer out of something else less important and reconnected it as an autotransformer, with part of the secondary working as a boost winding to make 120V from 90.

Thanks for the detailed answer. Just for reference, this is the ballast in question.
I suppose it's not work the risk then, considering HID lights need to be regulated fairly specifically to be stable.

My next question then, would this transformer work? It says 100v to 110-120v 500w.
And this is the cheapest one I could find. Why are these transformers so damn expensive.
 
Yes, it looks suitable. I think the LPSU might well be fine on 100V and it has an external AC input fuse which can be replaced easily if it doesn't like the increased supply current. But if you don't want to fiddle around testing and need max. reliability, get the transformer.

I guess the price reflects the fairly small market for that particular configuration - there can't be that many overseas electrical products imported into Japan, and of those, many will work satisfactorily on 100V anyway. Hence the reviews often mentioning US-made audio equipment, which has a cult following in the Far East and owners would be keen to ensure exactly correct operating conditions as valve amps typically have no internal regulation.

BTW I love the katakana 'ステップアップトランス' (Suteppuapputoransu).
 

Reply to 120v 400w Metal Hallide HID Light running on 100v line? in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I want to operate 3 lighting set up using metal halide lamps for studio works or cinematic projects in the future. as of now i have got two...
Replies
0
Views
1K
How do I limit or feed inrush current for higher constant current use? If I could find solution, then the chosen battery cell type can have much...
Replies
3
Views
996
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445
I have a 115vac line that tests with proper voltage and will power a low watt bulb but will not run a drill etc... Line from main panel to barn...
Replies
3
Views
970
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock