Discuss 2.5mm 2-core SWA for EV point? in the UK Electrical Forum area at ElectriciansForums.net

Dane

-
Reaction score
2
As the charging point must be outside the DB equipotential zone (separate earthing rod), are people using 2-core SWA for EV points and eathing via the armour?
 
I think in nearly all cases its a tt system you need to install for the charger, so yes if thats the case it would be pointless installing a 3 core, a 2 core would be ideal with an insulating gland

As for ccc, the cable used is usually a 4 mm/32a minimum i think
 
Most chargers are either 16 or 32 amp but the protective device inside is usually a rcbo and rated at 20 or 40 amp and usually a type c.
You then have to consider voltage drop, i installed one on a 10mm 2 core swa circuit and them put a rod in. Same charger on anothet circuit was 6mm H07 but used PME as it was only being used within the waeehouse and not outside.
Every install is different.
It all comes down to circuit design. Use the formulae in the regs or osg and you will find the answers.
 
Most chargers are either 16 or 32 amp but the protective device inside is usually a rcbo and rated at 20 or 40 amp and usually a type c.
You then have to consider voltage drop, i installed one on a 10mm 2 core swa circuit and them put a rod in. Same charger on anothet circuit was 6mm H07 but used PME as it was only being used within the waeehouse and not outside.
Every install is different.
It all comes down to circuit design. Use the formulae in the regs or osg and you will find the answers.

Yes, I understand the cable size may vary for long runs and other C factors, but the emphasis was more on the protection implied by 722.411.4.1. I understand it needs an RCD or RCBO, but compliance with the stated 18th ed. regs means an additional rod and no cpc connected back to the main DB. So a 2-core SWA of the required size is sufficient.
 

Reply to 2.5mm 2-core SWA for EV point? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
What's peoples thoughts on this? 2 core armoured to lamp posts via Lucy switches
Replies
2
Views
433
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
692
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
481

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock