Discuss 18th edition question in the UK Electrical Forum area at ElectriciansForums.net

I have been informed that a plasterboard ceiling is not considered to provide support for cables in the event of a fire, and that all wiring throughout its length will require support with (for example) steel straps, unless it is drawn through joist holes

The plasterboard comment is interesting... Who informed you of this?
 
There’s not many instances where a new build would be effected by this other than if trunking is used to house the cables to the DB or any detached garages with surface conduit drops for accessories inside.

Plastic trunking is not the issue here as it will melt in the fire. The idea is to stop entanglement of firefighters with the copper cables within the trunking.
 
The plasterboard comment is interesting... Who informed you of this?
Currently doing the 18th and this came from the tutor when we dissected the implication of the regulation. Got an NIC visit next month so will run it by him as well. But knowing how the IET interpret things it would not surprise me that plasterboard alone as a support would not meet the requirements
 
Plasterboard has a 30 minute fire rating from building regulations.
Check the Electrcial Safety First website to see if the questions of plastic plugs has been addressed in the faq section.
 
Plasterboard has a 30 minute fire rating from building regulations.
Check the Electrcial Safety First website to see if the questions of plastic plugs has been addressed in the faq section.
The fire rating of plasterboard was raised during the discussion, but this was not considered to meet the requirement for supporting wiring systems
 
If this is so important, why is the reg in the BBB lacking vital information ?

And no I’m not suggesting anybody ignores it .... just that inspections on completed properties will make this almost impossible to verify ....
 
Are you suggesting you will ignore this regulation?


521.10.202
Wiring systems shall be supported such that they will not be liable to premature collapse in the event of a fire.

This is a blanket requirement, no distinction is given to areas of wiring or type of installation. I have been informed that a plasterboard ceiling is not considered to provide support for cables in the event of a fire, and that all wiring throughout its length will require support with (for example) steel straps, unless it is drawn through joist holes.
This will have implications for rewires where cables are often fished through areas where floors are difficult or impractical to lift for access.

Does that now over-rule a previous/current reg that cables could be laid, horizontally, unsupported in an inaccessible void?
 
If this is so important, why is the reg in the BBB lacking vital information ?
How much vital information do you want? The regulation is very clear as far as I can see. Wiring systems must be installed to stay put and not collapse in the event of a fire. That clearly means they must be supported by fire resistant fixings to the structure of the building
 
Are you suggesting you will ignore this regulation?


521.10.202
Wiring systems shall be supported such that they will not be liable to premature collapse in the event of a fire.

This is a blanket requirement, no distinction is given to areas of wiring or type of installation. I have been informed that a plasterboard ceiling is not considered to provide support for cables in the event of a fire, and that all wiring throughout its length will require support with (for example) steel straps, unless it is drawn through joist holes.
This will have implications for rewires where cables are often fished through areas where floors are difficult or impractical to lift for access.
Of course the plasterboard gives fire protection, upto 30 mins.
If it didn’t then we would have to regard the regulation regarding escape routes to domestic new builds currently to the 17th edition and provide metallic support above the plaster board ceiling in hallways and all the exits which is completely unnecessary.
Never been pulled off an Niceic assessment on this.
 
Plastic trunking is not the issue here as it will melt in the fire. The idea is to stop entanglement of firefighters with the copper cables within the trunking.
Hence my comment that the cables housed in the trunking will need metallic support against collapse
 
How much vital information do you want? The regulation is very clear as far as I can see. Wiring systems must be installed to stay put and not collapse in the event of a fire. That clearly means they must be supported by fire resistant fixings to the structure of the building

with the greatest respect the BBB is vague in detail.....

If the IET considers plasterboard insufficient the BBB should clearly state this

As usual, a poorly written regulation open to interpretation .....

Being given 1 possible interpretation by a course tutor is complete tosh imho
 
Of course the plasterboard gives fire protection, upto 30 mins.
If it didn’t then we would have to regard the regulation regarding escape routes to domestic new builds currently to the 17th edition and provide metallic support above the plaster board ceiling in hallways to the exits which is completely unnecessary.
Never been pulled of an Niceic assessment on this.

I did some work in a Nursery stairwell years ago, and I was told to fit two layers of 12.5mm to provide at least 60 mins of fire protection.
I'm no structural engineer, but I'm not convinced about unsupported cables above a plasterboard ceiling require fire proof fixings. The property would be beyond saving by then.

When cables are visible, fair enough!
 
Of course the plasterboard gives fire protection, upto 30 mins.
If it didn’t then we would have to regard the regulation regarding escape routes to domestic new builds currently to the 17th edition and provide metallic support above the plaster board ceiling in hallways to the exits which is completely unnecessary
Based on the information I have been given I think you are wrong, all of the guys on the course, including me took the same line s you regarding plasterboard, but the tutor insisted all wiring systems require support even if above a plasterboard ceiling. Plasterboard collapses during a fire, it may be the case that plastic water pipes will melt which will flood ceilings and cause collapse during a fire. The wiring above if not supported will collapse as well and not meet the requirements.
 
Based on the information I have been given I think you are wrong, all of the guys on the course, including me took the same line regarding plasterboard, but the tutor insisted all wiring systems require support even if above a plasterboard ceiling. Plasterboard collapses during a fire, it may be the case that plastic water pipes will melt which will flood ceilings and cause collapse during a fire. The wiring above if not supported will collapse as well and not meet the requirements.

Who is this “tutor” ? and who does he work for ? And why is he making seemingly unjustifiable statements about plasterboard?
 
Based on the information I have been given I think you are wrong, all of the guys on the course, including me took the same line regarding plasterboard, but the tutor insisted all wiring systems require support even if above a plasterboard ceiling. Plasterboard collapses during a fire, it may be the case that plastic water pipes will melt which will flood ceilings and cause collapse during a fire. The wiring above if not supported will collapse as well and not meet the requirements.
Funny but I think your tutor is wrong
By the time a plasterboard ceiling collapses then the house is pretty much done for
He must know more than most about the fire protection quality of plasterboard
 

Reply to 18th edition question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am currently going self employed. I was never put through any 18th edition courses, so have booked myself onto my 18th wiring regs. I want...
Replies
12
Views
1K
Hi All, Im looking for some information for electrical improvers working abroad. Im currently self funding my way through my electrical course as...
Replies
2
Views
210
Hi got a 8 panel solar system on bungalow, changing the board to 18th edition spd board Solar feed is chased into wall so will this need a type B...
Replies
4
Views
266
Hi I’ve recenly completed my apprenticeship, I come into a conversation with many people that give me 2 answers 1 that I’m up to date with the...
Replies
6
Views
804
Hello all Well, been putting it off, but I need to upgrade my 17th edition to the 18th. Not been a practising sparky for over 5 years, but I have...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock