Discuss 80 amp rcd in the UK Electrical Forum area at ElectriciansForums.net

If it is an RCCB it will only trip on residual current, not overload.
If it is an RCBO it incorporates both residual current and overload protection.
 
So if it was a main switch am i needing a 100 amp rccb as the main fuse is 100amp or would after diversity being taken into account and is below 80 amp satisfy this or would i need a rccb off 100amp or a rcbo
 
Randall I have to ask what is your level of experience, because without causing offence this is pretty basic stuff which a qualified Electrician should know the answer to.
 
Main switches and rcd' do not offer any form of over current protection, take a split load consumer unit, two rcd's and a main switch.

the main DNO fuse protects the meter tails connected into the main switch, which is usually rated at 100A on the switch, strictly speaking you can't damage a main switch I suppose as the DNO fuse wold probably blow first at a guess.

its all down to being sensible and not overloading the RCD or main switch etc.
 
The reason i ask is i have seen alot of 63amp rcds with several circuits eg 40 amp shower ,32amp ring, lighting circuit, which could be more than the 63amps. So surely its should be higher.

I have also seen 100amp main switches trip under fault conditions?

I know they don't offer overcurrect protec but i have seen them trip specially main switches
 
The reason i ask is i have seen alot of 63amp rcds with several circuits eg 40 amp shower ,32amp ring, lighting circuit, which could be more than the 63amps. So surely its should be higher.

I have also seen 100amp main switches trip under fault conditions?
no you haven't.
I know they don't offer overcurrent protec but i have seen them trip specially main switches
......
 
Randall I have to ask what is your level of experience, because without causing offence this is pretty basic stuff which a qualified Electrician should know the answer to.

A few years out of being at collage for 3 years, but its always worth asking things as the question may be know but there are always some unawnsered reasons for things that happen, theres alot of contradictions from one electrician i have met to another and even experienced ones, this is proven on this site too.
 
Kurtis a main switch is purely a means of isolation they do not and cannot trip.
 
A few years out of being at collage for 3 years, but its always worth asking things as the question may be know but there are always some unawnsered reasons for things that happen, theres alot of contradictions from one electrician i have met to another and even experienced ones, this is proven on this site too.

So are you employed or self employed, I am not trying to trip you up just trying to establish if you are under someones wing or out there on your own trying to learn as you go.
 
I understand that theres things that exsperienced sparkys know but sometimes obvious things get asked, which make someone look like they don't know ,yet sometimes theres a reason, for instance, my rcd testing question. Yet their was alot of people agreeing and alot completely disagreeing , so very contradictory awsnsers from all you long time sparkeys.

Ive had a main switch trip when theres being a fault (loose terminal which melted the neutral solid bar to t neutral terminals at the top.
Customer said they tried putting it on but every time they did it made a noise and the main switch went.
 
Last edited by a moderator:
I understand that theres things that exsperienced sparkys know but sometimes obvious things get asked, which make someone look like they don't know ,yet sometimes theres a reason, for instance, my rcd testing question. Yet their was alot of people agreeing and alot completely disagreeing , so very contradictory awsnsers from all you long time sparkeys.

Ive had a main switch trip when theres being a fault (loose terminal which melted the neutral solid bar to t neutral terminals at the top.
Customer said they tried putting it on but every time they did it made a noise and the main switch went.

A main switch like this?
 

Attachments

  • image.jpg
    53.3 KB · Views: 54

Reply to 80 amp rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
490
when installing circuits protected my mcb's , i have always used the 80% rule. eg a lighting circuits where the load won't exceed 80% of the mcb...
Replies
2
Views
850
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
770
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
729
Our farm has a main 200 amp panel in the barn which services the barn, an addition to the barn with an apartment, an herb-gardening facility, and...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock