The regulations state that socket outlets intended for general use must be RCD protected. Where this enters into the realm of ridiculous is just the scenario you have. A 3036 board with no RCD protection to any of the circuits, and an electrician protects an isolated socket installed for a table lamp just to comply with the regulations.Despite lack of RCD protection and 3036 fuses as long as disconnection times are met and sockets are not reasonably likely to supply equipment outdoors,contrary to popular opinion the setup has been safe for decades and will be for many more. As already stated I would go with Tel's suggestion which will improve the safety of the entire circuit and be a worthwhile upgrade.
If that is not possible/customer declines cost I refuse to go down the farcical route of an RCD for one lounge socket and would just install it and label it "Not for general use".On the MW form I would state that the socket has been installed without RCD protection for a specific item of equipment.
Thats my take on it,many wont agree,nor am I suggesting it is technically the correct approach.
Really appreciate you elaborating for me. Far happier getting a fuller understanding rather than just quoting whatever the regs states. My client is open to whatever the best route is so will definitely try my best to go with Tel's as it makes sense. At least now I can fully explain it to her, rather than just saying 'that's what the regs state', and then she can make an informed decision.